The 3 amp fuse on the control board of my furnace blows often when the heat comes on and immediately when the A/C comes on. I got a new thermostat. Can the blue and yellow wires for the A/C be switched and cause this? Any other suggestions? Thanks, Jared
  • 3,361 Answers
Yes if the wires are on the wrong terminals the fuse will blow.
Also any short circuit of any wire will cause the fuse to blow.
The yellow wire is typically for the compressor contactor to engage.
The blue wire is typically a neutral wire.
If blue is touching any other wire and it is the neutral wire the fuse will blow.
Posted on Oct 17, 2010
Frigidaire furnace FG6RA 096C-16B comes on ignites starts to blow then 3 amp fuse blows replace it fuse blows as soon as power is on. Help
The problem is in the thermostat wiring, likely it is grounding somewhere between the thermostat and the air handler/furnace unit.
Dec 31, 2017 | Frigidaire Heating & Cooling
Coleman furnace dgaa077bdta
The control fuses keep blowing tells me one or more of the control that operate the control on 24 volts is malfuctioning. Most controls operate at about 5 watts and on a clamp on amp meter normally pull about 0.2 amp (p = current x voltage, 5 watts = 0.2 amps x 25 volts) I install 75 watt 24 volt transformer with a resettable overload to save on fuses. I reset the transformer and quickly go to the controls and determine the amp draw. When I find the one >0.2 amps I found the problem. The things to check is the emergency heat sequencer, fan control sequencer, reversing valve for heat pumps, main contactor on the condensing unit and any other 24 volt control loads. I have had to replace the themostat wire because the increase current for the thermostat wire can cause the entire length of wire to form a long heater and cause insulation degradationa and cause the thermostat wire to short out and blow the fuses.
Hope this helps
Aug 30, 2014 | Coleman Mobile Modular Home Gas Furnace...
My honeywell thermostat will not let the fan blow if it's on automatic
Depends on what type of heat you have...if it is electric, it could be your thermostat (some electric heaters use contactors & rely on the thermostat to switch the fan on). Heat pumps also use the thermostat to switch the fan on in heat & cool mode. Most electric furnaces use a sequencer to switch the low speed of the fan whenever there is a call for heat. Gas furnaces use either a fan/limit controller (if the unit is older) OR a circuit board based on time (after the thermostat calls for heat). SO depending on the type of system you have, it could be a bad sequencer, controller, relay, thermostat, or control board.
Dec 17, 2013 | Heating & Cooling
Goodman furnace GMT115-5B Turn fan to on on
Bypass the tstat first but that's where I'd be leaning.
Aug 14, 2017 | Goodman GMS90703BXA Heater
1993 Goodman gas furnace keeps blowing fuse when first turned on
You can take each thermostat wire off the control board and use a ohm meter and test to ground, should not have any resistance. Another way is turn off power take each wire off the board, then place one wire at back on the control board terminals ome at a time, untill the one you get to the one that blows the fuse. If the wires check out good sometimes the thermostat itself can have a internal short and cause the fuse to blow.
Nov 27, 2012 | Heating & Cooling
Air conditioning wont turn of, error code at furnace appears to be 24 - secondary fuse open?
There is a 3 or 5 amp fuse on the control board inside the air handler.
Disconnect power to the air handler,locate the fuse and replace it with a good fuse.
The fuse is the same type used in automobiles.
You can purchase them at a auto parts store.
After replacing and turning on the power there will be a 5 minute delay before the board and thermostat energize.
After 5 minutes set the thermostat for you heat or ac function.
If the new fuse blows a complete diagnostic must be done to the system.
Apr 24, 2011 | Carrier Heating & Cooling
3 amp fuse blows after three hours on Goodman 4 ton 16 seer pump
I would suspect you have a problem in the defrost circuit of your heat pump. there are a couple of things you can try. first just run the system on emergency heat and see what happens. you could have a defrost board that is shorting when it kicks into defrost. it sends a signal back to the furnace so it will come on during defrost. if you do not blow a fuse as long as you are running in emergency heat, i would suspect the defrost control board. also you could have a dead short in the wire that runs from the "w" terminal on furnace control board, out to the heat pump. keep in mind that any of the wires could be the cause and i am just tying to give you the most common things. your furnace will still run if you unhook all the low voltage wiring out at the heat pump. if you do this and stop blowing fuses. you know it is something on that wiring. goodl luck.
Jan 26, 2009 | Haier Energy Star ESA3183 Air Conditioner
My honey well thermostat keep clicking and I can't program it
If you have a programmable thermostat and it is a couple of years old you will probably have to install a new one. What kind of thermostat do you have? You can turn power off to furnace and then take thermostat off wall and take wires marked r & w and connect them together your heat should come on when you turn power back on. If not you could have blown the 5 amp fuse inside furnace. I would check the fuse inside of furnace. If you take panels off front of furnace you should find a controll board inside that runs furnace.If you have anymore question just reply back to me
Jan 07, 2009 | Honeywell Programmable Thermostat Heater
3 amp fuse blows on a carrier 58mcb furnace board
Hi!!! Does your ac unit work fine?If not check your low voltage problem..You have a low voltage problem check the wire going out to your condensor make sure that they are not touching..Good luck..Check low voltage wires..short in progress..
Jan 04, 2009 | Carrier 52CQ-312-4 Comfort Series Heat...
Trying to put a new thermostat on my furness , my furness is a GSC90904CXA the new thermostat is a Hunter 44110. I need help hooking up the thermostat.
I'm not familiar with that model # but most furnaces are similar. R goes to R (usually the red wire). If you don't have a seperate heat source, like a boiler, the wire needs to connect to both Rc & Rh. Stats usually come with a jumper in place. Then W to W (usually white), G to G (usually green) and Y to Y (usually yellow or blue). Before you make any connections, TURN OFF YOUR FURNACE. If you don't, you'll probably blow the fuse on the control board, or worse yet, blow your transformer.
Oct 16, 2008 | Goodman Heating & Cooling