I have a Clarke 9000 Proffesional Generator. It's equipped with a Merlin-Gerin Multi 9 GFI Circuit Breaker, #23201. The breaker is so sensitive that the slightest power draw on the system kicks it out. I've had the breaker replaced twice, with the same problem reoccuring. Other than bypassing the breaker completely, which I ultimately did myself, is there another fix for this problem?
When activated, the thermostat stays on for about 45 sec. and then kicks out indicating a gfi problem . . . this seems far too sensitive . . . can I override this in some manner?? Thanks, Wayne
You can replace the wall outlet with a GFI type and cut the ac cord end off and install a basic 3 prong for 120 volt system. AC unit controls don't like ground faults and should be corrected. The cord gfi may be going out.
Apr 03, 2015 | Heating & Cooling
Pump does not turn on. there is power to the board but nothing lights up
No power supply to "board" possibly 24vac, or an air type of control, so that the air supply pump is not active. Possibly the power supply to the pump and control board has "popped" the
circuit breaker. Check, the circuit breaker. There may also be a GFI Ground Fault Indicator that acts like a circuit breaker but is more sensitive, especially near water. Look at the receptacle that the motor plugs into. GFI has a test button and a reset button.
Mar 26, 2015 | Jandy AquaLink RS OneTouch RS8 Pool or Spa...
Clarke power washers 150
Need more info:
What fuse? the one at the end of the cord on the pressure washer? Or the circuit breaker on your house?
If it is the one on the cord it may have gone bad. To test replace it with normal plug (non-GFI) and plug it into an outdoor or bathroom GFCI (GFI) outlet. If it still trips that outlet then there is a ground fault in the device which may be minor or major.
If it is a home circuit breaker remember that electric pressure washers use a lot of power - typically 1500 watts. If anything else is plugged in it can trip the house circuit breaker.
Jun 04, 2014 | Garden
How to replace a Bryant GFCB120 Circuit Breaker
If you have a Bryant load center, you can use other breakers in it, including the Eaton GFCB120 GFI since several companies unified their design. The GFI (ground fault interrupter) or GFCI (ground fault circuit interrupter), same thing, may be required for a device you are installing, such as bathroom, kitchen or outdoor fixtures.
The Eaton series includes very clear installation instructions, but if your problem is that they are missing, then all you do is install the breaker in a open slot in the breaker panel, but you have to attach the neutral [white] wire differently. On regular breakers, the neutral goes right to the ground lug in the panel. With a GFI breaker, it goes through the breaker, and then is connected to the ground lug.
Mar 09, 2012 | Eaton Corporation GFCB120 GFI Circuit...
What GFI breaker is compatible with a Challenger Breaker Box
The National Electrical Code prohibits the use of mixing circuit breaker manufacturers and circuit breaker panels by requiring all electrical equipment to be certified (UL Listed, FM, etc.). Challenger breakers are UL listed, as are Challenger panels. All the circuit breakers installed must be made by Challenger and must be approved for use in that particular panel (more on this below). Installing a different brand breaker into the panel causes the panel and the breaker to lose the UL / FM listing. The lack of a listing causes the electrical code violation. Should a fire occur, and the source is determined to be the use of a mixed manufacturer panel / circuit breaker installation, you insurance company may balk at paying a claim.
If you are unsure of the circuit breakers that are approved for use in your panel, look on the inside cover of the door. On it should be listed the manufacturer's name and all the devices that that the panel will accept. Deviating from the list will trigger the loss of listing.
A final thought: Most GFI breakers are much more expensive than a GFCI outlet. Install a standard non-GFI Challenger breaker and feed a new outlet (next to the panel) with a GFCI plug via the LINE terminals. Connect the rest of the old circuit to the outlet's LOAD terminals. The portion of the circuit that is connected to the LOAD terminals are now GFCI protected. Overloads will trip the circuit breaker as usual, but ground fault issues will trip at the outlet instead.
I hope this helps and good luck! Please rate my reply. thanks.
May 11, 2011 | Challenger Circuit Breaker
No electrical power
You must find the reason the main breaker is popping ...
I'd start by unplugging everything and remove all breakers. Turn the main on ... does it pop? If it pops here look between the breaker panel and the end of your cord. Turn the power off - reinstall the first breaker - turn power back on. What happens ... keep doing this until the main or individual breaker pops - investigate that circuit to find your short.
If you get all breakers back in with out popping anything ... start plugging stuff back in. Something is shorting somewhere.
Let me know what you find please.
thanks
a
Oct 06, 2009 | Hilltop Rv 60 AMP CIRCUIT BREAKER CARDED
GFI on cord trips out.
Probable cause is a single pole gfi opposed to a double pole gfi.
* Do not use a single pole GFCI ON A MULTI WIRE CIRCUIT, IT WILL NUISANCE TRIP IMMEDIATELY
Use a two pole GFCI circuit breaker on such circuits.
May 20, 2009 | LG LWHD1800R Wall/Window Air Conditioner
I am looking for a merlin gerin circuit breaker but i cant find out where i can buy it from.
Her ya go:
http://www.drillspot.com/products/160507/Merlin_Gerin_MG24434_Miniature_Multi9_Circuit_Breaker
Feb 19, 2009 | Merlin Gerin MG24434 Miniature Multi9...
LG washing machine trips GFI Circuit Breaker
WASHING MACHINES ARE NOT TO BE CONNECTED TO GFI OUTLETS AND TRY TO CONNECT IT TO A CERCIUT THAT IS NOT WITH YOUR DRYER. (REG) OUTLET.
Jan 02, 2009 | LG WM2016C
Merlin Gerin MG24434 Miniature Multi9 Circuit Breaker Logo
83 people viewed this question
Top Merlin Electrical Supplies Experts
Craig Butler
Craig Butler
Steve
Gene Haynes
Are you a Merlin Electrical Supply Expert? Answer questions, earn points and help others