I have a fault coming up on my Eden CBX 24 boiler which says Defective Fan/no flame - missing or erroneus RPM signal, what do i do!!!!
3 Suggested Answers
  • 92 Answers
SOURCE: fan is constantly on, flame never comes on
You have a bad ignitor or ignition system part. The system is designed that if the is a failure in the gas heating then the fan runs and doesnt shut of so you will call someone to fix it .They all do this.
Posted on Jul 10, 2009
hvac1960
  • 2133 Answers
SOURCE: Vokera 24/28 Europa Combi Boiler Water
Check sensor whether fix in proper place.
Posted on Dec 02, 2010
I have a John wood GSW water heater, JW317RF that will not come out of "lockout mode". I have reset the water heater numerous times and it will seem like its going to run but never ignites. I have bled it...
id say the draft u feel is normal (if it wasn't fumes wouldn't exit the home) lock outs usually occur when there is a fault to exist in the burner circuit (detected) like the flame proving sensor being defective(very common) or no draft fan running , you ill need to do a little more looking to determine what is needed
May 28, 2017 | Water Heaters
Truck will be running fine, then all of a sudden it will completely shut off. After we wait a few minutes and pump the clutch and make sure it is all the way to the floor it will start, sometimes. S
You need the engine computer scanned for fault codes, i thank you have an ignition control problem like a module or distributor pickup coil issue. These parts whenthey fail should leave fault cdes so get them read.
Next, the check engine light will pause shortly followed by the second digit of the trouble code. For example if the check engine light blinks once and pauses followed by six blinks the trouble code number would be 16. If no code is present the check engine light will stay one constantly. To restart code gathering turn the ignition key to the "off" position, wait three minutes and turn the ignition key back "on" again without starting the engine. Remove the jumper wire once code gathering is complete. To clear code after the repairs have been made remove the negative battery cable for one minute and reconnect.
Toyota Diagnostic Connector
Toyota Code Definition Table
Code 11 Momentary interruption in power supply to ECU (electronic control unit or computer) up to 1991
Code 12 Engine revolution signal missing Code 13 Rpm signal to ecu missing above 1000 rpm
Code 14 Igniter signal to ecu missing
Code 16 A/T control signal missing from ecu
Code 21 Main oxygen sensor signal fault
Code 22 Water temperature sensor circuit fault
Code 23 and 24 Intake air temperature signal fault
Code 25 Air/fuel ratio LEAN
Code 26 Air/fuel ratio RICH
Code 27 Sub-oxygen sensor signal or heater circuit fault
Code 28 No. 2 oxygen sensor/heater signal fault
Code 31 and 32 Air flow meter circuit or Vacuum sensor signal fault Code 34 and 36 Turbo-charging pressure signal fault
Code 35 Altitude compensation sensor signal fault
Code 41 Throttle position circuit fault
Code 42 Vehicle speed sensor circuit
Code 43 No starter signal to the ecu
Code 51 AC signal on; DL contact off (in transmission shifter with diagnostic connector jumped)
Code 52, 53 and 55 Knock sensor fault Code 71 EGR system malfunction
Code 72 Fuel cut solenoid signal fault
Code 78 Fuel pump control signal fault
Code 81, 83, 84 and 85 TCM communication fault
Jun 28, 2012 | Cars & Trucks
MY IDEAL LOGIC 30 HAS FAULT CODE L2 ALMOST EVERY DAY SINCE INSTALATION DEC 2010
is boiler still under warranty?
normal warranty lasts at least 2 years
if so get ideal to send one of their engineers out
L2 relates to flame failure
either boiler has failed to ignite
or
boiler has not detected flame once lit
several causes
failure to ignite
ignition electrode/spark generator
failure to detect lit flame
detection electrode/detection lead
blocked condensate pipe
or defective condensate syphonic trap
you really need an engineer to check these components
Mar 16, 2011 | Heating & Cooling
My worcester bosch 28 si 11 series is fireing up on heating and systematicaly every couple of seconds turning the flame down to half flame then turning back up to full flame and the spark electrodes are...
This could well be a fan relay fault on the pcb, as in if the fan is cutting in and out it's triggering the pressure switch which in turn is sending confusing signals to the ignition and gas valve. Have you removed the controls connector cover and observed the righthand of the two little white boxes in the middle of the control board (pcb) with the boiler switched on? (be careful because it's live i.e DO NOT TOUCH ANYTHING) Is it sparking?
Nov 18, 2010 | Bosch Water Heaters
What are the carrier 8000ts led error codes?
They are listed inside the front panel of the main unit.
LED CODE
EACH OF THE FOLLOWING STATUS CODES IS A TWO DIGIT NUMBER WITH THE FIRST
DIGIT DETERMINED BY THE NUMBER OF SHORT FLASHES AND THE SECOND DIGIT BY
THE NUMBER OF LONG FLASHES.
STATUS
11 NO PREVIOUS CODE - Stored status code is erased automatically after 72
hours. On RED LED boards stored status codes can also be erased when power
(115 VAC or 24 VAC) to control is interrupted.
12 BLOWER ON AFTER POWER UP (115 VAC or 24 VAC) -Blower runs for 90
seconds, if unit is powered up during a call for heat (R-W closed) or R-W opens
during blower on-delay.
13 LIMIT CIRCUIT LOCKOUT - Lockout occurs if the limit or flame rollout switch is
open longer than 3 minutes.
- Control will auto reset after three hours. - Refer to #33.
14 IGNITION LOCKOUT - Control will auto-reset after three hours. Refer to #34.
21 GAS HEATING LOCKOUT - Control will NOT auto reset.
Check for: - Mis-wired gas valve -Defective control (valve relay)
22 ABNORMAL FLAME-PROVING SIGNAL - Flame is proved while gas valve is
de-energized. Inducer will run until fault is cleared. Check for:
- Leaky gas valve - Stuck-open gas valve
23 PRESSURE SWITCH DID NOT OPEN Check for:
- Obstructed pressure tubing. - Pressure switch stuck closed.
24 SECONDARY VOLTAGE FUSE IS OPEN Check for:
- Short circuit in secondary voltage (24VAC) wiring.
31 PRESSURE SWITCH DID NOT CLOSE OR REOPENED - If open longer than
five minutes, inducer shuts off for 15 minutes before retry. Check for:
- Excessive wind - Proper vent sizing - Defective inducer motor
- Low inducer voltage (115VAC) - Defective pressure switch
- Inadequate combustion air supply - Restricted vent
- Disconnected or obstructed pressure tubing
- Low inlet gas pressure (if LGPS used)
If it opens during blower on-delay period, blower will come on for the selected
blower off-delay.
33 LIMIT CIRCUIT FAULT - Indicates a limit, or flame rollout is open. Blower will
run for 4 minutes or until open switch remakes whichever is longer. If open
longer than 3 minutes, code changes to lockout #13. If open less than 3 minutes
status code #33 continues to flash until blower shuts off. Flame rollout switch
requires manual reset. Check for: - Restricted vent
- Proper vent sizing - Loose blower wheel - Excessive wind
- Dirty filter or restricted duct system.
- Defective blower motor or capacitor. - Defective switch or connections.
- Inadequate combustion air supply (Flame Roll-out Switch open).
34 IGNITION PROVING FAILURE - Control will try three more times before lockout
#14 occurs. If flame signal lost during blower on-delay period, blower will come
on for the selected blower off-delay. Check for: - Control ground continuity
- Flame sensor must not be grounded
- Oxide buildup on flame sensor (clean with fine steel wool).
- Proper flame sense microamps (.5 microamps D.C. min., 4.0 - 6.0 nominal).
- Gas valve defective or gas valve turned off - Manual valve shut-off
- Defective Hot Surface Ignitor
- Inadequate flame carryover or rough ignition
- Green/Yellow wire MUST be connected to furnace sheet metal
45 CONTROL CIRCUITRY LOCKOUT Auto-reset after one hour lockout due to;
- Gas valve relay stuck open - Flame sense circuit failure
- Software check error
Reset power to clear lockout. Replace control if status code repeats.
If status code recall is needed, briefly remove then reconnect one main limit wire to display
stored status code. On RED LED boards do not remove power or blower door before initiating
status code recall. After one status code recall is completed component test will occur.
Thanks for Choosing FixYa.
Kelly
Oct 05, 2010 | Heating & Cooling
F4 fault with Vizo Plus 24. Not condensation tube as this was changed to new tube with sensors on ''blue plug'' by engineer last year when I called them out for re-curring F4 fault - new sensors are bone...
Hi, if the ignition module fires or tries to fire 4 times, this indicates the module is faulty and locks out for safety reasons because of an internal fault.The f-4 code sounds like the pressure switch was open due to condensation not letting it fire up, so the switch was ok, so they changed out the tubing. When you re-set the boiler control module, it locks out due to a internal fault. Change it out and you will be back up and running. The electrodes from the module will cause this as they come from the module. Make sure the condensate trap has no blockage at all as this can cause this problem. I am not guessing, I would replace the boiler module control that you have been re-setting. Keep me posted,
Sincerely,
Shastalaker7
Mar 18, 2010 | Heating & Cooling
Goodman unit. when i turn it on the blower fan and the exhaust fan comes on butit does not lite no flames at all. i don't even hear the gas click in.
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Feb 15, 2010 | Intertherm P3RA-048K Air Conditioner
Fan comes one, should hear whooshing of ignition,
Jan 27, 2010 | Goodman Heating & Cooling
Goodman model gms8 will not light fan comes on then turns off
Jan 26, 2010 | Goodman GMS80453ANA Open Flame Mid-Size...
Protherm 100EC boiler not firing up
You likely have a flame sensor problem.
If you can wath the ignition proccess, see if you ever notice a flame. If yes, and it then shuts downm, you have a flame sensor failure, replace the sensor and clean the flame burners and orifices.
If no flame at all, then your ignitor is failing, or you are not gatting gas to the ignitor.
Aug 23, 2009 | Protech Systems FasNSeal FSWMKE4 4" Vent...
Heating & Cooling Logo
50 people viewed this question
Top Heating & Cooling Experts
paulcarew
Dan Webster
Dan Webster
Donni Steen