Question about Cutler Hammer BR120AF BREAKER CIRCUIT BR 1 POLE 20 AMP
Cutler Hammer 20 Arc Fault breaker for bedroom outlets will not reset after activating test switch.
    Sniper:
  • 66 Answers
The circuit breaker must be turned to the "off" position first from the middle position, and then to the "on" position. The cutler hammer arc breakers carry a lifetime warranty so if it will not reset you may want to contact the manufacture.
Posted on Oct 26, 2010
SOURCE:
Chaf vs braf breakers
Hi Will,
I am an electrician and can help you with this problem.
The panel should have a label that provides the catalog number of the panel. Many labels also detail all the breaker types that the panel has been tested with by UL, FM or other recognized testing laboratory. It is a violation of the electrical code to install any breaker into a panel that it was not designed to accept - even it it fits or can be "made" to fit. This means if it is not listed as an acceptable breaker, it must not be introduced to the panel.
The BR20 AF and CH20 AF are both "Combination Arc Fault Circuit Breakers". This means either device is capable of interrupting current flow when either: (1) an over-current condition exists, or (2) when an arc fault is detected regardless of load.
The fronts look very different:
The BR20 AF circuit breaker above.
The CH20 AF circuit breaker above.
These breakers are NOT interchangeable. The CH series has fully exposed clips to engage the relatively flat (or flush) powered buss bar of the panel, while the BR series has a slot in the body that accepts a thin (blade-like), raised powered buss tab of a completely different style panel.
You should replace the breaker only with a like type, arc fault breaker. A similar looking, ground fault breaker is NOT a replacement for this breaker.
I hope this helps and good luck!
Oct 31, 2012 | Electrical Supplies
THere is no electricity in the bedrooms and I can't get them back on?
If the circuit breaker will not reset - all the way off and then back on with a click sound. Then something you have plugged into the outlets in those rooms is probably shorted causing an over current condition. If the circuit breaker won't reset, shut off all lights and then unplug EVERYTHING and then see if it will reset. If it does, then replug everything one at a time until the electricity goes off again, that is the bad apple.But if it won't reset, then your breaker is probably bad. Yes, they do go bad, just infrequently.
Jan 11, 2012 | CUTLER HAMMER BR4040B200V BREAKER CIRCUIT...
Arc fault breaker trips when you turn florescent and can lights on
Sounds like something is wrong with the light check the wiring. Unhook the light and try ther breaker if breaker does not trip then problem is in the circuit.
Jul 24, 2011 | Cutler Hammer "CUTLER HAMMER" ARC FAULT...
Is it normal for BR115AF breakers to feel warm to the touch (130 degrees f) with amped loads of .6 and below? This was found on a presale home inspection.
Nope, at .6 it should be at ambient temperature. I suggest powering down the panel and check for loose connections(which will also cause a rise in temp)
If you are not comfortable doing this then get a qualified electrician to check it out.
Jun 16, 2011 | Cutler Hammer "CUTLER HAMMER" ARC FAULT...
Bought a Eaton Cutler Hammer Arc Fault 15 amp Single Pole circuit breaker for my old CH20 model Cutler Hammer CB Box (vintage about mid 1960s). CB package says "Use in Type CH" boxes. It...
I used to run into that being a service electrician all the time Smains! These problems can involve a little more legwork to figure out than some. The best advice that I can give you is, if at that age you can still find a part number on the breaker panel (they renamed them load centers to sound fancy lmao), if you can actually fine a legible one. Write it down and go to Eaton's website, then to load center. They have a parts number search that should take you right to your PANEL lol, and all the specs. I'm not there or if do it for you, hope this helps!!!
Aug 18, 2017 | Cutler Hammer "CUTLER HAMMER" ARC FAULT...
Our circuit breakers keep tripping. The house is only 12 months old and our electrician says the builder installed Cutler Hammer Combination type AFCI is the problem. Is there a problem with these being...
They can be defective, but usually not. It is usually something that is plugged in that will not operate on the arc fault circuit. Brush type motors are bad as they are actually arcing at times. Unplug all devices, and try to find the culprit. These are for your safety, and once you find the problem devices you should be fine.
Sep 09, 2010 | Cutler Hammer "CUTLER HAMMER" ARC FAULT...
I have a question
Sounds like the breakers are mis-wired. This is a common mistake with those kind of breakers. The white wire that is permanently attached to the breaker (usually coiled) connects to the neutral bar in the panel. Look closely on the breaker, you will see two terminals. The white (circuit) wire that goes out to load connects ONLY to the neutral terminal _on_ the breaker itself, _not_ to the neutral bar in the panel.
Dec 17, 2009 | Cutler Hammer "CUTLER HAMMER" ARC FAULT...