    Is there the way to change the end switch alone keeping the motor or to examine the actuator for possibly not hitting the switch?
    Not exactly as you described. The valve opens and closes following the thermostat all the time. However, its end switch that's supposed to close once the valve opens up, never does so, like with other zone valves. As a result the controller doesn't see the call for the heat and, therefore, the circulator and the boiler/furnace, remain off. I wonder if there is way to replace the end switch w/o changing the motor because I am not sure if I can change the entire head.
    If changing the entire electrical portion (head) takes not much more than taking 4 screws off the base, please let me know that and will gladly accept your solution.
    Thanks. You solution is what i was looking for. I will swap the heads with zone I have little use for now and then get a proper replacement.
    Guru:
  • 773 Answers
I hope I understand this issue correctly.
You are saying, that your zone valve motor runs when the thermostat tells it to run, but the switch does not move, and the valve stays open?
If that is what you mean, then it sounds like either some teeth on one of the gears broke, and or gears have come out of alignment. At any rate, even tho the motor is operating it is not manipulating the valve. The valve is probably okay, but the motorized unit may need replacing.
Posted on Oct 14, 2010
  • Don Reiman Oct 14, 2010
    Most zone valves come as complete units. You will have to go to a plumbing supply to see if they have just the power head in stock.
    If you can get a power head that is compatible with the valve you have, for instance, if you have a honeywell valve, you need a honeywell head. If you have a TACO, you need a TACO head etc. When you go to the plumbing supply, if you can, remove the power head before you go, and bring it with you. If you cannot get a compatible power head the whole zone valve will need to be replaced.
    Remove and replace power head as follows.....
    Shut off the furnace. Make sure there is no power to the head. Drain the pipe. There should be no water in the pipe. This is important. If there is any water, or pressure in the line, you could get burned. So make certain there is no pressure or water in the pipe when you go to change the power head.
    Once you have drained the pipe, you can remove the 4 screws, depending on how old and what make the valve is, and the assembly will come out. You will See the the ball and flange. Now you will be able to see if it is the ball that is damaged. If it is, this is one reason a zone valve does not close. If not there is something damaged in the gear assembly.
    When you put the new head on make note of the dimples on one side of the power head that will line up with the rest of the valve, these make sure you don't put it together backwards.
    Once the new head is on, and secured in place, you may refill your system, and give it a test.
    So basically 4 screws, but you must drain your system.
    If you need to replace the entire unit....
    Drain the system as explained before for the same reasons. Important for safety. remove the power head as previously explained. Cut the copper pipe as close to the valve as possible.
    You will have to sweat in a new piece of copper. Get a repair pipe. It is a small length of copper, that is just big enough to fit snugly over your existing copper.
    Cut a few inches of copper off of one side of where the valve was. sand the existing pipe on one side, flux both the pipe and the valve, and put the valve on one side of the existing copper. There should be a few inches of space between the other side of the valve and the other side of the valve.
    Using a pipe cutter, cut off about 2 inches of copper from the piece you cut off. Sand it, then flux it and put it in the other side of the zone valve. Sand and flux the end of the copper that is not connected to the valve a few inches. Take the repair pipe and slide it over the existing pipe that is not connected to the valve that you just fluxed. This is why you cut a few inches out. So you can get the repair pipe on, then slide it over the 2 inch piece you put into the other side of the zone valve.
    Now its time to sweat it together. Using a propane, or MAPP torch heat the first joint. Heat the pipe all the way around. Once the joint is hot enough, take the solder while still applying heat and touch it to where the joint is. It should **** in the solder. Do this all the way around the joint. Do this to all of the joints making sure the solder has filled the joint all the way around at each joint.
    Once you are done you may put the power head on the valve after it has cooled. it is important that it is cool so you don't melt the gaskets. Fill your system and check for leaks. If you find a leak, heat it up with the torch and ad more solder. Make sure if the leak is at one of the joints of the zone valve, that you remove the power head before heating.
    Once you are sure there are no leaks you are good to go.
    If you have to replace the entire unit, I can give even more specific instruction on how to sweat in the new valve, with illustrations. Just contact me directly through fixya.
  • 767 Answers
Hello my name is Heath it will be my pleasure to assist you. The zone valve power head is probably bad even though the zone valve operates the zone as far as opening and closing if the powerhead is bad then the end switch will not make.
How do I connect a 24v damper motor with 6 colored wires red white yellow green blue black to NO COM NC terminals.
Choose two colors of the thermostat wire, and connect them to the NO and COM and connect them to the zone control board leads for the zone intended. Almost all zone valves spring return open when deenergized. So ensure the zone valve is open with the system is off. At the base of zone valve there is a set screw that needs to engage the damper valve shaft in the open position with the motor in the spring release position. Most zone valve are 90 degree moment from full open to full shut. If you have a Carrier zone valve, they go full open to full shut in 45 degrees of motion. Your open stop need to be set so the valve stops in the full stop position.
To help understand the operation of a zone system, say you have 2 zone system and zone 1 thermostat initiates a heat or cool demand. Zone 2 valves energizes and shuts and zone 1 stays open and allow air to heat/ cool zone 1. If zone 2 thermostat simultaniously initiates the same heat/cool demand, the zone 2 valve opens and both zone heat/cool. When either thermostat is satisfied the opposite zone valve closes and when both thermostat are satisfied both zone valves open.
Hope this helps you understand zone operation. The same works for higher multizone systems.
Jul 27, 2014 | Honeywell Motorized Small Rectangular Hvac...
Tip
Honeywell V8043E and V8043F Zone Valve
You need a new Honeywell Zone Valve and you are confused by the different numbers of the valves. Let me explain a bit to help you sort through the differences.
The first thing is the V8043 number. This number is the same for the straight through two way valve body configurations. The next letter for most heating system zone valves is the one that is confusing sometimes. Usually it will be an E or a F. There are other Letters but they are not nearly as common for home heating.
This is the E valve
This is the F valve
The thing to remember here is that the E letter tells you that the zone valve has the 4 - 18” wires coming out of the motor. And the F letter tells you that the motor has the 5 terminal board on it. They can be interchanges but if you have one type already installed and you go to replace it you will have to do some figuring to know how to hookup the motor correctly. If you replace your valve with the same letter valve you will just be able to hook it up again as it was.
Then, as far as the last four numbers go, they just tell you what size pipe the valve is for.
If you need to replace the zone valve motor you can check the pricing for a replacement motor or complete head, but I have found that many times the best pricing will be to buy the whole valve and then just take the head off of the new valve and switch it with the old one.
http://www.fixya.com/support/r3894275-manual_honeywell_find_honeywell_manuals
on Jan 16, 2010 | Heating & Cooling
Tip
Honeywell V8034F1036 Zone Valve
The Honeywell V8043F1036 zone valve is a simple two way on-off low voltage valve that consists of two parts. There is an actuator that has a motor and an end switch, and then there is the valve assembly that controls the flow of the water.
The valve assembly is normally a straight through design that is built in such a way so that the valve can be installed without disassembly. The simple ball design is such that the ball is suspended inside the valve without touch any metal in the fully open position. This allows the valve to be soldered in the piping fully assembled. Each time the valve is opened and closed the ball is turned slightly which keeps dirt from building up at one spot and creating a leak. This also allows for even wear on all surfaces and therefore this valve virtually does not ever wear out from use.
The actuator contains a small 24v synchronous motor to open the valve and hold it open as long as power is supplied to the motor. When power is turned off the spring loaded return pulls the valve back shut. The power to the motor can be control through any low voltage thermostat. Power consumption is only 7.7va so up to 6 valves can be controlled from one 40va transformer. The actuator also has a manual open feature that allows you to manually open the valve in the event of a power failure. The valve will then return to normal operation when the power is restored.
In the event of an actuator failure the motor or the whole actuator can be replaced without removing the valve or draining the system. The replacement process is very easy and can be performed in a matter of minutes. The process only requires the loosening of two screws and the change over of the wiring.
The V8043F1036 Honeywell zone valve is one of the most common zone valves installed on many hydronic hot water heating systems. This zone valve has been a rock solid staple in the heating industry for many years.
There are some failures in these valves after years of use. The most common things that go wrong are the failure of the motor and the wearing out of the gears inside to the point where they skip and do not open the valve. The end switch will give problems on rare occasions.
Overall after installing hundreds of these valves I rate them as one of the best zone valves on the market. They are easy to install and service. Considering the wear and tear that a zone valve receives the total number of failures seen with these valves is very minimal
http://www.fixya.com/support/r3901905-honeywell_v8043e_v8043f_zone_valve
My gas forced water furnace has a zone stuck in closed position
EITHER ZONE VALVE RELAY HAS A BAD RELAY CUBE OR YOUR ZONE VALVE POWERHEAD IS BAD .YOU CAN GET JUST A REPLACEMENT POWERHEAD ASSEMBLY OR EVEN JUST A REPLACEMENT ZONE VALVE MOTOR . CHECK WITH A METER AND SEE IF YOU HAVE 24 VOLTS COMING OFF END SWITCH OF ZONE VALVE AND ALSO MAKE SURE YOU ARE GETTING 24 VOLTS TR AND TH/TR .
Jan 07, 2014 | YouTube Videos
Tip
Honeywell v8043e1012 Zone Valve
The V8043E1012 Honeywell zone valve is one of the most common zone valves installed on many hydronic hot water heating systems. This zone valve has been a rock solid staple in the heating industry for many years.
It is a simple two way on-off low voltage valve that consists of two parts. There is an actuator that has a motor and an end switch, and then there is the valve assembly that controls the flow of the water.
Overall after installing hundreds of these valves I rate them as one of the best zone valves on the market. They are easy to install and service. Considering the wear and tear that a zone valve receives the total number of failures seen with these valves is very minimal.
on Jan 15, 2010 | Heating & Cooling
I have a Weil-McLain hot water boiler for baseboard heat. The system has one circulator pump. The system has 5 zones - 3 work fine and two are not working. All the zone valves and thermostats are...
Hello.Prob#1 valve has a bad END SWITCH,change the power head,thad brings the circ on when open.Prob#2 try manual overide lever.iS IT TIGHT OR SMOOTH?DOES IT JUMP/SNAP?motor very hot? all bad signs.Change that power head too.The transformers are OK because 1 trans can only run 3 valves max.
Sep 20, 2010 | Honeywell (CT62B1015) Baseboard Heater
I have a red and a white wire but the heater wont
It sounds like you have at least 2 zones in your system. If this is a normal hot water boiler system with zone valves. When you have your thermostat call for heat it closes the 24 volt circuit that then energizes the motorized zone valve for that thermostat. In that motorized zone valve there is an end switch that will close and complete the circuit to the boiler. Zone valves when they start to clog up with mineralization will not allow the motor to go far enough to close the end switch, so then the boiler and circulating pump will not come on. If this is the case then you need to have the zone valve replaced.
Also make sure your wires at the thermostat are connected correctly. One thing you could also check at the thermostat to make sure it works or not is to jumper the 2 wires and see if your system starts up or not. If the system starts up then the thermostat or its subbase is defective. Hope I was of help to you!! Good luck!!
Nov 29, 2009 | Honeywell Programmable Thermostat Heater
How do i install a zone valve in my hot water heater. I need the schematic from boiler controller to the valve. if I tie the first floor to one valve , the rooms (2) will be on the last section before the...
The two zones have seperate supply and returns, correct? If not zoning will not be possible without piping the system in that way. Assuming the piping is correct, for two zones, you will need two zone valves, one cut into each zone. The wiring will vary, but for a 3 wire zone valve, (Taco), power from the transfomer goes through the thermostat, into terminal 1 on the Zone Valve, Terminal 2 on the zone valve goes back to the transformer, (24v common), and also to one "T" terminal on the aquastat (boiler control), and Terminal 3 on the zone valve goes to the other "T" terminal on the aquastat.
For a Honeywell, or other motorized Zone Valve, power again goes from the transformer, through the thermostat and into one side of the motor contacts/wires (depending on brand), the other motor wire goes back to the transformer, (24v common) Then the two end switch contact/wires go back to the T T terminals on the aquastat.
If you are using motorized zone valves, and only 2 of them, the transformer in the aquastat will be strong enough to power them.