Question about Goodman GMS80903BNA Heater
Replaced the ignitor on the goodman gms80903bna furnance. I am now getting the 6w red blinks on the led indicating a rollout switch problem. I did not have the rollout problem before the ignitor was replaced. the ignitor was the only thing that was replaced on this furnance.
  • 1 more comment
  • ldbut Nov 06, 2010
    no, the wires are all in place. i have checked this several times.
    I replaced the ignitor on the goodman gms80903bna furnance. I am now getting the 6 red blinks on the led indicating a rollout switch problem. I did not have the rollout problem before the ignitor was replaced. the ignitor was the only thing that was replaced on this furnance.
    Thanks heatman101
    The problem was a connector on one of the rollout switches was lose. This was causing
    the open condition. I put on a new connector and made sure it was crimped tightly and the
    problem was resolved.
    Thanks again
  • Goodman Master
  • 43,501 Answers
The roll out switch is often located where you could easily have hit the wiring as you changed the ignitor. It is located just outside and over the burners so that if the flame "rolls out" it will sense the heat and interrupt the ignition process.
Check the continuity across the switch, also check the wires to make sure that you have not knock any off accidentally or that there are no loose connections...
You are getting this code because of a open condition in this circuit.
heatman101
Posted on Nov 06, 2010
  • D. Floyd Kolb
    D. Floyd Kolb Nov 06, 2010
    Thanks!!
    Glad it was a simple fix!!
    Guru:
  • 1,524 Answers
There is a possibility you knocked the wires off.
Posted on Nov 05, 2010
Top rollout switch triggers with blinking code *6*, Furnace only runs with cover off
restart unit as soon as your inducer fan came on pump the 2 wires to pressure switch and wait to see how long it stay also watch the flame at the burner
Jan 27, 2014 | Goodman GMS90703BXA Heater
Amana Air Command 90 furnace LED light blinks 3 times pause 3 times
TRI-COLOR (DSI LED) DIAGNOSTIC TABLE
No. of Red BLINKS
1 Flame sensed when no flame should be present
Verify the gas valve is operating and shutting down properly. Flame in burner assemble should extinguish promptly at the end of the cycle. Check orifices and gas pressure.
2 BLINKS Pressure switch stuck closed/ inducer error
Pressure switch stuck closed. Check switch function, verify inducer is turning off.
3 BLINKS 1st-stage pressure switch stuck open/inducer error
Check pressure switch function and tubing. Verify inducer is turning on the pulling sufficient vacuum to engage switch.
4 BLINKS Open limit switch Verify continuity through rollout switch circuit.
5 BLINKS Open rollout/open fuse detect Verify continuity through rollout switch circuit, check fuse.
6 BLINKS 1st-stage pressure switch cycle lockout If the first stage pressure switch cycles 5 times (open, closed) during one call for heat from the thermostat the control will lockout.Check pressure switch for fluttering, inconsistent closure or poor vacuum pressure.
7 BLINKS External lockout (retries exceeded) Failure to sense flame is often caused by carbon deposits on the
flame sensor, a disconnected or shorted flame sensor lead or a
poorly grounded furnace. Carbon deposits can be cleaned with
emery cloth. Verify sensor is not contacting the burner and is locatedin a good position to sense flame. Check sensor lead for shortingand verify furnace is grounded properly.
8 BLINKS External lockout (ignition recycles
exceeded where flame is established and then lost)Check items for exceeded retries listed above and verify valve is not dropping out allowing flame to be established and then lost.
9 BLINKS Grounding or Reversed polarity Verify the control and furnace are properly grounded. Check and reverse polarity (primary) if incorrect.
10 BLINKS Module gas valve contacts energized
with no call for heat Verify valve is not receiving voltage from a short. If a valve wiring is correct and condition persists, replace module.
11 BLINKS Limit switch open - possible blower
failure overheating limit Possible blower failure, restricted air flow through appliance or duct work. Verify continuity through limit switch circuit and correct overheating cause.
12 BLINKS Module Ignitor contact failure Fault code indicates the module ignitor contacts are not functioning
properly. Replace module.Solid Module - internal fault condition Module contacts for gas valve not operating or processor fault.
Reset control. if condition persists replace module.
3 double 2nd-stage Pressure Switch Stuck Open/Inducer Error
Check pressure switch function and tubing. Verify inducer.
Nov 11, 2013 | Patton Electric Patton PUH680-U Electric...
Open rollout or open fuse on Goodman
the fuse is located in the circuit board in the blower compartment and the roll-out is located in the burner section and can be a reset-able switch style or the one time fuse link style which is a a small silver cylinder and is mounted in a ceramic piece and is held in with one screw. Both of these are mounted around the opening of the your burner assembly near the opening. This will be near the area of the gas valve.
Sep 24, 2012 | Goodman Manufacturing Goodman R410A 13...
My Goodman furnace, model GMS80903BNA, is not working. I removed the back panels and checked the pressure switch. That seems to be working fine. The exhaust inducer spins up, the igniter starts to glow,...
That blinking 3 times is indicating a pressure switch problem. Try checking for water or a blockage in any of the hoses going to the pressure switch or condensate drain. Check the air intake and exhaust pipe for any blockage including any saggs that may hold water. Make sure condensate drain or pump is working. If you get a glow from the igniter, there may be a blockage in the gas valve or piping.
Jan 23, 2011 | Goodman GMS80903BNA Heater
Furnance lights and goes right out install new inigter and new flame sensor i also notice the board green light stays on and doesnt give me any blinks to tell me whats wrong so is the board bad?
Without knowing what brand of furnace you have it's hard for me to say. But on most brands that I have installed and serviced when system is functioning right the diagnostic light blinks a slow steady pulse like your heart beat. With you already changing the the ignitor and flame sensor about the only other thing I can think of before changing the board would be the flame rollout switch. Watch your burner when it first fires and see if it is tripping rollout switch. If it is then I would clean burners and see if that helps. Good luck. Thank you.
Dec 14, 2010 | Heating & Cooling
RED BLINKING (6TIMES) ON FURNACE
THE ROLL OUT SWITCH IS LOCATED IN THE BURNER COMPARTMENT MOST CAN BE RESET
Jul 20, 2009 | Goodman GMS90703BXA Heater
Furnace blows cold air, ignitor won't glow.
ok this is going to sound funny but it seems as though the polarity is reversed going into your furnance. to correct this proiblem you first need to unplug the unit and where the cord goes into the furnance at that connection disconnect the two wires. Once theses are disconnected switch the wires .All you are doing is reversing the way the electricity flows into the circut board. I would wager that is the problem
Apr 13, 2009 | Heating & Cooling
Limit Switch
It is rare that a limit switch goes bad. It is a safety control. If it is shutting off your furnace there is a problem that it is protecting you from.
If the limit switch is shutting the unit down your furnace is overheating. Check the filters. Check for any obstruction in the blower assembly. Check to see if you can raise the blower speed. Make sure all registers are open in the house. Your evaporator coil could be obstructed if you do not take good care of your filters.
Feb 28, 2009 | Goodman GMS90703BXA Heater
Goodman gmn100-4
DO you see a red/orange glow? if you do the ignitor works, if not could be ignitor, or a pressure issue " once the inducer motor comes on you should hear a click than see a redish glow, if you dont than it is a pressure issue. way to check this is to pull the rubber hose off the switch and lightly **** on it while the unti tries to start if it comes on than something is stopping the switch from closing.I.E. bird in inducer motor or just a bad switch.
Oct 07, 2008 | Goodman GMS80903BNA Heater