Question about York Furnace Draft Inducer Blower Fasco # A224
I have a York 80 furnace it wont fire up I get 3 blinks which means pressure switch stuck open, I replaced pressure switch, still same problem, the inducer fan will not run, I thought it was a bad inducer fan, so I cut the end of old extension cord and hook it up directly, inducer fan turns on and when I press the safety button on furnace it fired right up with inducer fan running, disconnected power and furnace shut off. Cleaned all connections and hooked back up, but will not run off of circuit board? Could panel need replacing?
  • yecart2u Nov 05, 2010
    Thank you very much for your help.
    James
  • 43,501 Answers
From what you are saying the circuit board has gone bad... the relay that turns on the power to the inducer must have went bad. You will need to buy a new circuit board and replace the old one. Be sure to make all wires or change them over one by one so that you keep track of where they all go...
This is a very common problem and finding a new circuit board should not be hard.
Good luck!!
Heatman101
Posted on Nov 05, 2010
  • D. Floyd Kolb
    D. Floyd Kolb Nov 05, 2010
    Very glad to help!!
York Diamond 80, controller is blinking Code 3 (Pressure switch stuck open).
sounds like u nee a new pressure switch. check 1\4 inch tubing going to pressure switch, remove it make sure no condesation in it., blower will only come on once flame is establised, ventor motor comes on closes pressure switch, brings on ignitor then gas the blower, make sure no blockage in vent pipe
Dec 28, 2015 | Heating & Cooling
Amana Air Command 90 furnace LED light blinks 3 times pause 3 times
TRI-COLOR (DSI LED) DIAGNOSTIC TABLE
No. of Red BLINKS
1 Flame sensed when no flame should be present
Verify the gas valve is operating and shutting down properly. Flame in burner assemble should extinguish promptly at the end of the cycle. Check orifices and gas pressure.
2 BLINKS Pressure switch stuck closed/ inducer error
Pressure switch stuck closed. Check switch function, verify inducer is turning off.
3 BLINKS 1st-stage pressure switch stuck open/inducer error
Check pressure switch function and tubing. Verify inducer is turning on the pulling sufficient vacuum to engage switch.
4 BLINKS Open limit switch Verify continuity through rollout switch circuit.
5 BLINKS Open rollout/open fuse detect Verify continuity through rollout switch circuit, check fuse.
6 BLINKS 1st-stage pressure switch cycle lockout If the first stage pressure switch cycles 5 times (open, closed) during one call for heat from the thermostat the control will lockout.Check pressure switch for fluttering, inconsistent closure or poor vacuum pressure.
7 BLINKS External lockout (retries exceeded) Failure to sense flame is often caused by carbon deposits on the
flame sensor, a disconnected or shorted flame sensor lead or a
poorly grounded furnace. Carbon deposits can be cleaned with
emery cloth. Verify sensor is not contacting the burner and is locatedin a good position to sense flame. Check sensor lead for shortingand verify furnace is grounded properly.
8 BLINKS External lockout (ignition recycles
exceeded where flame is established and then lost)Check items for exceeded retries listed above and verify valve is not dropping out allowing flame to be established and then lost.
9 BLINKS Grounding or Reversed polarity Verify the control and furnace are properly grounded. Check and reverse polarity (primary) if incorrect.
10 BLINKS Module gas valve contacts energized
with no call for heat Verify valve is not receiving voltage from a short. If a valve wiring is correct and condition persists, replace module.
11 BLINKS Limit switch open - possible blower
failure overheating limit Possible blower failure, restricted air flow through appliance or duct work. Verify continuity through limit switch circuit and correct overheating cause.
12 BLINKS Module Ignitor contact failure Fault code indicates the module ignitor contacts are not functioning
properly. Replace module.Solid Module - internal fault condition Module contacts for gas valve not operating or processor fault.
Reset control. if condition persists replace module.
3 double 2nd-stage Pressure Switch Stuck Open/Inducer Error
Check pressure switch function and tubing. Verify inducer.
Nov 11, 2013 | Patton Electric Patton PUH680-U Electric...
York furnace won't ignite
Is the igniter receiving 120 volts after the pressure switch closes? If not, either the board is bad or the pressure switch is open
Nov 27, 2012 | Heating & Cooling
York 80 furnance model P3HUB12N08001A curcuit board light blinks 4 times. What does this mean?
Check on the back of the bottom blower cover...I think it is either pressure switch or high limit...
But the codes are always listed on that bottom cover on the inside...
Here is a tip that will help you try to figure out why your furnace is not working.
Basic Furnace or Heating System Troubleshooting
heatman101
Jan 22, 2011 | Heating & Cooling
On a 80% Rheem upflow furnace... The AC works fine but when switched to heat nothing happens. "OK" LED is on solid, second LED is blinking 3 times, "FLAME" LED is not on at all. What can be the problem?
Hello ANGUS,I think 3 blinks is open pressure switch,try taking the door off the furnace.The upper left hand side is a round black box with a hose attached to it .Gently tap the switch(box) and turn off power for 2 seconds andback on,then call for heat.the blower door has a sticker inside that tells you just what the blinks mean.
Aug 10, 2010 | Heating & Cooling
Gas furnace
Hi check out the pressure switch clean the air filter and check out the fan control see if this is clean
Feb 16, 2010 | York Furnace Draft Inducer Blower Fasco #...
Furnace code light flashes 3 times /pressure switch stuck open
Check the intake and exhaust plumbing for any obstructions. I had same issue, turned out to be ice in the air intake plumbing on outside of house. This may be the problem. The pressure switch can be tested by pulling hose from purge motor that goes to switch and applying a small amount of suction. The switch should make a clicking sound.