Question about TORK Variable Cycling Timer 8601
Im installing a TORK 1103.. Im hooking this timer up to 4 outlets.. I have a black, a white, a red and a copper wire.. my problem is I have to turn the timer on and off manually.. The clock is not working.. help!!!
  • 1 more comment
  • leepipino Oct 06, 2010
    Thank you for your quick response... How would i wire it without the red wires being that they are connected to the outlets.. its a split 20 20 breaker... and i need to hook up the 4 outlets.. so getting rid of the red wires how would that work?? Thanks again
    Thank you for your quick response.. Im now wondering how to wire it without the red wires.. as the red wires are connected to the outlet.. Im on a split 20 20 breaker.. Thanks again
  • 5,603 Answers
Your power feed hot should connect to the black, the neutral to the white and the load should tie to the red. The neutral of the load will also connect to the white. The bare copper is the safety grounDING conductor and should tie to the grounds within you box and also to the grounding (green screw of the receptacles). I would NOT use this timer if you do NOT have grounds in the box or metal conduit to the boxes.
Posted on Oct 07, 2010
  • Fred Yearian Oct 16, 2010
    Here is a site with the diagram you need:
    http://www.weisd.com/store2/17wire.pdf
    Use the schematic in the upper right corner.
    Please note you CANNOT feed this with a split breaker because you CANNOT share a neutral with a split breaker. You will need to feed this from a double breaker, not a split breaker.
    The two line inputs MUST be from opposite sides of the line for the 1103. The motor will not run unless they are.
  • 10,865 Answers
Hello Lee. The black wire is hot 110 volts. the red is hot 110 volts. the white is neutral and the bare copper is ground. IF you are only hooking up 4 outlets, only use the one hot wire [the black] do not use the red. Joe
Posted on Oct 06, 2010
I'm looking for help. Installing a Woods 59007 timer. It has 4 wires, red, black, green, white. My current electrical setup is a black, white, and ground wire in the box. How do I hook this up? T
Hook all the white wires together.
Hook all the greens or bare copper wires together.
Hook your hot black to the timer black.
Hook your black wire that goes to your light to the red switch wire.
then try the switch if the light doesn't work switch the red and black switch wires around black to light red to black power.
Oct 19, 2014 | Woods In-Wall Digital 5-10-15-30-Minute...
Wiring 15312 timer
You are asking about GE 15312 timer.
Open following link for exact single-pole wiring illustrations:
http://waterheatertimer.org/How-to-wire-GE-15312-timer.html
May 30, 2012 | GE Hardware & Accessories
I the manual wiring doesn't match what I have in the switch box. This switch is to operate 2 outside porch lights., previously wired to a single pole switch as follows.. one black wire to one screw and 2...
I test these timers.
GE 15071 timer has internal clock that runs on electricity. That's why timer has extra wire.
Intermatic, GE, Tork, Leviton, Sylvania, Woods, Utilitec etc in-wall timers each wire the same way.
The only tiny difference is GE doesn't have green ground wire.
http://waterheatertimer.org/Program-wire-Utilitec-0192773.html
Here's what to do:
1) Old switch has two screws (excluding green ground screw)
One screw on old switch has 2 black wires >> these are hot wires > timer black wire connects to these hot wires. This will power the timer.
2) The other switch wire connects to timer red wire. This will send timer signal to lights.
3) Timer white wire is for the timer clock.
Timer white wire connects to other white wires that are twisted together and covered with wire nut >>> these are neutral wires, and now timer clock will operate
4) For EZ connection to other white wires, strip back another inch on timer white wire so stranded wire can wrap like a candy cane around solid copper wires. Then twist wire nut on very tight.
5) When wiring is complete, push door on timer for manual override. Lights should turn ON-OFF. If lights do not turn on, reverse timer red and timer black wires. Make sure outdoor bulbs are working.
Add a comment any time
Dec 14, 2010 | Intermatic Inc. ST01C Digital In-Wall...
I have an Intermatic T103 DPST timer installed now (120v). The clock mechanism has failed. I bought Tork 1103 guts to replace it. The wiring is a bit different. Can u map for me which wires go to which...
T-103 has 120V clock motor with 5 terminals A 1 2 3 4
Tork 1101 has 120V clock motor with 4 terminals L 1 X 2
T103 is DPST and can control one-or-two 120Volt loads, or one-or-two 240Volt loads.
Tork 1101 is SPST can control one 120Volt load
Common ground between these timers one 120 Volt load
Changeover for one 120 Volt load:
White wires T103 terminal A go to Tork terminal X
Black wire T103 terminal 1 goes Tork terminals L and 1 (there is brass connector plate that connects L and 1 - if connector is missing, jumper between L and 1)
Black wire on T103 terminal 2 goes Tork terminal 2
If Load requirement is greater than T1101, Grainger sells T103 clock motor for $16
http://www.grainger.com/Grainger/INTERMATIC-Time-Clock-Motor-1PNK1?Pid=search
http://www.grainger.com/Grainger/timer-accessories/timers/electrical/ecatalog/N-8hi
How to wire T103
http://waterheatertimer.org/How-to-wire-T104-Intermatic-timer.html#T103
T1101 wiring manual
http://waterheatertimer.org/pdf/110111021103WIRING.pdf
Dec 02, 2010 | Intermatic T103 Indoor 120-Volt 40-amp...
I have a wall switch and two outside ligthts. there appers to be two black wires to old switch. Timer has white, black, red, and green. I hagve tried all wiring scemes and get lights to stay and not turn...
You posted under the ST01C timer.
ST01C has black, red and blue wires, and has a battery to run the clock.
You have black, white, red and green.
So your timer has an electronic clock and no battery.
Let's go through the wires one at a time.
You can add a comment and I will help further if needed.
Old switch has 2 black wires.
One of these wire is black-Hot
The other wire is black-to-Load (load is your light, fan, motor)
Black-Hot connects to timer-black wire
Black-to-Load connects to timer-red wire
NOW ... if these wires are reversed, the timer will not operate, so simply reverse the wires.
There are two wires to go:
Timer-green wire goes to bare copper wire.
Timer-white wire is the wire that runs the clock inside the timer. This is just like plugging in your alarm clock so the clock runs.
The timer-white wire connects to the other white wires located inside the box.
These white wires are usually twisted together and covered with a wire nut.
So untwist the wire nut and add the timer-white wire to these wires.
What if your box does not have these other white wires?
Then in that case, connect the timer-white wire to the bare copper and the clock will run.
Nov 06, 2010 | Intermatic Inc. ST01C Digital In-Wall...
How to wire a 1104 series time switch
8896f6e.jpgTork 1100 series
Tork 1103 can control 120V or 240V Loads (fan light motor)
It can control 1 or 2 different Loads
Tork 1103 has 5 screw terminals
L 1 Unmarked X 2
The Tork 1103 has a 120V clock motor that consumes 3 Watts and costs $3.50 per year to operate.
1) You have to have a white Neutral wire from breaker box connected to Unmarked terminal no matter if you are controlling 120V or 240V Load
2) You have to have a black Hot wire from breaker connected to terminal L no matter what load
If you have 1 Load 120V:
Terminal L black hot from breaker
Terminal 1 no wire
Unmarked terminal white neutral from breaker
Terminal X black wire going to Load
Terminal 2 no wire
White wire going to Load connects to Unmarked terminal
So 2 white wires are on terminal 2
If you have 2 Loads 120V (Load1 Load2)
Terminal 1 jumper your black hot from Terminal 1
Terminal X black wire going to Load1
White wire going to Load1 connects to Unmarked terminal
Terminal 2 black wire going to Load2
White wire from Load2 connects to Unmarked terminal
So 3 white wires are on terminal 2
If you have 2 Loads 240V
Unmarked terminal white neutral from breaker (no other wires connect to this terminal)
White wire going to Load1 connects back to 240V breaker
White wire from Load2 connects back to 240V breaker
If you have more questions, add a comment and I will help
Oct 30, 2010 | TORK Variable Cycling Timer 8601
I have a 110 Pool Pump and I am trying to wire it into a Tork1103NC timer. From the pool pump I have a black, white and green wire that I need to wire into the timer. Can you tell me what position those...
Here is Tork 1103 wired for single load.
1) The green pump wire and bare copper wire go to green ground screw
2) Pump black wire goes to pole 2, the NO (normally open) pole
3) Pump white wire goes to unmarked screw
4) Black from circuit breaker goes to pole L
The T1103 comes with a removable brass bar that connects pole L and pole 1
If that removable brass bar is not there, then add a jumper between pole L and pole 1 as shown in diagram above
5) White neutral from breaker box goes to unmarked pole (all whites connect to unmarked pole)
In your case, pole X is not used. Pole X is NC or normally closed > which means the power is ON continuously until timer turns on, and when timer turns ON, the NC pole turns OFF
Oct 11, 2010 | TORK Variable Cycling Timer 8601
Im installing a TORK 1103.. Im hooking this timer up to 4 outlets.. I have a black, a white, a red and a copper wire.. my problem is I have to turn the timer on and off manually.. The clock is not...
Tork 1103 is mechanical timer with 125V 3 watt clock motor
Dial on front face rotates when clock has voltage
Dark and light colored pins connected to dial, and turn timer on and off
There is removable brass bar that connects poles L and 1
You have 4 wires:
Red >>> I'm not sure about this wire, is this Hot wire coming from tandem breaker?
Black >>> this is Hot wire coming from tandem breaker
White >>> this is Neutral wire
Bare ground
Test wires:
Please test Black and Red to bare ground to see if these are both Hot
Test Hots to white to confirm this is Neutral
Solution ASSUMES black and red are both Hot, and white is Neutral
You have 2 problems:
Prob 1) Clock does not rotate dial: so clock is bad -or- clock not wired correctly
Prob 2) You are able to control 4 plugs using manual override, which means load wires are correct
However, you want to wire timer 'without red wire' (which is confusing, since red wires are connected to outlets)
Solution Prob 1:
1) The diagram show the N or Neutral wire is connected to Unmarked pole on timer
2) Black Hot has to be connected to pole L
3) Unmarked pole and pole L must be wired with 120V as shown before dial will rotate
4) If wiring is correct and dial does not rotate, then clock motor is bad
5) If dial rotates, check outer rim of dial to see if you have dark and light pins for on-off functions
6) Notice that all the Neutrals connect on Unmarked pole
Solution Prob2:
Are you saying that the household wiring extends beyond the 4 plugs, so when you turn off the 4 plugs, it also turns off more plugs and switches farther down the line? If so, you need to wire plugs with separate hot wire.
Let me review features on timer which might help:
1) There is removable brass bar between poles L and 1
2) If brass bar is removed, then you need Hot wires on both L and 1... but you can jumper between L and 1 with short black wire
3) If brass bar is there, then one Hot connected to either L or 1 will power both clock and load.
4) Timer is DPST double pole single throw ... so you can control 2 different loads ... one load connects to Unmarked pole and pole X ... another load connects to Unmarked pole and pole 2
If brass bar is removed:
Jumper between poles L and 1 ... so only one Hot wire is used on your timer.
Below shows jumper on poles L & 1: hot to load is on pole 2
Oct 06, 2010 | TORK Variable Cycling Timer 8601
Not sure how to wire my Tork 1103 timer
The L terminal would be for your "hot" incoming black wire. The X terminal would be for your load outgoing black wire. Connect both white neutral wires to the blank terminal (notice this feeds the timer motor. The other two terminals (1&2) are not necessary if it is a 110V single circuit.
Aug 03, 2010 | TORK Digital Interval Timer Ssa100r-24
I have a tork 1103 electromechanical switch. its working but wont
T1103 can be wired many ways.
T1103 has 240V clock motor.
http://waterheatertimer.org/Tork-timers-and-manuals.html#1101
You are connecting 240Volt pool pump to timer.
Open link below and see wiring diagram: look at bottom left diagram:
Electricians don't guess, they test.
Turn power off and separate wires for testing.
Tape tester leads to wood sticks to keep hands away from power.
Stand on dry boards. Wear dry clothes.
Do not touch anything metal.
Turn power ON.
Test each wire to bare ground wire.
For 240V circuit, two different wires should light up tester. Working from your description, by code, these wires should be black and red.
Each of these wires is Hot wire.
These are called Line wires, wires going to pump are called Load wires.
Hot wires connect to terminals L and 1. This will power the clock motor and dial will rotate as time passes, assuming clock motor is good.
Hots are identified.
Test one of the hot wires to remaining wire, and not to bare ground.
Tester lights up on Neutral wire. This should be white wire.
Double check that Neutral wire did not light up on bare ground.
Neutral is not connected to any 1103 terminal.
Remaining wires go to Load (pool pump).
By code, assuming Hot Lines are Red and Black, the Red & Black Load wires connect to X terminal and 2 terminal, in either order. One wire on each terminal.
White wire connects to Neutral wire and is covered with wire nut.
Add a comment for more free help.
Also take advantage of fixya phone service.
For a price, expert speaks with you over phone while you work on timer or any do-it-yourself project.
Fixya is always less expensive than a service call.
Jul 15, 2010 | TORK Digital Interval Timer Ssa100r-24
TORK  Variable Cycling Timer 8601 Logo
43 people viewed this question
Top TORK Hardware & Accessories Experts
Craig Butler
Craig Butler
Andrew Taylor
Andrew Taylor
pawnpower
Are you a TORK Hardware and Accessory Expert? Answer questions, earn points and help others