Question about Carrier XHB123D X/Y Series Heat/Cool Air Conditioner
Inducer fan on my gas furnace is constantly running even with no call for heat what could this problem be?
    Guru:
  • 1,524 Answers
Bad lock-out switch
Posted on Nov 04, 2010
Have an older Coleman mobile home furnace (Mdl 8665D766). Both blower fan and booster motor work fine; however, during heating, booster motor will keep constantly running after system cycles through
The booster motor? Do you mean the inducer motor that helps push the exhaust? If the inducer motor won't shut off when the thermostat is satisfied and everything else does shut off, it sounds like the contacts on the relay that powers the inducer are at fault
Feb 03, 2018 | Coleman Heating & Cooling
Heat lock out and blower runs
It sounds like you may be having a high limit trip, but I need more details.
Feb 01, 2014 | Gibson KG7SC072D24B 72,000 BTU 92.1% Gas...
My York furnace sometimes doesn't completely ignite
A noisy inducer probably is headed for replacement.
The igniter can produce a healthy glow and still be defective. Mine had to be replaced with a new, improved one.
The thermocouple could be defective even though it seems to open the gas valve when it should.
The heat sensor in the bonnet could be defective. That controls main blower operation.
The heat exchanger could be cracked.
Jan 10, 2014 | Heating & Cooling
I have an older Carrier furnace type 58ss. The main burner will not ignite. Operating look ~ thermostat set @ 78 deg, switch furnace on, inducer fan running, pilot light clicks and ignites, inducer still...
power to gas valve ok .. Replace gas valve after checking gas valve coil for continuity/resistance... with valve removed ...and power to valve ... try blowing thru valve from supply side ... stuck valve.... replace...
Nov 01, 2013 | Heating & Cooling
Draft Inducer problem
On the call for heat from the thermostat the inducer should come on first, a pressure switch proves that the inducer is moving enough air up the stack, closes and energizes the ignition and burners come on. 30 to 60 seconds later the blower comes on. Everything should stay on as long as the thermostat is still calling for heat. When the thermostat is satisfied the burner and inducer shut off and the fan will run to remove the heat from the heat exchanger and then shut off. Cycle complete. Some inducers have a post purge so when the thermostat is satisfied the burner shuts off, the inducer runs for 30 seconds or so and then shuts off. I am thinking that your furnace may be running on the limit switch and when the burner is off but the inducer stays on, maybe the limit is shutting of the inducer. Check your air filter and make sure all your heat registers are open and that the return air grill is not blocked.
Dec 06, 2017 | Heating & Cooling
For some reason the heater does not generate heat. the fan works but no heat. Any Ideas?
I've got an easy way for you to check, and then we can help you from there.
First pop open both lids to your furnace (this may require a screwdriver). Turn up your thermostat, push the safety interlock button in if it has one (it's a button that turns off the power when the doors are removed), and watch.
On most modern furnaces (past 20-25 years) you'll hear/see:
1. Inducer fan
2. orange glow (ignitor)
3. Gas valve opening and ignition (flames)
4. Main Fan.
that's normal heater operation.
The most common issue here is a burned out ignitor, in which case you wouldn't see the orange glow but the sequence would attempt to continue anyway (the gas valve will open and hiss gas, but it won't lite, then it'll give up and try again a few minutes later).
On older furnaces there's a pilot light to start with, the click of the gas valve and boom... ignition.
On new furnaces it's
Inducer fan
gas valve opening
spark - ignition
Main fan.
and there are some oddballs in between, particularly the Lennox Pulse. If that's your furnace just back away slowly and call a professional... some guys won't even touch those, so be sure to mention what it is... if you call a pro.
So go ahead and watch it run, then tell me/us what you see.
May 06, 2011 | Bionaire Heating & Cooling
I have an 11 year old natural gas forced air furnace--a Goodman GMPN100-4 Rev B, which is 100K BTU and 92% efficient which was working fine at the end of last winter. I went to turn it on for the first...
You are correct. If the inducer motor is warm, but not running, it has seized up. If you replace this yourself, I also suggest that when you replace the inducer fan, check to make sure the secondary heat exchanger isn't clogged, or the condensate drain(s). If you have an HVAC contractor replace it, he should do this for you. It shouldn't run more than $350, to have it replaced and he can check for clogs (The price I'm quoting is for standard hours).
You can check this yourself by running the inducer fan without it being attached to the furnace, then attaching it to the furnace. If you notice a significant reduction in airflow, then you have a clogged secondary heat exchanger. I've run across this situation before on this particular model. The owner recenly replaced the inducer motor, but couldn't figure out why he was still having problems. I suspect the clogged heat exchanger contributed to the inducer motor to failing previously, and feel It would definitely be worth checking while you have the fan removed to help eliminate any future problems that could result from this, including heat exchanger failure. The manufacturer of this unit actually recommends you clean the secondary heat exchanger every year, but this is overkill if your furnace was installed and set up properly. I'd recommend doing it every 10 years and you're at that mark now. Instructions on how to do this are in the manual for this unit if you have it. Otherwise, e-mail me at wheels38_97@yahoo.com and I can send you a copy.
Finally, check the limit and flame roll out switches after replacing, as they could have tripped when the motor failed.
Oct 22, 2010 | Heating & Cooling
I get 4 blinks it say open limit switch what does that mean
Your induce fan motor senor is out. The little fan motor that take out the heat has a sensor that tells the furnace thats its working. Some time it get stuck. Try blowing and sucking into the tube. you should hear a click
www.fastacservice.com
Oct 16, 2009 | Goodman GMS90703BXA Heater
Heat not coming on carrier gas pack code 31
code 31 indicates pressure switch did not close or reopened during the heat cycle....1st thing to check is the inducer motor,,this is a small motor that turns a small blower wheel that draws the exhaust gases through the furnace and blows them into the vent pipe....1st locate the inducer assembly,,most easily identified by the small plastic fan blade that cools the inducer motor as it runs..1st turn off tstat and turn off furnace power switch..then turn on furnace switch,then set tstat to heat,set the temp above room temp by 5 degrees...remove the furnace front cover,locate the inducer motor,,if it isnt turning,but is warm or hot after a minute or so,likely the inducer motor is bad..if it isnt turning and isnt warm after 1 minute,then likely the main control board is bad,,not turning the inducer motor when it should,,,,,if the inducer motor is running,,then the pressure switch isnt closing,, could be a bad pressure switch but more likely there is a problem with the venting...some possible problems that would cause the pressure switch not to close in an 80% eff furnace [metal vent pipe] are: [1] a blockage in the vent pipe,base of chimney,dead bird at the furnace where vent connects to furnace or down inside the inducer assy,accessed by removing vent pipe from furnace....if all clear the chimney could be blocked up inside,,is the draft good when vent is removed from base of chimney?..if furnace is a 90%+ type [pvc plastic vent pipe],,then check the intake pipe at the furnace by removing it where it attaches to top of furnace..is the intake clogged with anything?..then check the intake and exhaust pipes outside for blockages,,including ice/frost/snow at the exhaust pipe outlet..
Jan 26, 2009 | Goodman GMS90703BXA Heater
Urnace fan of some sort runs all the time - set on automatic
If you have it cleaned twice a year they should be able to find this problem. It is one of two thinkgs. There is a limit switch on the fan at the top (inducer) this may be weak and causing the inducer run frequently. The other is there is another limit switch it is a main limit on the fire wall it is also weak and that is why the main blower is running it is trying to cool that limit.
Jan 26, 2009 | Carrier XHB123D X/Y Series Heat/Cool Air...