2 TON SPLT UNIT MITSUBISHI MODEL NO MU24AV
THAILAND /
Building hight is about 16 meters, condensing unit at roof,
in installation manual hight is 15 metes with 30 meters pipe run and pipe size is 5/8", and it is not mention that there will be any oil retrun problem
1.Do we need to fix a p oil trap at riser or no need?
2. Do we need to change suction line size or keep same size?
3 if same size of piping and with out oil trap will system works without any problem?
After installing the system would I advice to measure pressures. By the lenght of pipes and hight difference of the units will there be a pressure drop. Be aware if more pipe lenght as the original is used, oil should be added to the system (oil is sticking in the pipes, the more lenght and traps, the more oil will be in the pipes instead of in the compressor).
Posted on Jul 26, 2008
    Scholar:
  • 104 Answers
Pipe size is okay, not that I know any better than the manufacturer, but I would recommend at least two and possibly even three oil traps in the vapor line on the way back up.
Posted on Jun 15, 2008
NEED TO KNOW THE TONNAGE ON THIS UNIT
2 1/2 ton. home is about 1200-1400 square feet ?
Apr 18, 2016 | Ruud Matching Split Air Conditioner
What is the problem with running a 10 SEER condenser with a 13 SEER air handler other than efficiency? I had a 2 ton 13 SEER air handler installed last August to replace one about 27 years old. The...
as most ac units are capillary tube control not tx valve having matched units is critical. as for cost the condensing unit is much more complex and expensive than the evaporator.
Feb 14, 2015 | Amana Goodman R-410A Heat Pump Condenser 2...
Purchased Rheem 4 ton 16 seer AC installer just left
Ask your installing company for the AHRI number. If installed with a
matching furnace and coil as listed in the certification then you will get 16 seer rating. If they installed something different than what is listed in the certificate then demand all parts listed or a refund.
Jul 18, 2014 | Rheem 14AJM49A01-RHLLHM4821JA 4 Ton 16...
Aircondition builds ice on coil
Either lack of refrigerant, stopped up metering device or capillary tube/s, or lack of air flow (due to bad blower motor, or dirty indoor coil) Good luck.
May 19, 2014 | Rheem Complete Split System Gas Furnace 5...
I have a Ruud Model # UACC-036JAS. Any idea on
Hi, yes the number you are showing me 036 indicates its a 3 ton unit. For every ton of cooling, you will have 12,000 btu's of cooling. 36 divided by 12=3 ton unit. Its showing me also its a Ruud Handler 2.0 ton which would be a Model# UACC-024JAS? If your mobel number is the one you gave me, UACC-036JAS, this is a 3 ton unit, absolutely no questions. I hope I have been of help to you. I am a licensed air conditioning / Refrigeration /Heating Contractor. Let me know if I have been of help.
Sincerely,
Shastalaker7
PS If this is a split system with the indoor air handler and condenser outdoors, both coils must be the same tonnage for it to work for you properly. You can't have a 2 ton indoor evaporator coil with a 3 ton condensing unit.
Jun 28, 2010 | Ruud Handler Air Conditioner
I just serviced a carrier split dual condensers on the roof and cooling unit in the building, i shut the breaker off on the roof connected to the condensing unit, but it goes on and off what is wrong?
I would look a faulty breaker. If you're replaced the breaker and the problem persists, I'd look for either a floating neutral or open ground. A neutral/ground problem is doesn't have to be near the equipment but closer to the feeder panel.
Aug 13, 2009 | Carrier Heating & Cooling
MR. SLIM
that is not the correct m/n normally it wouls be like pu24 36. for every 1 ton the is 12,ooo btus son a PU 24 IS A 2 TON A 36 IS 3 TON A 42 IS A 3.5 TON ETC
Aug 12, 2009 | Heating & Cooling
Oil Leak
This would indicate a leak somewhere in the condenser sheet coil. I hate to be the bearer of bad news but you should call a service tech in to fix this problem.
Aug 29, 2008 | GE Zoneline AZ38H12DAD Split System Air...
Heating & Cooling Logo
811 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen