Question about Chicago Pneumatic Air Tools & Compressors
Iam runing 94 ft to an out building , and need a 100 amp service to a sub panel what size wire do I need. line is going under ground
  • 98 Answers
SOURCE: AC Breaker trips and AC Fan turns slow.
Sounds like you have a bad capacitor for your squirrel cage fan , now as for the a/c unit sounds like you have a direct short in compressor to ground or leg to leg , check all wiring to make sure that it is not grounding out or melted together.
Posted on Jul 23, 2009
co7196
  • 3433 Answers
SOURCE: 220 VAC, 25 amp service line for a 50 ft long
8 ga on the 100
10ga on the 50
Posted on Nov 12, 2009
  • 760 Answers
SOURCE: I am installing a sub panel in a detached building
You could use 6/3 with ground. You must take an equipment ground conductor along with your current carrying conductors. Still drive a ground rod at the building, and add a seperate ground bar in the sub panel. Connect your equipment grounding conductor from main building along with the equipment grouding conductor to the ground rod. Do not bond the neutral in the sub panel to ground. Be aware you will still have some voltage drop, so a 220V air conditioner might be better.
Posted on Sep 24, 2010
  • 56 Answers
SOURCE: what size aluminum electric wire do I need for 90
Number 2 alu it is good for 90 amps
Posted on Sep 30, 2010
  • 5245 Answers
SOURCE: how to wire a 100 amp sub panel
Copy following link:
http://waterheatertimer.org/How-to-install-a-subpanel.html
If you need further help, I’m available over the phone at https://www.6ya.com/expert/gene_9f0ef4df2f9897e7
Posted on Sep 12, 2012
What size wire is needed for 100 amp, under ground service
It depends on the regulations of your district, and the line voltage, AC or DC.
Just as an example only, it may possibly be 3 x #4 conductors for the service wires, and a #5 ground conductor. But you need to check with the authority.
Mar 01, 2017 | Car Audio & Video
Wiring diagram for three phase power with two 200 amp service boxes inside building
This work requires a license (or qualified person) everywhere that the National Electrical Code is enforced.
If you're asking how to wire a single phase 200 amp panel from a larger, 3 phase panel of the same voltage - ONE way is to install a 2 pole - 200 amp breaker into the 3 phase panel. Provide 4 correctly sized conductors with the correct insulation in a cable or conduit between the 3 phase panel and the 200 amp single phase panel. Two of these conductors should be black and red (for 120/208 volt system) and connect to the 2 pole - 200 amp circuit breaker terminals, the third should be white and connected to the neutral bus bar. The forth should be green and is connected to the neutral bus bar as well but *only if* it is "service equipment" If it is a "main or sub panel", the green wire should be connected to the ground bus bar. The other end of the conductors should be terminated in a "main lug only" 200 amp panel. The back and red connect to "line 1" and "line 2" bus lugs, the white to the neutral bus bar that is NOT electrically connected to the panel enclosure (do not install the screw or strap between the bar and enclosure). The green must be connected by installing a separate bar that is securely fastened both mechanically and electrically to the enclosure for ground connections.
There is a great deal going on here - and plenty of variables that can change how to do this work, safely and correctly. This is an example of just ONE of many different ways to do the work for a particular installation. There is no one way that works for all situations. If your situation does not support this method - you will have an unsafe installation and subject the building and people in it to a dangerous fire / safety hazard.
Please, consult a licensed electrician before attempting this work.
Nov 17, 2011 | Square D Qo 200 Amp 40 Circuit Indoor...
How do I run from a 100 amp main panel to a 60 amp subpanel, 125 from my house to the garage
See 60 Amp sub-panel image
Above image shows drawing of 60Amp sub-panel located next to main panel. Drawing shows #6 wire... 125' distance to garage calls for #4 wire. I ran #4 to my barn and have no problems.
Give thought to how many new breakers you want at garage.
See photo of subpanel that holds three 240V breakers
Using drawing as a guide. Replace existing 240Volt breaker with new 60 Amp breaker. Two hot wires connect to new 60 Amp breaker. Neutral connects to neutral busbar.
More space: You can free up space in main breaker box using a tandem breaker. Or by doubling up 2 lightly used 120V circuits onto one breaker. Do not double-up on 240 Breakers
Conduit: You want PVC conduit large enough to fit three #4 wires. Bigger conduit is easier to pull wires ... and maybe later ethernet wire, or alarm wire etc.
Ground wire: You can put a ground rod at garage and run #6 bare copper between sub-panel neutral-busbar and ground rod. Attach ground wire firmly with grounding clamp.
I want you to check with local electrical supply for exact code in your area concerning conduit requirements, grounding, and wire size. Tighten all lugs very tight against wire.
Oct 03, 2010 | Siemens 100 Amp Main Breaker Renovation...
I am installing a sub panel in a detached building from my house. Which is 100 ft away. I plan to have four separate circuits. One that will service a ceiling fan and 3 for plug ins that will only run a TV...
Sep 10, 2010 | General Electric GE ELECTRICAL TQD22200X2...
Jul 23, 2009 | Goodman CLQ36AR49 Air Conditioner
Need wiring diagram for sub
u should have two pos, an two neg. on the back of the sub run a wire from one pos to the other same with neg. now just run a pos an neg from the box to one side of the sub u should have one side with two wires runing to the pos. an neg. if u need more help let me know bertman285@hotmail.com
Apr 25, 2009 | Car Audio & Video
12 inch subs emit engine noise
You will have to go buy noise filters for the headunit. This will stop engine noise
Jan 31, 2009 | Precision Camera Precision Audio 12-inch...
Water heater ground
You have clearly lost your ground due to PVC. One solution would be to run copper ground wire from the hot water tank to the metal splice on each end of the PVC. It is not necessary to go all the way back to the breaker box.
Jan 23, 2009 | Water Heaters
Fuse keeps blowing when sub volume is turned up
the amp draw rating on the amp is 100 you need to put a larger fuse in, such as a 150 amp, it would be a good idea to go to 0 ga but not needed. you might also want to upgrade your altenator.
Nov 29, 2006 | Jl Audio 1000/1 Car Audio Amplifier
Open Questions:
Air Tools & Compressors Logo
65 people viewed this question
Top Chicago Pneumatic Air Tools & Compressors Experts
John Trevino
Ronny Bennett Sr.
Ronny Bennett Sr.
Are you a Chicago Pneumatic Air Tool and Compressor Expert? Answer questions, earn points and help others