Question about Goodman Heating & Cooling
My goodman model gmt070-3 is not igniting. it gives me a blink code of 3, which says its a pressure switch or vent blockage. i pulled the pipe and its clear. what does the pressure switch look like and how do i test it?
  • Goodman Master
  • 43,501 Answers
The pressure switch will look something like this
They do go bad sometimes or the tubing may get kinked or have water in it....check all of the tubing that goes to it...
To test it you will need an OHM meter and see if the contacts close if you pull a vacuum on it...
I often just s u c k lightly on it....to see if I hear it click faintly....
but then that is not fail proof either... it can trip that way but not with the vacuum from the fan....
They are not a high $$ item and I would just try replacing it if nothing else seems to be wrong...
heatman101
Posted on Nov 07, 2010
My Goodman furnace, model GMS80903BNA, is not working. I removed the back panels and checked the pressure switch. That seems to be working fine. The exhaust inducer spins up, the igniter starts to glow,...
That blinking 3 times is indicating a pressure switch problem. Try checking for water or a blockage in any of the hoses going to the pressure switch or condensate drain. Check the air intake and exhaust pipe for any blockage including any saggs that may hold water. Make sure condensate drain or pump is working. If you get a glow from the igniter, there may be a blockage in the gas valve or piping.
Jan 23, 2011 | Goodman GMS80903BNA Heater
Furnace problems
On - OK
1 Blink - Ignition failure. Check Gas flow, gas pressure, gas valve, flame sensor.
2 Blinks - Closed pressure switch. Check pressure switch (stuck in closed position).
3 Blinks - Pressure switch - failre to close. Check venter, pressure switch, vent blockage.
4 Blinks - Open limit switch. Main limit or aux limit are open. (My comment - Means overheating in chamber. Often result of blocked intake air. Bad filter. In my case, plastic wrap had been sucked into the intake. )
6 Blinks - False flame sensed. Check sticking gas valve.
Rapid continuous blinking - Incorrect twinning, incorrect primary polarity. Reverse transformer secondary leads, reverse primary wires.
Closed pressure switch can be from dirty combustion vents, bad chamber pressure - like missing screws, maladjusted gas pressure, failing pressure switch, loose hoses, moisture in the hoses or fan blades The switch need to be closed to ge the unit to work
Jan 23, 2008 | Goodman GMS90703BXA Heater
I have a gms8 furnace that will not light. The error code that I get is 3 fast blinks
Sorry to read about your problem, I hope this helps you out.
3 Blinks represent a problem with the combustion fan, pressure switch or a vent blockage.
if you have snow, it could be blocking the intake vent. if not that, most likely a defective preassure switch.
I tried to help you. Please help me and Rate/Vote on my response. We take the time to answer your question's. take the time to rate us.Thanks and good luck
4 Thumbs - Very Helpful
3 Thumbs - Helpful
Jan 02, 2011 | Goodman GMS90703BXA Heater
Light blinks 3 times on a Goodman model gmh80453an
Three blinks is an indication of a pressure switch error. Check your air filter, condensate pump or drain, vent termination and air intake for blockage or debris. Also check the inducer housing assembly for a build-up of water. Pull off the hose(s) going to the pressure switch and clear out any moisture. You may be able to jump out the pressure switch only after the inducer starts blowing to test it. If it starts, the switch is bad. If your venting runs horizontal for any length, make sure there is no build-up of water in either pipe by tapping it and listening for a thud. It should sound hollow and echo when you listen. If you **** in on the pressure switch very lightly, you should hear it make contact and you can test it with an Ohm meter for continuity. Hope this helps!
Jan 18, 2010 | Goodman Heating & Cooling
I am getting the pressure switch blockage and the three red light code. Replaced the pressure switch and still does not work
Hi, the pressure switch won't close error isn't always caused by a defective switch. Occasionally, there really is a blockage in the vent system and that is why there is a pressure switch. You should check for such a blockage, usually caused by a smashed vent cap or spider webs in the vent pipe. Good luck.
Jan 11, 2010 | Goodman Heating & Cooling
Goodman furnace wont come on
If this is a High Eff furnace:
1) Remove the compartment that has the igniter and burners, turn the
power back on, if the furnace lites then you have a problem with the
intake air vent, probably iced over if you live where its cold.
2)Make sure the exhaust vent is not getting backpressure from the
wind.
3) you could cut the pipes on the inside of the house to disconnect them from the furnace, test run the furnace with no pipes.If the furnace
runs then you have a problem with the installation of the vent pipes.
4) Do not run the furnace without the exhaust pipe disconnected,
go to the hardware store and get a couple of rubber clamped
couplings and hook-up the exhaust pipe!
Good Luck
Jan 09, 2010 | Goodman GMS90703BXA Heater
The led light blinks 3 times then pauses then
Pressure switch error code, Check the air filter for blockage, check the vent pipes for blockage or water, make sure the condensate drains are working and that there is no water in the hose(s) that go to the pressure switch(s).
Jan 06, 2010 | Goodman GMS90703BXA Heater
Three blinks on gas furnace, will not maintain flame
3 blinks indicates a pressure switch error. Check or replace air filter, condensate hoses for blockage, check small hose uo to pressure switch(s), check the vent pipes to make sure they pitch back to the furnace, check the air intake and exhaust pipes for any blockage outside. If all looks good, jump out pressure switch as soon as the exhaust fan starts to turn and see if unit starts. If it does, replace pressure switch.
Dec 01, 2009 | Goodman Heating & Cooling
GMP075-3 heater no igniter voltage
Check the venting for a restriction, check the condensate hose for blockage, check the pressure switch and hoses going to it. And make sure the small exhaust fan spins freely.
Nov 20, 2008 | Goodman GMS90703BXA Heater
Goodman GMS90904CXA Wont ignite, light blinks 3 times
Ok, you either have a inducer fan issue or a pressure switch issue or a plugged vent pipe. The inducer turns on to establish a draft for the exhaust. If it is not working you will get this error code. If the pressure switch does not sense pressure caused by the inducer, it will give this code. If either the intake pipe or exhaust pipe is blocked (even y just a little) it will give you the same error code. If the condensate hose or receptical is plugged, again it will give you this error code. Good Luck!
Oct 20, 2008 | Goodman GMS90703BXA Heater
Heating & Cooling Logo