The fan comes on, the burner ignites and then goes out withing 3-5 seconds. Fan continures to run another 30-60 seconds then it too shuts off. Also want to know if this furnace has a filter. We could not find one and I live in my trailer in an area that is very dusty.
  • 24 Answers
The flame sensor is bad. It is a simple replacement, although the style is a bit different from manufacturer to manufacturer.
Posted on Oct 09, 2010
Janitrol GUPS075-3 Furnace burners will not stay lit
The first thing I would do is make sure the flame sensor is clean, this is a metal rod immersed in the burner flame on the opposite side of the igniter. If too much oxidation builds up on it, it will not allow the burner to stay lit. To clean, just turn off furnace and remove flame sensor and clean with steel wool and then reinstall. If this does not solve the problem there may be a problem with the gas valve.
Nov 08, 2012 | Heating & Cooling
I have a Johnson air ease 90 plus.I turn the thermostat up and exhaust blower comes on igniter comes on and i can hear the natural gas release for a second or two then igniter shuts off along with gas. Fan...
If the burners come on for a few seconds and shut off check the flame sensor near the burners and clean it with steel wool, usually this will fix the problem. The flame sensor is a metal rod that is immersed in the burner flame on the opposite side of the igniter. robhvac47_7.jpg
Jan 17, 2011 | Heating & Cooling
My furnace fan will turn on as if the furnace is going to run, then the pilot lights the burner but with in 3 seconds it shuts off. Could this be due to a bad thermostate
Hello
No i don't think your stat is bad as the unit is trying to run.There is a temp run switch in the plenum of the unit that could be causing this problem.
Its located in the metal box on top of the heater,it may be mounted externally also.
What this does is it senses air temp and tells the fan to run or not run.
You may also have a post ignition problem causing the burner to shut down.
Nov 26, 2010 | Heating & Cooling
Hello, I have an achiever 90 plus ruud, when I turn it on the flame ignites but after 3 seconds it goes out, it does this 3 times than turns off. Help?
Are you saying that main burner is coming on or pilot /hot surface ignitor or spark ignitor ? If your induced draft motor is coming on then a few seconds later your main burner is coming on for 3 seconds and then shutting off but blower motor is not coming on I would look at flame sensor to make sure it is telling the fan motor to come on. Normally they will try three or four times and then lock out. One easy way to check blower motor is to set your thermostat to fan on. Fan motor should come on and run till you shut it off.hope this help you.
Nov 05, 2010 | Heating & Cooling
William forshaire 435 runs well for awhile until
Try cleaning your thermocouple,and resetting it where was, which is located at the pilot flame. this should solve your problem.
Feb 23, 2010 | Heating & Cooling
Have a Goodman GMT070-3B which the vent motor seems to be sticking. I took apart and cleaned the brushes and reassembled. The furnace will come on only after what seems like the vent motor comes up to...
The whole assembly must be replaced.
The sequence of operation is -
Combustion fan purges the heat exchanger. A pressure switch verifies combustion air fan is running. Usually a 30-45 second purge before the hot surface ignitor glows, or the spark ignition starts.
Gas valve opens after 10-15 seconds and main burners light. Control board monitors for flame and shuts gas valve after 2-3 seconds if main burner does not light.
If burner does not light, some boards repeat this for 3 tries, then locks out and is reset by cycling power.
Air blower comes on after another 30-45 seconds after main burner ignition.
Times may vary based on the specific controller board. A flow chart and timing sequence should be located somewhere on the unit, usually in the fan compartment.
Dec 16, 2009 | Goodman GMS90703BXA Heater
No ignition and E04 Code
The HSI (ignitor) has 2 wires, its like a cigeratte lighter, power is applied and it heats then glows red, the single wire you mention is the flame sensor, used by the control board (igntion module) to ensure the burner has lit or it shuts the power to the gas valve off but keeps the fan operating for a period of 1 hour till it resets.
It sounds like your ignitor is defective, it happens often, depending on your location, you may be able to purchase one, but I would advise having a service tech do it.
The manual for troubleshooting and repair can be found at this link:
http://www.staritepool.com/pdfs/MiniMaxNTServiceManual.pdf
Aug 14, 2009 | Pentair MINIMAX NT TSI IGNITER
Riello 40 F5 oil burner, on boiler, intermittently running
with a forced draught burner the fan motor would be checked via a pressure switch. if the pressure switch is not set correctly or the fan is too weak the contacts will not be made in the switch and the burner will lockout. if the damper is not open enough when the fan runs then the air supply will be too small for the switch to make. check to see if you have a capacitor on the fan windings if this is faulty then the fan will fail intermittently.
Jan 19, 2009 | Heating & Cooling
Heating & Cooling Logo
15 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Donni Steen