Ihave a Day & Night Furnace M/N:58GS050-3 Series 301 S/N:Z33A65482. My problem is with no wiring whatsoever landed @ terminal strip fan runs @ high speed constantly.With stat wired up & a call for heat I get no spark,just fan(fan switch -auto). 24vac is present into circuit board from transformer, but drops out to 15.xx @ R & C.If I apply 24v directly to R along w/other wiring,fan stops,but after ignition main burners light,fan never runs.
3 Suggested Answers
  • 16 Answers
SOURCE: Goodman forced air gas furnace not firing
if your power vent moter is not running you should not have have glowing ignitor.Frist the vent moter must close an air prove switch in series with the idnitor .seems you have a stuck air prove switch.Its the one with a hose attached
Posted on Apr 07, 2009
  • 114 Answers
SOURCE: power up unit and thermostat,
You have a short circuit, which is obviously dangerous. Your blower motor is controlled via a 24VAC control circuit, but is 120VAC. The circuit board and gas valve are probably history, but it needs to be troubleshot to determine the scope of the damage.If you remove T stat you will see several colored wires. The red and green wire when touched together should cause your fan blower to run. If that works when you bypass t stat the t stat is gone. The red to white will open your gas valve on your heater. The red to the yellow or blue will start your AC compressor or condenser fan motor. Be careful with the yellow and blue wires as one is actually a neutral and one goes to the AC contractor on your condenser unit contractor. Hope this helps!
Posted on Aug 02, 2011
How do you hook up the thermostat to a Central Electric feh-017ha-04 furnace? Also, where do the A/C wires hook up to the furnace?
The standard color code for the HVAC is as follows....
Red=Hot or 24v
White=Heat
Green=Fan
Yellow=A/C
White 1=secondary heat.
Blue=Spare
Orange=Heat Pump
C=Common
The thermostat has the terminals marked R,Rh,W,G,Y.
The furnace should have a terminal strip with similar markings.
If you only have 1 control transformer this will be easy.
Hook the wires up using the colors I have listed. If you don't have the same color wires go with whats close to them....such as use Orange for Red etc. It really doesn't matter as long as they are landed on the same terminals on the thermostat and furnace. Two wires running to A.C unit outside put one on Y the other on C. If you need any more help let me know!
Jun 02, 2014 | Intertherm Heating & Cooling
Pleasureway Traverse furnace fan runs when funace is off.
Bad/ stuck fan relay or temerature sensor is not shutting the fan off. Or there is a short on the low voltage fan control circuit. Check to see if the Green terminal is jumpered to the Red terminal at either the furnace control board of the 'stat, if not, ohm the wires with both ends off- I've seen installers accidently shoot a staple thru the wire and short the wires together more often than even I can believe! Hope this Helps! PS Some furnaces have fan switches inside the furnace- check for one and see if it's "on"- sounds too simple, but sometimes the "simplest" is the correct answer.
Mar 22, 2013 | Heating & Cooling
Ac/fan stopped cooling/blowing/ i hooked up red & green wires and fan blows. now what?
Just to understand what you are saying; You are hooking a wire between the R terminal & the G terminal on the fan control board and the fan runs. When you turn the fan on by the thermostat is does not.
Assuming that you have 24 volts at the G terminal (or wire) at the air handler/furnace when the fan does not run, I would have to say, based on the information that I have been given, that you have a bad fan control board.
Nov 20, 2011 | Heating & Cooling
Never got an answer to ? on a new goodman board #B1809913S. I want to know where to hook up the a/c circuits, yellow for t-stat =cool, and the cond wires. there is no terminals on the board for these...
Most of the time you would hook it up to Y on the furnace terminal strip. G would you to G which is Fan control....... But if you don't have a terminal on the furnace you can hook up the yellow wire from the thermostat Y directly to the condensor wires from the AC and the other wire from the condernsor to C common ternimal........ just make sure that the blower fan comes on with the AC or it won't cool.
Jun 26, 2011 | Heating & Cooling
I what to wire two lights up in garage from a consumer box in my garage do i go from box to switch first or light first,
You take a 2 conductor w/ground "romex" cable from the distribution panel, where the breakers are, to the switch box first. Then run the cable to the lights. You strip off the ends of the cable in the switch box and land the black wires on either screw terminals of the switch. Use a "twistlock" connector and connect both white wires together. Take a separate ground wire, about 6" long and twist it to the remaing ground wires. Terminate the 6" wire to the switch ground screw. At the lights, land the black wire to the black wire or dark screw, whichever you have. Land the white wire to the white wire or light colored screw. There should be a green wire from the light it will land with the ground wire.
Feb 20, 2010 | Dryers
Furnace lights fan comes on then fan goes off furnace stays light until overtemp takes it out code flashes 4
Have some one hold the bottom door safety switch, turn furnace on wait until heating fan relay clicks, and check at terminal (Heat) & terminal (neutral or where all the white wires are located on the control board) for 115 volts to 120 volts. If voltage is present replace blower motor, if voltage drops out while running then replace control board.Turn power off to furnace, open bottom door and feel blower motor with hand, if motor is real hot replace motor. you can not oil this type of motor, it has to be replaced along with the compacitor. Good luck.
Jan 22, 2010 | Goodman Furnace Draft Inducer Blower ...
I have a honeywell thermostat model # th5220d1003-0636 & need to know what connections to make for gas forced air heat.
This is a Focus Pro 2 heat,2 cool thermostat. If you are connecting this to a single stage(1 heat) residential furnace then your connections are: At the thermostat the R and Rc therminals are internally connected so you can connect your R terminal wire from the furnace to the R terminal at the thermostat(this is your 24 volt supply for both heating and cooling. The W or W1 wire (heating) from your furnace you connect to the W1 terminal at the thermostat. The W2 wire from your furnace(if your furnace is a 2 stage furnace) you connect to the W2 terminal at the thermostat. The G wire from your furnace(indoor fan) you connect to the G terminal at the thermostat. The Y1 wire(cooling) from your furnace you connect to the Y1 terminal at the thermostat. The C wire(common or neutral) from the furnace you connect to the C terminal at the thermostat.
Nov 14, 2009 | Honeywell Programmable Thermostat Heater
I need to know how to rewire my heil air conditioner 6 wires are lose?? they are red white orange black red and purple!!!! Model number ph5036akb4
the wires at the thermostat????...this can be very tricky because the colors could mean nothing...every installer can wire it differently...if they used one continuous thermostat wire it's not too bad....you have to go down to your furnace and look in the fan compartment or wherever the thermostat wires enter the furnasce....generally a brown wire with 5 wires colored inside....find the wires where they connect to the furnace circuit board , terminal strip or fan centre and write down all wires and their corresponding terminals...for example...Red wire is on "R"white wire is on "W" and they may not match their color....thats ok.....then connect them at the thermostat accordingly////if you only have 4 wires you will require the jumper wire between RH & RC ...if you have 5 wires...remove the jumper or ignore that....good luck :)
Oct 31, 2009 | Heating & Cooling
Electric Furnace Trips Breakers
it is normal for a breaker that is run right on the edge (50 amp and your furnance to use 45) to get weak after a while . the first thing you should do is change the breaker with the same type and amp rateing . it should take care if it
Jan 16, 2009 | Heating & Cooling
No y connection on furnace module to connect a.c. This is on a goodman model gmp075-3 furnace. I bought the b18099-13 replacement module and still no y terminal. I dont know were to land the t-stat...
"Y" terminal at the stat feeds condensing unit outside, common from the condensing unit to common on the furnace transformer.
"G" terminal on the stat brings the fan on for air circulation. In cooling mode "Y" terminal also brings the fan on. If this furnace was not A/C ready check the VA capacity of the transformer. Should be about 40VA. Make sure there is a fan relay to bring the fan on in the cooling mode.
May 01, 2008 | Heating & Cooling