Goodman gas pack .induction fan comes on but want fire in heat light on circuit board blinks two then off then two
  • Goodman Master
  • 3,315 Answers
Could be the pressure switch not working or the hot surface igntior not working
Posted on Oct 15, 2010
Pressure switch goodman furnace 100-4 blinks three times, installed new switch still wont start.Also does inducer motor start before gas fires??
2nd question first here: Yes, inducer motor (exhaust fan) must run before gas an fire.
MY FOLLOWING ANSWER WAS COPIED OVER FROM YOUR OTHER POST...
I'm going to assume you can operate and understand a VOM, as well as being able to observe the proper safety procedures for performing service work.
In the case of a control board returning an error code for a failing pressure switch, but the pressure switch actually checks out OK, try this:
Test your exhaust fan power leads for power coming in from the board during the first few seconds at the start of the heating cycle. If power is not showing up there, there is likely another circuit malfunctioning somewhere preventing startup. However, if power is showing up there, then deactivate the system and disconnect the exhaust fan power supply leads from the motor. Test the motor's coil for continuity - a failed exhaust motor coil will result in no vacuum for the pressure switch, hence no heating cycle allowed by the control board.
In my case, the exhaust fan actually failed due to a broken coil lead at the binding post to the push-on connector. I was able to repair the coil lead myself - at no cost - hurray!
Oct 20, 2011 | Goodman GMS90703BXA Heater
Goodman gmp0503 unit has status light blinking slowly all the time. The indoor blower wont even come on when you switch from auto to fan on thermastat. The status light says for one blink to check gas...
Take a jumper wire and jump out the R and W terminals on the furnace. The heat should come on. If it does not, you have a bad board. A steady blink indicates no call for heat. You may have either a broken thermostat wire or a bad thermostat if unit fires when you jump it.
Mar 20, 2011 | Goodman Heating & Cooling
Gas will not come on goodman gmnte 120
The exhaust motor starts first andthen closes a small air switch (pressure switch)...if blocked pipe or tube to switch unit will not fire. You can also look at the light on the circuit board for blinks...this will tell you what is wrong. Read bottom blower door for fault codes
May 09, 2010 | Goodman GMS90703BXA Heater
Goodman forced air gas furnace not firing
if your power vent moter is not running you should not have have glowing ignitor.Frist the vent moter must close an air prove switch in series with the idnitor .seems you have a stuck air prove switch.Its the one with a hose attached
Apr 04, 2009 | Heating & Cooling
GOODMAN CMA80905CXBA FURNACE. INDUCTION BLOWER NOT ENERGIZING. GETTING 3 "BLINKS" FROM DIAGNOSTIC LIGHT (LOW PRESSURE SWITCH OPEN). THE A/C WORKS & THE BLOWER FAN COMES ON WHEN THE STAT IS IN...
the pressure switch is closed before the draft motor closes it.the board is telling you that this is not right.pull the wire(either) off of the pressure switch to see if furnace tries to light.if it does,you should replace the pressure switch.
Oct 02, 2008 | Goodman Heating & Cooling
Goodman Furnace m/n GKS90453BKAC
A constant red light (not blinking) indicates that the thermostat is not calling for heat. Of course you know it is but just to be safe, jump out R and W on the board. If it continues to do the same as you indicated, replace the board.
Dec 05, 2007 | Goodman GMS90703BXA Heater
Goodman ac/gas furnace unit mdl. # gmp075-4
i HAD THE SAME PROBLEM, TURNS OUT IT WAS THE FLAME SENSOR, CLEANED IT, AND ALL WAS GOOD
Nov 27, 2007 | Cozy (W352E) Heater