Question about Goodman GMS90703BXA Heater
3.5 TON GSH14 GOODMAN WITH TXV
HELP!!! BRAND NEW....COOLS GREAT BUT WILL CUT OUT ON THE HEATING SIDE AFTER ABOUT 10 TO 20 MIN.....ACTS LIKE ITS OVERHEATING OR LINE OBSTRUCTION OR TXV...SOMETHING OF THAT NATURE....2 SO CALLED HVAC COMPANIES NEAR ME CANT FIGURE IT OUT....HELP PLEASE.....
THANKS JEFF
  • Anonymous Nov 10, 2008
    does not heat goob
  • 370000 Nov 10, 2008
    have 3 ton 14 seer goodman heat pump ac works great heat pump does not, had for two years .changed txv two times in summer superheat set at 12 winter have to reclaim freon to get heat to work? and still don,t get good heat this was one of goodmans first 14 seer heat pumps was there a problem with them
If it cuts out on heating cycle only, it has to be the metering device at the outside unit, which i think is a txv for that model. Take the outside unit apart, run it in heat and watch the txv and see how it responds, also check the bulb n make sure its secure....
Posted on Oct 20, 2008
    Problem Solver:
  • 22 Answers
Is it a heat pump? or the furnace cutting out?
Posted on Oct 11, 2008
3 ton heat pump with piston in air handler. After unit shuts down it makes loud fluid flow noise for about 2 minutes
adding a tvx will not help. the sound you here is the pressure equalizing and that has got to happen for the compressor to start again the next time. A tvx will give you a higher efficiency because it can adjust to changing temperature conditions. Only way i know to quiet the noise is to try to insulate the lines better.
Sep 14, 2014 | Goodman GSH130301 Heat Pump, 3 Ton, 13...
Why does furnace heat cut back?
You might try checking your return filter. The new filters (pleated 3 month, ie real expensive ones) cut back your air flow 35% from the amount the regular 30 throw away allow. When air flow reduces the temperatur from furnace increases and can cause inadvertant high temperature limits to trip. If you are using a clean return filter, next you need to physically observe the air inlet side of your cooling coil to see if it is blocking air flow due to being dirty. If you have trouble with seeing the inlet, you might need to get a professional to take the air handler apart.
Oct 29, 2012 | Goodman Manufacturing...
Not cooling as it should
If you have a crushed, kinked, or otherwise restricted fitting in the system, it's possible the cooling may be affected. Pressure readings can be thrown off, and refrigerant flow can be inhibited.
Since the unit is new, you should have a complete parts and labor warranty, so ask the installer what the reason is that the system doesn't provide the cooling you were probably promised when they sold it to you. They should have taken into account the location of the condensing unit, the size and insulation in your house, indoor and outdoor conditions, your geography/climate, and any other load factors before selling you the system.
Jul 22, 2010 | Goodman CLQ36AR49 Air Conditioner
AC not cooling
first off you should have a four ton unit. what is your super heat? is it pulling attic or outside air?
May 27, 2010 | Goodman CLQ36AR49 Air Conditioner
3 ton condensor and 2.5 air handler
I hate to use rules of thumb but 500sqft per ton depending on your windows and insulation. you are probably ok with a 2.5 ton however it will not work with a 3 ton outdoor unit as you have figured out. depending on how long that ac has been in you may want to replace it with a 2.5 ton due to the damage to the compressor valves because of the mis match. or if the indoor is newer and the original system may have been a 3 ton then i would replace the A/H. and be prepared to replace the outdoor if the valves are to far gone. If the trane is a new high effiency 2 and the goodman is just a 10 SEER you may be able to have a txv installed on the trane unit and a kickstart device outside. but only if its a high effiency but their again if the A/C fails you couldnt have a high effiency 3 ton you would have to drop down to 2.5,
Sep 22, 2009 | Heating & Cooling
Goodman 2.5 ton 14 seer with txv. low compressor amps
no it's good,man. LOL. The RLA is a max not a target. What is the RLA for the compressor?
Aug 12, 2009 | Heating & Cooling
Delfield 'New 6000XL 6051 Side by Side Refrigerator
How was this unit originally equipped? TXV? Use only a TXV OF CORRECT size. In refrigeration if you have a 6000btu rating you do not use a 1/2 ton valve you use a 1/4 ton (3000btuh) at most and would need consulting with an engineer to arrive at the correct valve.
SO was the TXV the other fellow replaced an OEM valve? If not this may be the problem as most TXV's off the shelf are designed for walk-in refrigeration Not Reach ins. An OEM valve may be the trouble here.
Now not to stress the TXV but also the compressor (what was the original model?) Make sure it is designed for the particular heat range and size for this application. As you probably know 1 size compressor designs for AC will not be OK on Refrigeration at same BTU rating.
Call Del field and verify what they are using or recommending for this unit. model and Seal no required and the existing model and SN.
Also to my knowledge a receiver is not required and in fact will only add to your trouble. Receivers are for changes (wide differences) in condensing temperature and pressure. Never saw an application for one with a condenser designed from factory for indoor use with either type of expansion device.
If you need Del fileds number email me at farfield@hughes.net and in th subject line enter delfield?.
Feb 14, 2009 | Delfield 'New 6000XL 6051 Side by Side...
Goodman heatpump. Crazy pressure in heat mode
Check the TXV valve on the outdoor unit, it could be stuck closed. We have been experiencing the same problems with the 410 systems and the TXV was the culprit. Good Luck
Dec 19, 2008 | Goodman CLQ36AR49 Air Conditioner
3ton heat pump googman 14 seer
Give me the model numbers on the heat pump and the coil, I would expect its a really poor match.
Nov 11, 2008 | Goodman GMS90703BXA Heater
Goodman GMS90703BXA Heater Logo
363 people viewed this question
Top Goodman Heating & Cooling Experts
Dan Webster
Dan Webster
Paul Carew
Tim Whalen