Question about Empire DV-210-SG Wall Mounted Panel Heater
I have the dvb-1 blower kit on this 4 year old unit and the fan never stops. Thermostat and heater all work otherwise. Fan control switch? Other?
3 Suggested Answers
  • 4736 Answers
SOURCE: Model BP28-BMP-4 Heater will
Sorry you're having a problem. As the Mantis is one of the most efficient vented heaters on the market. In fact, it's furnace rated.
It sounds like their may be a relay problem, but can't be sure. I would suggest that you call Empire Comfort Systems on Monday and ask for either Rich or John in Technical Service. I' am sure that either one can help you with this technical issue. The number is 800-851-3153. Be sure to have the Serial Number of this unit, as well as the Model #, when you call.
Posted on Feb 05, 2011
  • 4736 Answers
SOURCE: Had a problem with the thermostat connected to
Jake, it sounds like the motor coil wiring on the blower that doesn't work may be damaged or has been disconnected.
Regarding the one that is still running. The automatic fan control is located on the bottom of the blower assembly. The fan control is a nonadjustable, automatic type. The fan control will require between 3 and 7 minutes of main burner operation before the fan control "closes" and activates the blower. The blower will continue to run between 3 and 7 minutes after the main burner shuts off, before the fan control "opens" and deactivates the blower. In which case, if it continues to run and run and run, the fan control switch (part # R-2503) may have failed and will need to be replaced. You can order the part from Empire Comfort Systems Tech Service 800-851-3153. Have the Model Number, Serial Number of the heater handy, as well a the Part Number. when you call.
To help you further, I have included a link to the Owner's Manual for that model wall heater. You can download and print it for future reference.
http://www.empirezoneheat.com/assets//EHS/manuals/GWT-%2825,35%29_Manual.pdf
I hope this helped you troubleshoot and solve the problem. Please let me know. Thanks.
Posted on Jun 11, 2011
2002 4 ton Bryant air conditioner shuts off, fan still runs but not cooling is problem in the controls in the attic or in the AC unit or both?
With a non heat pump it is a simple 24 volt AC control circuit. In the attic there is a relay that is actuated via the fan control wire directly from the thermostat. On the thermostat there is an auto/man switch that controls the fan. Manual the fan runs all the time. Auto fan turns on and off with the outside compressor.
If the system is not calling for cool and the fan continues to run the fan relay is sticking. common problem. Sometimes after running for several days the relay will stop sticking if not, replace relay.
If the system is calling for cool and the compressor stops I would still expect the fan to run until thermostat tells the A/C to off. Some compressor units include a safety switch or high-pressure cut-out switch A blocked internal valve bad control board or external fan in outside unit defective no air flow in outside unit.
High pressure cut out not good,
Suggest turning temp max cool and observe. If acceptable cool and the compressor runs without interruption all is good, except for the blower in the attic. Safely check relay in attic blower circuit.
Hope this helps.
Jun 28, 2017 | Bryant Heating & Cooling
I have new blower motor. it dosen't stop running
Could be a bad blower motor resistor,mounted by the blower.
Sep 28, 2016 | 2002 Dodge Ram Pickup 1500
My Bryant Gas furnace model number is 373LAV036095 the pilot light won't light. Gives us indication that the pressure value is stuck??? Sends into lockout mode. Where is the pressure value located in the...
This is a down flow unit. There is no pressure valve on this unit. Here is all the parts on this unit.
1. Manual - reset, when used.
2. Blower and blower motor
3. Relief box also known as a exhaust flue.
4. Gas valve control knob or electric switch, ON/OFF
5. Gas Valve
6. Gas burner
7. Ratting plate
8. Blower door safety switch
9. Blocked vent safeguard tube and switch
10. Gas Manifold
11. Manual limit switch (2)
12.Hot surface ignitor
13. Flame sensor
14. Inducer blower motor
15. Control board with relays and transformer.
That is all the parts. The first thing the heater gets a call from the thermostat to the control board marked W. The board sends 24v to the inducer fan relay which makes and causes the inducer fan to come on now there is a small tube that runs from the inducer fan box to a switch when the switch makes it sends power to the board which proves you have cleared the exhaust flue then the flat surface ignitor starts to glow and then gas valve opens and fires. now if this tube is stopped up the heater will not fire and will lock the unit out. Also if the flue is stopped up with trash it will do the same thing. If you are not familiar with gas heating units you should call a service company out and check out the system there is a lot of things that need to be checked out every heating season as to keep you and your family safe.
Mar 02, 2015 | Heating & Cooling
My blower on my carrier furnace unit won't turn off? a/c or heater doen't turn on.
gas furnace??? check the start capacitor, put unit in ac mode and see if fan comes on(switch fan to on at thermostat) if it does not a fan problem or capacitor problem. when in cooling mode thermostat controls fan, when in heating mode, furnace controls fan
Feb 18, 2015 | Carrier Heating & Cooling
Heater blower stopped working?
You may want to try your fan on all speeds. If it will work on high, you have a bad resistor for the fan motor. ( high speed doesn't go through the resistor ).
If it doesn't work on any speed, I would check the following;
1. Make sure the fuse isn't blown for the fan blower motor.
2. Check, or have checked the wires between the fan control switch and the fan blower motor.
3. Have the fan control switch checked.
4. Have the fan blower motor checked.
I hope this helps you.
Feb 03, 2011 | 2002 Buick Rendezvous
VW Jetta GL 2000, AC - Heater Fan stopped
blower motor or resistor or the blower motor control switch.
Jun 01, 2009 | 1998 Volkswagen Jetta
Electric furnace/heater pump/fan unit won't shut off
There are dip switches on the main board.. When you remove the lower panel on the air handler there are instructions to where the dip switches should be for your units fan control. if the switches are in the correct configuration.. The Thermostat may be malfunctioning or not wired properly. and last.. and most expensive.. the motherboard may also be failing.
Jan 09, 2009 | Heating & Cooling
Blower stays on with new themostat
Check to see if there is a short between the green wire and the red wire. Green is the fan control wire for AC. Sounds like some wires may be touching. How did the old t-stat get fried?
Jan 02, 2009 | Honeywell Programmable Thermostat Heater
Heater no longer works on auto fan, only manual fan
When you call for fan in auto ensure your getting 24 volts at pin on control board, if it is not energizing then there is a problem with the relay.. Before you change out the expensive control board, try the therm..
Dec 09, 2008 | Heating & Cooling
Heating & Cooling Logo
64 people viewed this question
Top Empire Heating & Cooling Experts
paulcarew
rudyjoe
Level 1 Expert
Dan Webster
Dan Webster
Are you an Empire Heating and Cooling Expert? Answer questions, earn points and help others