Question about Ruud Central System Air Conditioner
Furnace ignites properly but blower does not come on. The lower blower compartment door has a switch on it when you take the door off the blower starts and runs but its not doing that now. The blower works because I can turn thermostat to on and it comes on it just doesnt come on after the burners have ignited when Ive switch it to auto
  • 3 more comments
  • bessfletchal Oct 06, 2010
    Where is the relay located and is there a way to test it
    Ok the fan works when I turn the switch on the thermostat to on it comes on. When I turn it to auto it doesnt come on after the burners light. Now when I used to take off the door on the bottom of the furnace the blower would come on even if the furnace wasnt running now it doesnt could it be the switch on that door when I push on the switch I can hear a humming when I let off it stops.
    THE FAN MOTOR IS NOT THE PROBLEM IT WORKS THE FURNACE IGNITES CORRECTLY BUT THE BLOWER DOES NOT COME ON. IF I SET THE THERMOSTAT TO ON IT BLOWS IF I SET IT TO AUTO IT DOESNT
  • bessfletchal Oct 07, 2010
    With the thermostat set to heat and blower to auto the blower doesnt come on after the burners ignite. However if I have it set to ac and the blower set to auto it comes on when the ac comes on. So Iam thinking it has to be something to do with what ever tells the blower to come on after the burners have ignited.
  • Rusty Entrekin Dec 23, 2012
    It may be a stuck fan limit control switch spring. Remove it's cover and rotate the dial back and forth to loosen the spring.
    President:
  • 2,777 Answers
Can you switch it to heat and still get the same result? It sounds like the actual main controller me be to blame here.
Let me know,
Thanks
TIm
Posted on Oct 06, 2010
  • Tim Grayson
    Tim Grayson Oct 07, 2010
    It is the same mechanism that tells the fan to come on with AC as it does with HEAT.... so the mechanism must be malfunctioning. It is the control unit of the furnace, and it sounds like it needs to be replaced.
    Thanks
    Tim
  • 3,600 Answers
Be sure the fan on the thremostat is set to auto for the fan to come on, if that does not work force it to manual if it does not work then you have a problem with relay for the fan.
Our Gibson KG7TC060D24B "tries" to start, but the shuts off before ignition. Technicians have replaced the control panel and other components but the problem persists, with the furnace working for a few...
This is possible, however it is possible they are missing something simple. I hope you can follow along.
1) Is this a Sealed Combustion Furnace, meaning you cannot get to the burners even after you remove the Door Panels?
2) If yes, is this furnace vented with pvc/plastic piping?
3) If yes, do both pipes go outside?
4) If yes then try this.
1) Turn the main power off to the furnace
2) Remove the Door Panel to the burner section.
3) Turn Furnace back and turn the thermostat all the way up.
4)Look into the burner compartment and tell me if the igniter glows red. If it does and the goes out with the burners not coming on.
5) If you feel comfortable or know of someone that is.
6) Turn the furnace off, remove the panel that conceals the burner compartment.
7) Turn the furnace on, if the igniter glows red and the burners ignite. Your problem is in the venting system. Most likely the intake pipe if it goes outside. It could be plugged or something is blocking it. If the burners do not ignite the next thing to make sure that is happening is that the Exhaust blower is operating and you can feel air outside where the pipe terminates. If you it is but no very strong, then your problem could be the inducer motor or to small of vent pipe.
If you could, send me some information about how it starts up
1) Main blower may come on and shut off, make sure the blower runs in on position 1st then back to Auto position. If it does not, you have another problem.
2) The Exhaust blower should come on next
3) About 17secs. later the igniter should glow red.
4) You will here the gas valve make a click
5) The Burners will ignite
6) The flame sensor rod on the far left hand side of the burner will keep the burner lit. If it is dirty the burners will shutdown.
7)About 90secs. later the main blower will come on.
Oct 26, 2013 | Gibson KG7TC060D24B 60,000 BTU 95.1% Gas...
Furnance fan works,but the burnrs won't ignite
Hello my name is Heath it will be my pleasure to assist you. First thing to do is go to the furnace and look in the small peep hole in the lower blower door and see if there is an led light that is flashing a certain number of blinks record the number and look for a diagnostic chart on the inside of the blower door or the upper side panel of the furnace if there is no flash code present you can try resetting the power to the furnace and see if the furnace will fire up.
Sep 19, 2011 | Heating & Cooling
I am having a problem with the furnace not always starting and locking out after 3 tries. However, if I leave the door off, the furnace works fine. I suspect the pressure switch called "Front Cover...
Hello, The first thing to check is the door switch on the furnace. it is located behind the blower compartment door. Turn off power to the unit and disconnect the wires going to the door switch, use a multimeter and set it to ohms, place each meter lead to the terminals on the door switch you should read infinite ohms, if not replace the switch. Let me know what you find.
Feb 06, 2011 | Goodman GMS90703BXA Heater
My heat will not cycle on the blower motor continues to run even if I turn my thermostat off. I have pulled the disconnect out twice and I still can't get the blower to turn off .Gas burner won't ignite....
One thing to try is to remove door from blower compartment and see if that shut the blower off, There should be a switch on the edge of the furnace frame that is turned off when the door is removed. Also look in the burner compartment and see if you can locate a small silver fuseible link close to burners. If your furnace has this then use ohm meter to check across it and if it reads open then temporarly jumper it . Put blower door back on and see if this stops the fan running. Not all furnaces use this link but it one easy thing to check. Hope this helps. Thanks
Dec 07, 2010 | Heating & Cooling
Furnace will not come on after changing filter. Is there a safety switch on the covers?
There is a switch on the blower compartment cover that needs to be closed to make your furnace work. It should be located on top frame of blower compartment, Make sure you have the cover properly closed. Hope this helps you. Thanks
Nov 22, 2010 | Goodman Furnace Draft Inducer Blower ...
I can hear the heater come on but the fan will not start
It would help to have more information on your heater, age and brand.If it's an older unit it may be a bad limit switch. on both old or newer it could be a bad blower motor or motor start capacitor.On newer models flame sensor may be bad and not leaving burner on long enough to start blower. Sorry I can't be more helpful. One thing you can try is to remove front cover on furnace then cover on blower compartment. Check to see if blower turns freely. Reinstall blower door making sure it is in proper position as most models have a switch on top frame of furnace that must be closed for blower to work. Also check on your thermostat and see if it has a fan or fan on position. If it does switch to that position and see if fan runs.It would help to diagnois if you would time burner when it was on. Hope this helps some. Thanks
Nov 06, 2010 | Heating & Cooling
Furnace blower won't stop running
Usually when the furnace blower motor runs all the time
The limit switch or rollout switch is usually open or bad.
The furnace board is seeing that one of those switches is open, so it brings the blower on to try to get the heat out of the combustion chamber area, so the switch will close. But if the switch is bad and won’t close, the furnace board will keep the blower running continuously.
Jan 04, 2010 | Amana Comfort Zone 12M32PBEH Air...
Coleman furnace -- fan runs, ingniter won't light,
The chances are that the furnace was running when the power went out. This will cause the high limit switch to cutout and needs to be manually reset.
You will find that switch in the blower compartment near the blower. Usually somewher near the highest point of the cabinet.
Push the little red button firmly till it clicks.
When the power goes out while the furnace is running the heat builds up because the blower shuts down immediately and causes this limit switch to cut out.
If you have a electric tester you can also follow the low voltage circuit till you find the open switch. Ther is usually a wiring schematic on the door cover of most furnaces.
I hope that this will help you to solve your problem!
Thanks for using Fixya!!
Heatman101
Dec 09, 2009 | Coleman Propane Forced Air Heater...
I have a Trane Xe-60 furnace about 19 years old. During summer months, with thermostat set to deliver air, the outside condenser runs, but furnace blower does not. I can move thermostat lever from auto to...
THIS IS A COMMON PROBLEM WITH THE DOOR SWITCHES, MY FIRST ANSWER WOULD BE REPLACE THE SWITCH SECOND WOULD BE OPEN THE DOOR AND PUSH THE BUTTON IN AND SEE IF THE FURNACE WILL WORK. THIS SWITCH IS JUST A DOOR SAFTEY IF THIS WORKS. I HAVE TAPED A PIECE ON THE INSIDE OF THE DOOR WHERE THE SWITCH WILL HIT THE DOOR ABOUT A 1/4 INCH THICK AND SEE IF THIS WILL GET YOU RUNNING UNTILL YOU CAN GET A SWITCH
Oct 12, 2009 | Omega Trane Furnace Draft Inducer Blower...
Blower on colman gas furnace will not come on. (have no gas yet)
I'm not a furnace technician. But I have worked on several Coleman trailer furnaces. So keep in mind that my terminology might not be exactly correct. But I think I can help you.
I don't know what model you are running, but most of them run pretty much the same. You have a four basic components to check. Thermostat; Ignition Control Module; Pressure Switch; and which ever of the following that you have (Glow plug, Electronic ignition, Pilot Light).
I'm assuming that you are referring to the blower as the "Rat wheel blower" (round wheel looking thing with fins on it). If my assumption is correct and if the power from the breaker box to the furnace junction box (Probably with a on and off switch on top or side), than when you give it power (from breaker box and turn thermostat up) the fan (not blower) comes on. If it doesn't there is a probably a problem with your Thermostat or Ignition Module. If it does come on and your glow plug or you igniter tries to work. Than yes, you are correct, you have to have gas pressure to let the pressure switch know that there is adequate gas supply pressure (gas- 5 to 7 W.C, propane 11 to 13 W.C). The reason for this is if the Pressure Switch doesn't feel the correct pressure. It thinks you have a leak and won't release gas for ignition. After you turn the gas on. If the furnace doesn't ignite. Make sure the Thermostat is definitely wired properly. Now we are down to one of three problems. If the Glow Plug, Electronic Ignition, or pilot light are working properly. Than we are down one of two problems. The Ignition Module or Pressure Switch. Check pressure on the Pressure Switch. If yuou don't smell gas it is probably OK. But it is best if you use a manometer. I have rarely found Pressure Switches bad. Normally if I get to that step. It is the Ignition Module. The Ignition Module kind of like the brain of the furnace. It is located behind one of your front panels. It will have approximately 10 wires going to it. Some will be going to the Thermostat, some to the Glow plug (Igniter), some to the Pressure Switch, and some going to the blower.
I have probably said more than you need to know. If I did I apologize. But to wrap it up. You were probably correct. You definitely need gas for the blower to kick on. The furnace has to light and heat up before the blower will Start. Not to keep rattling, but to check to see if the blower motor will run. Is to switch the Thermostat from "auto" to "run".
Good Luck
Nov 17, 2008 | Coleman Propane Forced Air Heater...
Ruud Central System Air Conditioner Logo
369 people viewed this question
Top Ruud Heating & Cooling Experts
Donni Steen
Bill Long
Tim Whalen
Are you a Ruud Heating and Cooling Expert? Answer questions, earn points and help others