Mismatched heat pump
I am running a 3 ton condensing unit matched with a 2.5 ton evaporator. what trouble will I have later on. I also use a hydrocarbon refrigerant charged at 10 degrees below ambient. HELP PLEASE
    President:
  • 2,712 Answers
This will create an overload on the evaporator, and you will definitely see issues along the way - overheating, higher electric bills, poor cooling, just to name a few. In other words, they waste money, electricity, and dont provide the comfort expected.
Best get them matched to avoid future issues which can result in expensive repairs later on
Here is a better explanation I found online:
"One gets higher SEER ratings through several avenues. One of the easiest is through a larger coil. Look at R22 3 ton units at 10 SEER and look at the same tonnage at 13 SEER and you cant help but to notice how much larger the higher SEER is. Greater coil face (hence the larger unit) means more refrigerant necessary to fill the thing. Secondly, higher SEER is also achieved through lower compression ratios (the ratio of absolute pressure discharge divided by absolute pressure suction). Obviously the suction pressure has to remain at a certain pressure/temperature. Thus, we need to lower the discharge pressure - remember the lower the compression ratio (the lower we can get the top number) the more efficient.
If your new coil outside is larger it needs more refrigerant. If your indoor coil is fed by a fixed orafice and the outdoor pressure is lower, the evaporator pressure will be lower without the help of a TXV metering device (the metering device is yet another way to get higher ratings along with Scroll compressors and variable speed motors). Considering that your outdoor unit is larger (needs more refrigerant) and most likely your metering device is not TXV (cant adjust for the lower compression ratio and lower high side pressure) your unit is most likely acting under charged due to the mismatch. Remember, your fixed meter device is looking for a certain pressure behind it and the newer higher efficiency condensor may not provide it. Your unit may very well have a leak; however, I would look to the mismatched equipment first.
Everyone has their opinions on matching coils and changing the evaporator coil and metering device when the condenosr is changed out in a higher SEER rating. My experience from talking to the manufacturers and reading the test results of units PURPOSELY mismatched and tested for performance lead me to make sure they are matched. The test results I have seen show that mismatched equipment will not even give the 10 SEER rating of the original unit - they waste money, electricity, and dont provide the comfort expected.
HVAC is like a see-saw on the playground. Its a balancing act to get the right action out of it. Saying X-tons condensor mismatched to X-tons evaporator is the same as having one real skinny kid on one side of the see-saw and a one really fat kid on the other side. Both are 3 years old - just like the unit halves are both the same tonnage. The 2 kids are not rated or matched the same for capacity all things considered. While its funny to watch on the playground, the same is not funny in your house when you are paying alot of money for equipment and the service it is supposed to provide. Unfortunately, chances are good the unit will not perform to any standard that is worth while in its current configuration."
Posted on Jun 11, 2008
  • Swilin Sampson
    Swilin Sampson Jun 11, 2008
    If you found the advice I provided useful, kindly take a moment to "Accept" my solution. Should you have any further queries, please post back and I will try to assist you further as best I can..
    Cheers!
    IrishDruid
    Brigadier General:
  • 3,614 Answers
Well, it will go on the usual problem.. the lower the capacity and did not meet the standard will be the first got damaged/problem....-0r- it will also be the cause of unexpected shutdown of the whole unit...
let me know...
  • micromaster
    micromaster Jun 11, 2008
    like installing or somehow by example that you will buy a pair of shoes, of course you will not buy different size for each foot...like 9 1/2 for the right & 8 1/2 for the left... and in this i thinkyou will never get a good performance in walking or in runing..
    That's how..
    Sergeant:
    Champion:
  • 230 Answers
The temperature should be maintained within the specified range ,this may be done by the control units so check that carefully
    Genius:
  • 3,587 Answers
Well..this is a load variant issue. Depending on your cooling load, and the voltage input fluctuations(energy in does not equal energy out) you will have the air conditioning equivalent of a mismatched differential in a Jaguar.
If you can limit the coolant temperature range, via the thermostatic control, and keep a close watch on your fluid pressure/levels, you might get away with this.
usually, you want to have this arrangement in a reverse differential.
Posted on May 31, 2008
Why does my A/C condenser compressor turn on and off every 5 minutes?
You need good airflow across the indoor coil, the evaporator. Air warms the refrigerant. If there is no airflow, the refrigerant will come back out freezing cold (in liquid form) and can damage the compressor valves. Before charging any ac unit, good airflow must be checked for across both evaporator and condensor.
Too much, overcharging will cause freezing all the way back to the compressor in a capilary tube type of ac.
Where is it the refrigeration lines are freezing cold?
Apr 28, 2015 | Heating & Cooling
What is the problem with running a 10 SEER condenser with a 13 SEER air handler other than efficiency? I had a 2 ton 13 SEER air handler installed last August to replace one about 27 years old. The...
as most ac units are capillary tube control not tx valve having matched units is critical. as for cost the condensing unit is much more complex and expensive than the evaporator.
Feb 14, 2015 | Amana Goodman R-410A Heat Pump Condenser 2...
2 ton unit
6719f81e-d5d1-47c4-b80f-e11712a6cac5.pngNo oversizing the condenser will not work well, however oversizing the evaporator coil by 1/2 a ton actually increases the units efficiency and is recommended to do by most utilities on units they finance.
Jul 07, 2013 | Goodman CKL36AR36 Air Conditioner
Trying to get info (tonnage seer rating) on a weatherking mod# 10ajb48a01 condencing unit to find a matching evaporator coil and cannot find anything on internet
This is a 4 ton model condensing unit. You can go up 1/2 ton for the evaporator, meaning a 4 1/2 (A) coil will work just fine and allow a bit more cooling capacity.
Sep 10, 2011 | Weather King 12AJA4801AH Air Conditioner
I am removing a 3 ton condenser and replacing with a 31/2 ton condenser . The evap coil is a 3 ton with an expansion valve with a 11/2 ton to a 3 ton rating. Will i have any problems. The 31/2 ton unit is...
Yes you will have problems you can go up a 1/2 half ton on the coil but not with the condenser don't do it you will regret it even with an expansion valve.
Jun 21, 2011 | Heating & Cooling
What is the HP rating if a 3 ton air conditioner?
Hi, this depends on the compressor that is installed in this unit. It may be a Copeland scroll, a Tecumseh, its hard to say. Most compressors are around 2 hp for a 3 ton unit. On the data plate it will tell you the h.p. of the blower and condenser fan motors such as 1/4 h.p., or 1/3. If you can get the name and model numbers from the top of your compressor, you can call a a/c, Refrigeration parts house, wholesale and they will have it in there manuals. The B.T.U. rating for your compressor is 36,000. There are 12,000 BTU's per ton of cooling, this is something that almost no one knows, but now you do. If it were a smaller unit such as a 2 and 1/2 ton, it would be 30,000 B.T.U.'s. You can look at the model number of a unit and you will see numbers like this, 024, 2-ton, 030, 21/2 ton, and 036 a 3 ton unit and so on. Your compressor alone will be in the range of a 2 horse unit, which ever the brand of compressor they installed in it. Please don't forget to rate me on this as I know you will be kind. I will be here if you ever need help on repairs or trouble-shooting your unit in the future, just use my user name below.
Sincerely,
Shastalaker7
A/C, Heating, & Refrigeration Contractor
Sep 04, 2010 | Heating & Cooling
I have a 3 ton split system using a Rudd 3 ton condensing unit model UAHE036JAS . The compressor is going bad and I would like to replace it with a new condensing unit operating on R-22 . I do nt want to...
Only if they are still available in your area. Goodman still has a few R-22 units left in Texas the last I heard and that is only if your local supply stores can order them. They are getting to be far and few between since they have stopped making the equipment. You might also get a second opinion, a lot of companies are just trying to benefit more by replacing everything, but you could still have a R-22/410A compatible indoor coil and copper line set, they just have to use a flush kit to get all the old refrigerant out of the system. 410A is easily contaminated and runs at a lot higher pressures, that is why they want you to replace everything, but there is still hope. It will save you a little money just having the system flushed and replaced with 410A condenser, but only if compatible. Hope this helps and good luck!
Aug 19, 2010 | Ruud UBHC Air Conditioner
Does the orifice, which needs to be installed in the inside unit of an a/c for a house, come with the outside condenser? I had an a/c system installed and an orifice was never installed. the original...
The orifice is the metering device inside the evaporator coil and comes installed from the factory in the coil itself. Some condensers do come with orifices taped to the side of the unit, but they only do that to ensure you have the right size orifice. Sometimes you will have a 3 ton evaporator and a 2.5 ton condenser. In this case you want to change the orifice so that it meters the refrigerant correctly. But if you have a 3 ton condenser and a 3 ton coil, which is normal, you don't have to do anything. So to answer your question, your coil already came with a orifice inside and nothing needs to be done unless there are two different sized units as described above. Hope I didn't bore you too much and helped you with your question!
Aug 19, 2010 | Goodman CKL60AR60 Air Conditioner
I have a Ruud Model # UACC-036JAS. Any idea on
Hi, yes the number you are showing me 036 indicates its a 3 ton unit. For every ton of cooling, you will have 12,000 btu's of cooling. 36 divided by 12=3 ton unit. Its showing me also its a Ruud Handler 2.0 ton which would be a Model# UACC-024JAS? If your mobel number is the one you gave me, UACC-036JAS, this is a 3 ton unit, absolutely no questions. I hope I have been of help to you. I am a licensed air conditioning / Refrigeration /Heating Contractor. Let me know if I have been of help.
Sincerely,
Shastalaker7
PS If this is a split system with the indoor air handler and condenser outdoors, both coils must be the same tonnage for it to work for you properly. You can't have a 2 ton indoor evaporator coil with a 3 ton condensing unit.
Jun 28, 2010 | Ruud Handler Air Conditioner
Rudd 2 ton 10 S
The small copper line should not be really hot its supposed to be carrying liquid refrigerant which has already had the heat "pressed" out of it by the compressor and carried of by the air flowing over the condenser coil. This could indicate a few things; that your unit is overcharged, you have a mismatched evaporator coil and condenser, an ineffective condenser fan motor or a clogged condenser coil and as a result your compressor is shutting of due to an overload condition from the building heat and back pressure between the compressor outlet and the evaporator inlet.
First make sure your condenser is clean and that adequate air is flowing over the fins of the condenser coil. Then be sure your equipment is a matched system. A indication that your condenser fan motor is not at speed is slow starting a humming sound and excessive heat. In my experience this complaint is generally the result of a bad condenser fan motor that over heats and shuts of after a short period and the build up of heat in the liquid refrigerant line of course trips the compressor overload circuit- which by the way usually takes hours to reset. I hope you've already resolved this, but in case you haven't......
Aug 01, 2008 | Ruud Matching Split Air Conditioner
Heating & Cooling Logo
148 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen