Have two new 5 ton Infinity air conditioning units with gas furnace in residential installation. Repeatedly getting "change filter" warning. Indicated CFM is 1400 on high cool. This seems low to me. Shouldnt the CFM be closer to 400 to 450 CFM per ton? Could the problem be caused by undersizing the ducts? What CFM is recommended for the 5 ton unit on high? Hank Haeseker, PE
  • Carrier Master
  • 43,501 Answers
Yes, you are correct... the air flow should be at least 400 CFM/Ton for good efficiency. 350/ton if you have a dehumidification mode....
But under 300 is totally unacceptable...
The problem probably is the ductwork.....or check that a number of your vents are not restricted or shut off by dampers...sometimes when balancing a system many of the dampers will get shut down to force air flow to the fartherest areas and this will cause low air flows...
Also take a good look at the return duct...this can cause many problems.....especially if it is undersized.
The problem I am having with all of this is that with the units you have the blower motor is a ECM motor that will make up for many mistakes by move air at higher static pressures and also overcoming many of the problems with undersized ductwork....
So I am also wondering if the motor is not programmed correctly...check that out also...
At any rate the installing company has a responsibility to make sure the installation is working correctly...A call to Carrier directly will get you action....if the original company will not correct the situation then get the name of another company from Carrier and have them send them out the access the system and make a recommendation on fixing it...
Carrier does not want a bad rap on theri equipment so they will often hire another company to fix the job if it is botched up...
Rattle chains till you get you problem corrected!!!
heatman101
Posted on Oct 15, 2010
What could cause carrier fault code 42 besides bad inducer
Could be several causes.
1. Blockage on piping
2. Water in inducer housing slowing down inducer impeller
3. Condensate trap for furnace clogged up.
4. Inducer motor going bad.
5. Leak in vacuum hoses or not connected.
Welcome To the Best HVAC
Oct 09, 2014 | Carrier Comfort 13 Series 1.5 ton 14.5...
It will not say on unit what the kbtu is?
There is 12,000 Btu of cooling per ton. 5 tons = 60,000 BTU
Sep 07, 2013 | Carrier 5 Ton Infinity High Efficiency...
Carrier infinity 80 won't heat
does your burner flame up and then go put two or three times if so
all you have to do is take out the burner and clean all the soot out of it and then wipe off the sensor
Oct 09, 2012 | Carrier Infinity Series Variable Speed...
I have a Coleman/Evcon furnace model #DGU08016UB that has a concern. In my attempt to check my furnace before we need it for the winter; the following condition occurred. Condition: Flashing code of...
jump out pressure switch see if it lights check hose to pressure switch see if they are split or connections are not good ,cut off ends and put back on presure switch.
Sep 21, 2011 | Coleman Heating & Cooling
I just had the furnace installed six months ago and have used the air condtioner over the summer but never the furnace. When I went to change the controls for the furnace use, the blinking ''change...
Hi, sometimes depending if the unit is an up flow or down flow that depends where they put the filter.If you don't have a return grill in the ceiling, then it would be in the bottom of your furnace. I am sure its hard to remove as it is new, but i am sure it is there.Sometimes there is a grill on the lower wall beside the furnace they could have put it in. They may not have installed one? Good Luck, Sincerely, Shastalaker7
Nov 27, 2009 | Heating & Cooling
Residential HVAC - Repair vs Replace? Heat Pump? Two Stage AC?
for 65 dollars i would replace the coil I do however love gas and heat pump combos it will cut your gas bill by about 75% only uses gas below 30 deg
you may want to try a honeywell 8000 stat it has random circulation fan comes on and just circulates the air also used for gas hp combo with an out door sensor and you don't need the fossil heat kit as for the copper if possible replace it due to don't trust any ones soldering as for units the are all about the same look for warranty some replace unit others have life time comp if only going to be in house for 10 yrs hard to recover cost give replacement allowance when sell
May 11, 2009 | Ruud UBHC Air Conditioner
Need a schematic diagram on a trane furnace model blu080k0942b0
Have you checked on the inside of both front panels?
Mar 05, 2009 | Heating & Cooling
Heating & Cooling Logo
89 people viewed this question
Top Carrier Heating & Cooling Experts
Dan Webster
Dan Webster
Bill Long
Are you a Carrier Heating and Cooling Expert? Answer questions, earn points and help others