Goodman furnace model #GPO 125_4 REV 8 Installed 6/2/2002
Going out on high temp. This is a list of things all ready checked
check list
1- Blower running right direction
2-A-Coil clean
3-Replaced high temp switch
4-Replaced gas valve
5-Heat exchanger no rings pop lose
6-Heat exchanger looks good from top side,Removed blower
  • charo2 Jun 11, 2008
    Check temp. at high limit switch ,230 in 4 min.
    vents open
    intake open ,removed filters
    Question;What does goodman use to seal the ends of the
    heat exchanger at the transducer motor
  • charo2 Jun 12, 2008
    1st. let me THANK you for your help.
    I thank it could be the burner flame
    Gas pressure to high from gas co.or
    wrong orifice for altitude.
    I will take burners apart an check them
  • 1,420 Answers
Have you measured the temperature in the suppy plenum? Should be 140 to 160 max. If hotter, you have a blockage in the ductwork or vents closed. If within spec, bad circuit board.
Posted on Jun 10, 2008
  • Chandler Ede
    Chandler Ede Jun 11, 2008
    Typically if you are refering to the inducer motor, nothing. Are your exhaust temps real high? More than 200 degrees? Is the board flashing any lights? Try this link for a troubleshooting guide. http://www.dnmech.com/furnace_info_older...
My goodman GMVC95 furnace circuit board is flashing On 6 I replaced the flame sensor but it's still flashing. Does it have to be manually reset?
Alright, have you checked the low voltage fuse on the circuit board in the blower compartment? Make sure you check the roll out switches as well. If all of these issue appear to be fine then you may have a bad circuit board. There has been a bad batch of circuit boards going around many of the popular furnace brands this winter. Trane Gas Furnaces and Goodman Gas Furnaces have been effected. We sell both brands and have had to replace many circuit boards on new furnaces. Trane Gas Furnaces Installed Goodman Gas Furnace Installation Gaithersburg
Feb 03, 2018 | Goodman Heating & Cooling
No heat from furnace, Goodman GMPN080-4 Rev A. Cycle is solid red status light, then 3 flashes indicating open pressure switch because the inducer fan does not come on.
Jimbo, it sounds like you are aware of the operational sequence to suggest using a voltmeter to check the actual wires going TO the combustion air fan...if there is no voltage from the board, the board is bad. Just make sure one of the high temp limits are not open... one may be in the blower compartment on some and one will be near the top of the vestibule and a roll out switch should be near the burners. They should all be wired in series.
Always check the manual reset safty switches as the first step in troubleshooting.
Nov 21, 2015 | Goodman Heating & Cooling
Have a gmp125-4 furance blower runs all the time checked themostat wires error code 1 blink then 2 then 3 then 5 furance works if you turn power off turn back on when heat kickes off blower comes on gives...
Sounds like limit switch issue. Furnace heats up, high temp limit switch opens, fan will stay on. GMP model is older and do not have the codes.
May be over fired, have airflow problem, to cause the limit to open.
Next time before shutting off power, try to find the limit, it has two wires that connect to a 1.5 x 2 inch card mount to the furnace fire wall. tap on it and see if the blower stops. If so replace the limit.
Sep 06, 2011 | Goodman Heating & Cooling
To much air flow..3ton blower..can i slow this down..i know its adjustable..ii hope down..what speed do they come from the factory
Should be able to slow down. Inside bottom door of furnace there are 4 or 5 wires, connected to board and blower motor. White is common. Red is slowest, then orange, blue, black fastest.
1 of these wires should be connected to Air Cond tap, one to furnace tap and 2 to unused taps.
If you are currently running furnace, connect red wire to heat tap. Make sure unit does not get to hot. Should be able to hold hand on Metal duct above furnace without getting to hot. Temp coming out of furnace should be around 35 to 60 degrees higher than temp coming into furnace. Actual heat rise temp is listed inside top of furnace rating tag.
Jan 17, 2011 | Goodman GMS90703BXA Heater
What is the model number for the Draft Inducer Motor Goodman GNP075-2REVB Furnace
I think you must mean GMP075-2rev8 check this link for parts listing:
http://site.famousparts.com/goodman/PDF/RP-169C.pdf
Johnstone supply which has many locations in many cities sells Goodman and stocks parts, and available mailorder http://www.johnstonesupply.com/corp/Default.aspx
Feb 18, 2010 | Goodman Furnace Draft Inducer Blower ...
Blower will not shut off
check the settings on automatic fan control check fan control is clean on the back , check humdifer stat is not set too high ,if fitted .........
Jan 09, 2010 | Goodman Furnace Draft Inducer Blower ...
Goodman furnace GSM100-4 model has constant ligt blinking. Will fire all burners and in few seconds shut off. Help
for what ever reason, your shutting down on high temp
4 things to check
1 the filter
2. your fan, is it comming on....... to circulate the heat.
3. your hi temp thermostat is bad and needs to be replaced.... it should be a sqaure with two wires
you can just ohm it out to know sometimes orange but it differs some
4. above your fan are the coils, ar5e they clean and free of restriction
Oct 28, 2009 | Goodman GDS80904BNA Open Flame Heater
Goodman furnace
double check your wiring. R terminal on the furnace will provide 24 volts to the t-stat. W terminal in the t-stat will send 24 volts back to the furnace W terminal to turn on the heat. G terminal in the t-stat will send power to the G terminal in the furnace when the t-stat is switched to fan on. Y terminal in the t-stat will send power to the Y terminal in the furnace which in turn will send 24 volts to the A/C outside. The C terminal in the furnace should be connected to the c terminal in the A/C outside as well as to the T-stat. Check the fuse again
Jun 02, 2009 | Goodman GMS90703BXA Heater
Goodman Model GMNT100-4 Auto Power Down and Up until Temp.
Keep in mind all furnaces and circuit boards are not the same. Look on the back of the door to the blower compartment. You should find the list of diagnostic codes. Look up four blinks it should narrow down the problem. Although from the discription you gave it sounds lie the high limit control. When a high limit appears to be acting up it DOES NOT mean that the high limit needs replaced. The high limit just may be doing its job. This means that the furnace is overheating. Check your filters. Are all of your registers open? Is your blower set on the right speed? Is your blower going bad? Is the blower motor capacitor bad? Is your evaporator coil restricted? Just changing a high limit switch does not always solve the original problem!
Good luck....
Apr 01, 2009 | Goodman Heating & Cooling
Furnace won't stay running
1 FLASH
Furnace fails to operate.
• Integrated control module
diagnostic LED is
flashing ONE (1) flash.
• Furnace lockout due
to an excessive
number of ignition
“retries” (3 total)1.
• Failure to establish flame.
Cause may be no gas to
burners, front cover
pressure switch stuck open,
bad igniter or igniter
alignment, improper orifices,
or coated/oxidized or
improperly connected flame
sensor.
• Loss of flame after establishment.
Cause may be
interrupted gas supply, lazy
burner flames (improper gas
pressure or restriction in flue
and/or combustion air
piping), front cover pressure
switch opening, or improper
induced draft blower
performance.
• Locate and correct gas
interruption.
• Check front cover
pressure switch
operation (hose, wiring,
contact operation).
Correct if necessary.
• Replace or realign
igniter.
• Check flame sense
signal. Sand sensor if
coated and/or oxidized.
• Check flue piping for
blockage, proper
length, elbows, and
termination.
• Verify proper induced
draft blower performance.