Question about Cross Furnace Draft Inducer Blower 115 Volts Fasco # A064
Tempstar GUJ100N16A1 I think the limit control is not working. Blower won't shut off, came on even with furnace off. Replaced old termostat with Hunter brand. 2 wire heat only. Seems to be working. Can't get blower to turn off without turning off of power to furnace.
Tempstar DC90 pilot light or burner keeps going out. The furnace will run continuously. Even if I turn heat off at the thermostat. I have to kill power at the panel box to get it to shut off. Then I've...
The reset button near the ignitor is a high temperature limit safety switch. When the furnace gets too hot and the manual reset limit switch is tripped, it most likely goes into a 'safe' mode where the gas control is locked out electronically and the blower is made to run continuously to rid the heat exchanger of the excessive heat. This will continue until the reset is pushed and the power is cycled off. It will remain an endless cycle unless the reason for the overtemperature condition is not corrected.
Your furnace 'temperature rise' is getting too high due to a lack of air across the heat exchanger for whatever reason. Some of those reasons could be a restricted air filter or a blower motor that's cycling improperly on its internal winding thermostat. You could also have a dirty air conditioner 'A' coil (evaporator) on top of the furnace restricting the air flow. Nevertheless, you are going to have to have it serviced by a reputable service company's technician to correct what's wrong.
Nov 13, 2014 | Heating & Cooling
Janitrol gmp gas furnace ignitor troubleshooting 125 blink
if it is shutting off abruptly the limit is either wired wrong or set wrong. If the fan comes on and blows the flame out there is a hole in your heat exchanger which can result in fire or carbon monoxide poisoning. Have an experienced tech take a look at it to be safe.
Nov 25, 2017 | Heating & Cooling
Coleman furnace running, won't shut off, blowing cold only
Hello, the blower will run continues if 1) the limit switch has tripped 2) the relay on the intergrated control board is stuck Try tapping on the control board and let me know if it shuts down.
Nov 04, 2012 | Heating & Cooling
Tempstar DC90 willnot shut off
I can't stand the tempstar smart valve! Now I'm not sure what a dc90, but if you have a gas fire residential furnace I know what it is. The smart valve controls gas and flame proving only. The blower issue is probably one of the high temp safeties that has stuck. During a call for heat, your system verifies that all safeties are closed. If this sequence is not correct, then the unit assumes that the unit has overheated due to a high temperature safety issue, and brings the blower on to cool it down, normally for 90secs. Also if the unit is calling for heat when the power is turned off, still calling for heat when power is turned back on(like you said by throwing the switch), this will also bring the blower on for 90sec, then blower will/should turn off, and the heat cycle will start. So if your tstat is calling for heat(heat on and set temp higher than accrual temp), and you turn off power then turn power(main voltage) back on, this will bring blower on for 90secs. Now, the burners staying on is a different issue. I've not seen that in 15 yrs of service on a smart valve. There is probably 24volts feeding the "W" circuit, for some reason. On the control board there is a terminal block with R W G Y C. The W is your heat. This W receives a 24v signal from your tstat. Turn off power, remove W from the board, then turn power back on. If no heat then you've isolated your problem to the control wire coming from your tstat, or the tstat itself. If it continues to heat with W disconnected then its something in the furnace, circuit board? Hope this helps!
Mar 04, 2017 | Null Heating & Cooling
Unit does not stay lit
A few questions for you. If the thermostat is satisfied as in turned below room temp, does the blower shut off. Are the filters clean? Furnaces have a limit control that governs how hot the heat exchanger runs. If the limit switch opens for some reason the fan or blower will continue to run until the limit switch closes. So dirty filters? A very dirty blower wheel? A blower motor that is not coming up to speed, Could just be a bad limit switch that is opening up at a lower temperature than it should. I would also check the pressure switch sensing tube. The end could be blocked with deposits
Sep 06, 2017 | Heating & Cooling
Gas furnace with Honeywell smart valve code error 6:2, replaced the following: pressure switch, smart valve, ignitor flame sensor and control board. Cleaned out the condensate line. Still getting 6:2 flash...
Hello, it sounds like your Furnace might be shutting off due to your high limit switch.A limit switch will open when the furnace overheats due to low airflow, . check air filter, clean blower wheel, and check to make sure the blower wheel is running at proper speed and not dragging sometimes cause by a weak capacitor. Anything that restricts airflow will cause a limit switch to open.
Mar 08, 2011 | Honeywell Heating & Cooling
My heater will kick on right away but after 3-5mins it stops producing heat then a few mins later it will start heating again. Why?
The furnace could be shutting off on High Limit ...means your furnace is running too hot...check your filter and make sure return air vents are clean and clear....also it can be the Heat anticipator in your thermostat...which controls how many times your furnace cycles...basically your furnace should come on and off 5-6 times/hr ....need more info on your type of furnace and type of thermostat
Oct 19, 2009 | Holmes Products HCH4062 Ceramic Compact...
My heater turns on the gas starts but then it shuts down
Try to locate the red and white wires either behind your thermostat or on the furnace itself. Jump them out and see if the furnace stays on. If you do it at the furnace you will need to hold the door switch down. If it runs fine, you have found your problem (the thermostat) if it goes out again, the furnace will display a number of blinks on the circuit board. Look on the reverse side of the furnace access door and there should be an Error Code chart to get you started figuring where to look next.
Nov 10, 2008 | Goodman GMS90703BXA Heater
Cross Furnace Draft Inducer Blower  115 Volts Fasco # A064 Logo
169 people viewed this question
Top Cross Measuring Tools & Sensors Experts
Vuk B
Tom Chichester
Are you a Cross Measuring Tool and Sensor Expert? Answer questions, earn points and help others