Question about MGE Pulsar Evolution 2200 (esv22) UPS System
As soon the equipment is turned on the display indicates "internal fault serv. required". By using the enter pushbutton, the screen shows : fan fault 007 although the three fans runs correctly. I changed also the fans but the problem is still on. The UPS seems to correctly work both with batteries and from AC line.The switching from AC to Batteries and viceversa is ok, the load is constantly supplied. During operations, despite the output voltage is constant the led 20 (green) and 22(red) randomly bounces and the speed of the fans changes a little. Thanks a lot for the help !
5 Suggested Answers
StorminP
  • 64 Answers
SOURCE: When i plug the AC-IN into the UPS, the UPS can
I hate to tell you this, and you may dissagree with me. You will never get an out-put because I think that the ouput diode is shot.
That may be why your dad is not using the unit. Sometimes not knowing what is wrong with the unit, and then pawn it off on someone else to try a figure out the problem. you may well find that it is damaged beyound repair based on cost of repair. Buy a new one.
Posted on Sep 08, 2009
  • 21 Answers
SOURCE: ups temprature fault
From what info you gave me. It sounds to me like it is either too small for the load, or it is in a confined space where heat is building up (UPS has to be outside of a desk office, etc.) or the rectifier is going bad and heating up. I would check to see if it does it by hooking up a small load to it like a radio or something, and if it is in the open, not overloaded then rectifier is bad,I see it alot. I am a Master Electrician and have worked on many UPSs'. Remember that if you keep a UPS loaded to it's full potential (which you shouldn't do) it will get hot. The rule is to only load it up to 80% of it's rating and you will be fine. To find out how many amps it will handle you simply devide the VA of the UPS by the supply voltage. Example: 1200va UPS supplied by 120v. is good for 10 amps. 1200/120 = 12 amps, then it is wise to add 25% more to the watts or amps when sizing them. Also, if it has a cooling fan make sure it isn't blocked by lint and is working, if it isn't working it will get hot fast. Good luck!
Posted on Nov 10, 2009
SOURCE: I have an MGE Galaxy 3000 15KVA which i replaced the batteries.
This is Easy,
MGE software is exclusive to them, they do this so that in the event the UPS needs any work you have to use them for remedial work, the problem is because they hold the monopoly they charge through the roof for parts and labour. you will need a factory trained engineer to turn up with a laptop to switch off the "Maintenance Alarms" I have an engineer that has the Software and availabilty to parts and we are much cheaper than MGE direct.
if you need any UPS help contact Glenn Prince @ Adept Power Solutions Ltd 01264 326726 or go to website www.adeptpower.co.uk
Posted on May 13, 2010
nilutpalsono
  • 238 Answers
SOURCE: My MGE Evolution 3000 ups will not deliver voltage
check the inverter ckt.
Posted on Aug 06, 2010
How do I change the auto settlement time on verifone vx 510
Press 6 then set up, enter password- alpha alpha 66831 enter (alpha key above 2 key) then it will display
phone
terminal
communications
Select Terminal using purple more key or the next key if one displays until you see auto settle time. Press Select- then on bottom of screen you can enter the time using HHMM- military time. if you want to close at 1100pm you would enter 2300 press exit and yes to save, red x until back at main screen. if your screen goes to a default screen that says comm serv and something else, choose the option that is not comm serv and this should take you to a home screen you are used to seeing.
Feb 27, 2015 | VeriFone VX510
Tip
Oldsmobile service light 1991-01
Alero
2000-01
Turn the ignition to the ON position, engine OFF. Press the RESET button and release. The CHANGE OIL indicator will start flashing
2000: Press and release the RESET button again.
1999: Press and hold the RESET button until an audible chime is heard and then release the button.
Intrigue
2000-01
Turn the ignition to ON without starting the engine. Fully press and release the accelerator pedal three times within five seconds. If the CHANGE OIL SOON indicator flashes two times, the system is resetting. Turn the key off after the the light has finished flashing, then start the vehicle. If the CHANGE OIL SOON indictor comes back on, the engine oil life monitor has not reset. Repeat the procedure again. If the vehicle is equipped with the U20 option code, the vehicle as an oil life low indicator. The oil life low indicator shows an estimate of the oil's remaining useful life. When the oil life index is less than 10 percent, the display will show OIL LIFE LOW. To reset the oil life monitor, press and hold the MODE button until the light appears next to OIL LIFE. Press and hold the trip RESET button until the oil life percentage changes to 99 percent.
Alero,
Intrigue,
Cutlass Supreme
1999,
1998,
1996-9
To reset the "CHANGE OIL" light, turn the ignition switch to the "RUN" position with the engine off. Fully depress and release the accelerator pedal three times in five seconds. The light will flash twice and go out.
Aurora
1995-99
To reset the "OIL LIFE" message, press the "ENG" button with the ignition on until "OIL LIFE PERCENTAGE" is shown. Press the "RESET" button for 5 seconds. "RESET" will appear and then "OIL LIFE" will show 100%
Eighty-Eight,
Ninety-Eight,
Regency
1994-97
When "CHANGE OIL NOW" is displayed, press the "RESET" button. Press "SEL" to display "OIL". Press "SEL" to display oil life. Press and hold "RESET" for 5 seconds. A "RESET" message should display with oil life changed to 100%.
Eighty-Eight,
Ninety-Eight
1992-93,
1991-93
Press and release the "TEST" button on the Driver Information Center. This will illuminate "CHANGE OIL NOW" if it is not already illuminated. Press and release the "OIL" or "OIL INDEX" button. Next, press the "RESET" button and hold for at least 7 seconds.
Toronado,
Trofeo
w/o CRT Display
1991
To reset "OIL LIFE INDEX", press the "2 OPTIONS" button: three times if the vehicle is equipped with a phone and compass, once if equipped with neither. While "OIL LIFE INDEX" is displayed, press and hold the "RESET/ENTER" key at the bottom right of the 15 button switch for 5 seconds.
on Dec 07, 2009 | Oldsmobile Alero Cars & Trucks
I bought a house with a Night Sentry Solid State Timer model # EJ341 and have no instructions on setting or programming the unit.
rapid Programming.
1. Move control lever to OFFCLEAR for at least 5 seconds
• red indicator light goes off
• all time settings are
erased.
2. Move control lever to ON.
• red indicator light will start
flashing.
3. Check a clock; then turn pushbutton time dial clockwise at least one click.
• stop at the half hour nearest to present time (note
AM or PM).
Note: When turning pushbutton time dial, do NOT
accidentally PRESS at the same time.
4. Press pushbutton time dial once to enter present time.
• red indicator light goes off (present time has been
recorded).
5. Turn pushbutton time dial clockwise to desired
ON time.
• red indicator light blinks with each click.
6. Press pushbutton to enter ON time.
• controlled light(s) will turn on.
7. Turn pushbutton time dial clockwise to desired
OFF time.
8. Press pushbutton time dial to enter OFF time.
• controlled light(s) turn off.
9. Repeat 5-8 for other on/off times.
10.Turn pushbutton time dial for at least 2 more turns
from the first ON time to complete this program
• red indicator light will turn on and stay on (steady
light means timer is in automatic).
Note: Pushbutton time dial does not turn
automatically after setting to indicate time of day
Aug 22, 2010 | Hardware & Accessories
The screen went black the litte red lite blinks...
the light indicates an internal electronic fault with your set
projection TV`s have integrated protection circuits
built into the circuit design, these circuits turn the
power off automatically when a fault has bin detected this
is in order to prevent a more costly repair, these circuits monitor
power supply , vertical and horizontal deflection
over voltage, or x ray, and also faults with convergence circuits.
Diagnosing these faults require test equipment and a good knowledge of
electronic repair techniques, and also a repair manual.
Apr 28, 2010 | Televison & Video
APC BR1500LCD Fault F01
This is a printout of the fault codes
System Fault indicator is on and all other
front panel indicators are flashing.
Internal UPS fault. One of nine Internal UPS Fault Messages is displayed:
F01 - On-Battery Overload F06 - Relay Welding
F02 - On-Battery Output Short F07 - Temperature
F03 - On-Battery XCap Overload F08 - Fan Fault
F04 - Clamp Short F09 - Internal Fault
F05 - Charger Fault
Nov 23, 2009 | APC BR1500LCD UPS System
Lost my manual for chef condor integra oven - need to check auto functions and how to set them
For TOuch Control oven:
1. Press Finish Time touch pad
2.press ^ touch pad until clock displays the required am or pm finish time.
3. Press Cook Period touch pad.
4. Adjust the cooking time as in step 2, using up and down arrow touch pads. (hours and minutes needed to cook food)
5. Press Automatic touch pad.
Press Fan touch pad to select fan speed. Red indicating light shows normal speed.
7. Turn oven thermostat to desired setting.
8. Press Keep Warm touch pad if keep warm function is required at end of cooking. 9. At end of cooking time a buzzer will sound for 1 minute and the KEEP WARM cycle will now operate until the meal is ready to be served.
10. To cancel the Automatic cycle, press Manual touch pad and turn oven thermostat off.
For Multifunction oven:
1. Set time of day.
2. Turn Function switch to Finish. 0.00 will be displayed.
3. Turn display switch + to give the required am or pm finish time. (an illuminated bar in the bottom left corner indicates when the clock display is pm).
4. Turn Function switch to Cook then turn Display switch to + till desired cooking period is displayed (hours and minutes needed to cook food)
5. Turn Function switch to Auto. The automatic programme is now ready to use.
Turn upper oven thermostat to desired setting.
If keep warm function is required, turn function switch to Cook (optional)
Happy cooking!
Jun 14, 2009 | Ovens
Toshiba a200 laptop Have black screen even tho laptop has booted up, going by the usual sounds.Took battery out and used ac adapter, but same problem.Switched power off several times, left off over night...
You could have a defective screen - follow this to determine the fault.
Defective CCFL backlight, it may have the following symptom:
  • Screen flashs on red/pink and off.
  • Picture stays on in red and slowly be come normal.
  • Picture flickering with dim display.
  • Picture flickering on and off.
All these symptoms indicate that the LCD backlight lamp (CCFL Lamp) has reached the end of the life and all you need to do is replacing the CCFL lamp
Connect an external monitor to your laptop and power it up, if you see the normal Windows images then the video card and laptop is OK and the problem is definitely the backlight.
Dim image and/or dark display on the laptop's LCD screen indicates a faulty LCD backlight and it could be the inverter that supplies high voltage to the CCFL lamp or it is the CCLF lamp is nearly burnt out or burnt out, most likely this is the case.
The inverter can be replaced easily but the CCLF lamp is more time consuming and requires soldering skills.
Check out www.lcdparts.net for parts, repair service and DIY info.
Apr 19, 2009 | Toshiba Satellite A200-0ET00X Notebook
Fan flow error 1611 I/O
The ProLiant DL380 G3 server requires that both primary and redundant fans exist in a specific configuration in order to perform optimally. Any deviation from the specified configuration will cause one of the above error messages to occur and the internal Health LED to illuminate. In a ProLiant DL380 G3 server without the redundant fan option, the server will shut down after the error message is displayed. In a server with the redundant fan option, the internal Health LED will illuminate and the appropriate error message regarding fan redundancy will be displayed. The purpose of this document is to detail the required configuration for both primary and redundant fans.
DETAILS Both primary and redundant fans in the ProLiant DL380 G3 server must be configured to meet specific requirements in order to avoid the error messages above and in some instances, subsequent shutdown of the server.
All primary fan locations (2, 4, 5, 6 and 7) must be populated with a fan before the redundant fan locations (1, 3, or 8) are populated. If a primary fan location is left unpopulated, the server will display one or more of the error messages shown above. In addition, the internal Health LED (the top LED on the front panel of the server) will display the status of the fans.
When the redundant fan option is used, all redundant fan locations must be populated. ProLiant servers do not support partial population of redundant fans. If any redundant fan location is populated without also populating all other redundant fan locations in the server, the fan system will not be fully redundant and one or more of the error messages above will be displayed.
Figure 1 below illustrates a ProLiant DL380 G3 server configured with all eight fans installed for fan redundancy. The server airflow is divided into three zones: processor, I/O and power supply. Shared fans 4 and 7 each provide airflow for two zones. If a shared fan fails, the failure is experienced in both zones.
Figure 1: ProLiant DL380 G3 server configured with all eight fans installed for fan redundancy
The internal Health LED (the top LED on the front panel of the server) indicates failed or missing components. The internal Health LED should be observed to determine the status of the fans as follows:
RED LED: A red LED indicates that the minimum fan requirements have not been met. Minimum fan requirements indicate that all primary fan slots must be populated with functioning fans.
  • If the 1611 fan "x" is not present (where "x" is the fan location) error message is displayed at POST and the internal Health LED is red , then a primary fan is missing.
  • If the 1611 fan "x" failure (where "x" is the fan location) error message is displayed at POST and the internal Health LED is red , then a primary fan has failed.
AMBER LED: An amber LED indicates that the minimum fan requirements have been met; however, requirements for redundant fan configuration have not been met. This means that all primary fan slots are populated with functioning fans, but at least one redundant fan has either failed or is missing.
  • If the 1611 fan "x" is not present (where "x" is the fan location) error message is displayed at POST and the internal Health LED is amber , then a redundant fan is missing.
  • If the 1611 fan "x" failure (where "x" is the fan location) error message is displayed at POST and the internal Health LED is amber , then a redundant fan has failed.
Note: In a redundant fan configuration, the error message fan system not fully redundant will also be displayed at POST if any redundant fan slot is left unpopulated or if a redundant fan has failed.
Nov 21, 2008 | HP Compaq ProLiant DL580 G4 (430811001)...
Computers & Internet Logo
93 people viewed this question
Top MGE Computers & Internet Experts
Jax Planet
Jax Planet
Raj Patel
Are you a MGE Computer and Internet Expert? Answer questions, earn points and help others