I have a Goodman GME8 Gas furnace. The gas sequence for startup seems to work normally, However when the blower starts, the gas continues for 15-30 seconds then stops. the blower will run for about 1 min beyond that then this resumes after about 2 min.
SOURCE: goodman ac/gas furnace unit mdl. # gmp075-4
i HAD THE SAME PROBLEM, TURNS OUT IT WAS THE FLAME SENSOR, CLEANED IT, AND ALL WAS GOOD
Posted on Dec 13, 2007
machtcl1
  • 61 Answers
SOURCE: furnace starts properly, then shuts down, led flashes 8 times
The first thing to look at is the flame sense rod.
Shut off power to the furnace, remove, clean sensor with steel wool or sandpaper then reinstall the sensor. Reapply power and it should run properly.
Posted on Jan 10, 2009
  • 9 Answers
SOURCE: furnace flame goes low fan stays on
if the gas pressure is good on inlet and outlet of valve u might wanna chk the burner trays and manifold for flakes, dirt, spider webs ect... once u kno the passages are clear from obstruction you can focus on the mechanical. (sounds like gas valve may be getting weak and not able to open fully)
Posted on Mar 22, 2009
  • 116 Answers
SOURCE: I have a Goodman furnace GMPO75, blower cycles on
disconnect the green wire at unit if stops then stat bad if continues look for fan relay or thermal disk calling for fan to come on let me know if this dont repair it and i will pull up the wiring on that unit
Posted on May 10, 2009
  • 116 Answers
SOURCE: How to install a new blower motor in a Goodman gas
remove the blower unit it slides out on some gas furnaces you may have a control bord in the way if you dont have a goodman motor you will need a belly band to clamp to new motor to provide the mounting arms also after loosening the shaft set screw spray w wd40 turn on side and shake motor should fall out if gas furn 115v motor hope this helps
Posted on Jun 09, 2009
I have a goodman gmp075-3 furnace, blower and igniter are working fine but not getting any gas to get furnace going
Check if 24 volts is being sent from the board to the gas valve, if not the board is nad and will need to be replaced, if there is 24 volts at the gas vlave terminals then the gas valve must be replaced.
Nov 08, 2012 | Goodman GMS90703BXA Heater
Gmp075-3 furnace wont stay lit
Sounds like an airflow issue. Is the return air clean? System is not tripping the limit switch with the door off because it's getting all the air it can handle, with door on its not getting enough air???
Aug 15, 2017 | Goodman Heating & Cooling
I have a model GMP075-3, S/n9509835876 that will not lite the gas. The blower does come on for awhile then shuts off for several seconds and trys to restart. I can smell gas at the furnace while the blower...
Unplug your quick connect at the ignitor and chek to see if it has continuity. If it checks good start the furnace and see if you have voltage present at the quick connect. If ya ain't got volts going in then their is a problem with the board. Rich has a nice video at HVAC for beginners HERE
Oct 29, 2011 | Goodman GMS90703BXA Heater
I installed a new goodman unit this past spring. It seems to work ok to good in the day time but the tempature is warmer so we do not need as much heat. At night I know the thermostat is coming on. I...
Heating Mode (Goodman Service Manual)
· The furnace control checks for an open main limit (this
limit is normally closed). If the limit is open, the furnace
will remain inoperable until the limit is closed. During
an open limit the circulating air blower will be
energized. The status light will blink four (4) times.
· The room thermostat reacts to a demand for heat.
· The control will then check to insure that the vent
pressure switch is open. If, at this point, the vent
pressure switch is closed the control will blink two (2)
times and will remain inoperable until this situation is
corrected.
· The venter blower is energized.· The vent pressure switch will close when it detects a
pressure in excess of its setting. If the pressure switch
fails to close the status light will flash three (3) times.
The sequence cannot continue until the pressure switch
closes.
· After a pre-purge of about ten (10) seconds the electronic
ignition device will be energized.
· After a slight delay the gas valve will open.
· The burners will ignite and the flame sensor will detect
the presence of flame. The ignition device will
deenergize. If the sensor does not detect the burner
flame, the gas valve will close and the ignition cycle
will be repeated for a total of three attempts. If, after
the third attempt, the presence of flame is not detected,
the furnace will go into a lockout condition for one (1)
hour. It will then repeat the ignition cycle. This one (1)
hour lockout and retry will occur indefinitely.
· Thirty (30) seconds after the main valve is energized
the circulating air blower will be activated.
· The furnace will remain in operation until the demand
for heat is satisfied.
· Once the demand is satisfied the venter will shut off,
and the circulating air blower will shut off after the field
selectable time off is attained.
· The furnace will remain dormant until the next demand
for heat.
Dec 03, 2010 | Goodman GMS80903BNA Heater
Model #GMPN100-4 Goodman furnace. Vent fan
The sequence of events for furnace operation is -
Fan purge for 30-45 seconds. During this time, a pressure switch is actuated by the running of the purge fan, proving the control board the purge fan is running.
After purge and purge prove, the hot surface ignition and or spark begins. After a few second delay, the gas valve will open. The control board then monitors for flame prove through another sensor located near the burners. If there is no flame within 3-5 seconds, the gas valve closes. It will repeat this process, usually 3 times, before it shuts the system down, which requires a power down of the system to reset.
I have seen trash get into the hose between the purge blower and the purge switch. But you could be having other problems.
Dec 17, 2009 | Goodman Heating & Cooling
Have a Goodman GMT070-3B which the vent motor seems to be sticking. I took apart and cleaned the brushes and reassembled. The furnace will come on only after what seems like the vent motor comes up to...
The whole assembly must be replaced.
The sequence of operation is -
Combustion fan purges the heat exchanger. A pressure switch verifies combustion air fan is running. Usually a 30-45 second purge before the hot surface ignitor glows, or the spark ignition starts.
Gas valve opens after 10-15 seconds and main burners light. Control board monitors for flame and shuts gas valve after 2-3 seconds if main burner does not light.
If burner does not light, some boards repeat this for 3 tries, then locks out and is reset by cycling power.
Air blower comes on after another 30-45 seconds after main burner ignition.
Times may vary based on the specific controller board. A flow chart and timing sequence should be located somewhere on the unit, usually in the fan compartment.
Dec 16, 2009 | Goodman GMS90703BXA Heater
Goodman GMP075-3 ignition problem
bad board,i have had several board failures on goodman
Dec 18, 2008 | Goodman GDS80904BNA Open Flame Heater
Heating & Cooling Logo
143 people viewed this question
Top Goodman Heating & Cooling Experts
Dan Webster
Dan Webster
paulcarew
Brandon Berry
Brandon Berry
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others