50,000 BTU input per hour.
Posted on Oct 12, 2010
What's wrong with my furnace?
The relay for the motor is stuck or the points inside the relay are arced closed. Replace the relay.
Apr 26, 2016 | Goodman Janitrol Amana Goodman Janitrol...
My janitrol furnace started to make a lot of noise over the last few days. Could something be loose or does it need to be cleaned?
I hate to say it but it sounds like the bearing in the fan is going out. If your lucky there's a replacement...if not then a new furnace. You will have to have it looked at by a furnace tech.
Its too bad I can't hear the noise then I'd have a better answer for you, sorry.
Dec 30, 2014 | Goodman 66005 Furnace Draft Inducer Motor...
Janitrol GUPS075-3 Furnace burners will not stay lit
The first thing I would do is make sure the flame sensor is clean, this is a metal rod immersed in the burner flame on the opposite side of the igniter. If too much oxidation builds up on it, it will not allow the burner to stay lit. To clean, just turn off furnace and remove flame sensor and clean with steel wool and then reinstall. If this does not solve the problem there may be a problem with the gas valve.
Nov 08, 2012 | Heating & Cooling
I hooked up a coleman electric furnace to a janitrol condenser heat pump . The t-stat wires on electric furnace are red white green and yellow. I added a blue for common off of transformer for digital...
Hi, first of all you need to get a hand full of 5 amp auto type fuses and install one on the hot leg of the 24 volt secondary side of the transformer. Just use 2 female crimp on connectors and put the fuse in the middle of the hot wire. Saves $$$$ on replacing transformers when you have a dead short on the low or high voltage side of any transformer, just a trick of the trade, food for thought. Fuses are much cheaper. On your electric unit, you may not need the common on this to operate the digital stat if it has batteries. This may be your dead short. On the Janitrol condenser, the red is your 24v as you no. They are using blue in place of yellow for cooling. Red is hot, W is heat, G for fan, and blue is cooling on this Janitrol. Keep in mind you are connecting to a heat-pump also, so make sure the wiring is correct. Are you installing this for secondary Heat?? More then likely, the blue common you have added is the dead short as the janitrol uses the blue for a cooling relay in place of yellow. Anyway, use the 5 amp fuse, trick of the trade to save on the transformers. Please keep me posted, as I know know you have this under control.
Shastalaker7
A/C, Heating, & Refrigeration Contractor. Good Luck!
Feb 09, 2011 | Coleman Heating & Cooling
I have JANITROL GAS FURNACE that the MAIN LIMIT
First, replace the limit. What causes a furnace to cycle frequently would be either a malfunctioning thermostat, a shorted thermostat wire, a bad control or the thermostats heat anticipator is not set right.
Jan 30, 2010 | Heating & Cooling
I have outside Goodman-Janitrol furnace and air unit and
two things to try first to get you pointed in the right direction. First disconnect the R or RH wire from the T-Stat. If the furnace turns off (Stops firing w/ fan to turn offabout 90 sec. later) then you more than likely have a bad Thermistat. If it continues to run Pull the R wire from the Furnace circuit board. put door back on furnace if it stops you have a short in the wire. Still Running? Most likely a bad curcuit board. Hope this helps.
Oct 12, 2009 | Goodman GMS90703BXA Heater
Janitrol gup power vent ignition sequence
inducer motor should run for several seconds before furnace lights, this proves the pressure switch and ensures proper ventilation
Sep 30, 2009 | Goodman Heating & Cooling
Janitrol furnace wont ignite
it is probably a bad hot surface ignitor
Jan 29, 2009 | Kitchen Appliances - Others
I have a gmpn-80 janitrol 90% eff gas furnace,it is only 15 months old,my condisation tray is melting and cracked do to heat in which case leaks water all over....why would this be happening?
Most likely the cause is that the furnace is firing too hot. When a furnace is installed and set up, the manifold gas pressure and fan speed has to be set by the technician so that the temperature rise through the furnace is a maximum of 50 deg F (i.e. if air enters the furnace at 68 deg F it come out no hotter than 118). The target temperature rise on any gas furnace is anywhere between 30 and 50 deg F. If the furnace runs too hot, either the manifold gas pressure must be turned down or the fan speed must be turned up to keep in this range.
Jun 28, 2008 | Heating & Cooling
Heating & Cooling Logo
198 people viewed this question
Top Goodman Heating & Cooling Experts
Dan Webster
Dan Webster
Paul Carew
Tim Whalen
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others