Question about Goodman GMS90703BXA Heater
My furnace comes on, then shuts down 10-11 seconds later......I have 4 blinks on the board...I have put a new thermostat on, opened all vents (return & registers), completely cleaned the flame sensor, and still have the same problem. What else can I do to solve my problem?
    Problem Solver:
  • 16 Answers
Flame sensor is dirty. steel rod that is in the burners flame path can be removed with 1 screw and cleaned with sandpaper.
Posted on Oct 07, 2010
Where to look from here?
It sound like the limit switch is shutting off and not coming back in to play .
Mar 14, 2017 | Heating & Cooling
1993 goodman status light 4 times blinking
Witch blower is running, the inducer or the systems blower?
System blower could mean the the high limit is opening and shutting down the systems gas train, I would check this out first.
The other problem could be with the pressure switch for the gas train, it is supplied from the inducer motor, check to see if it is operating fully.
HSI boards do go from time to time, this sounds more like a system control problem.
Jan 24, 2008 | Goodman GMS90703BXA Heater
My girlfriend has a forced air Goodman furnace in her house. Her furnace has been not running well. Whenever the filter gets dirty the furnace does not run right which it to be expected. The problem is...
where is the thermostat located? i should be on a inside wall in a comon room and not around lights, computer or heat vent or air return. a thermostat is just a switch and will operate in its enviroment. does the fan cycle off before the heat starts blowing again? the fan on these are on a timer that the t stat will have to "brake" open on reaching temp to shut off. not knowing where your at look this over and i hope it helps. i dont think i would let someone sell me a control board for this problem.
Feb 08, 2011 | Goodman GMS90703BXA Heater
My heater isn't blowing any heat. I hear the fan come in, and i think i hear the gas come on, but nothing comes out of the vents. The fan only comes on for a couple of minutes and then goes off.
Ok so here is a sequence of the heater lighting and the solution for your problem...
1. Thermostat calls for heat. 2. Draft inducer motor starts. 3. Pressure switch attached by a small plastic or rubber tube senses the negative pressure produced by the draft inducer and closes. 4. Draft inducer runs for 30 seconds to a minute before you hear a gas hissing sound. The ignitor did not glow, the flame sensor (a small metal probe about 1/8" in diameter, with a white porcelain base) does not sense the flame, so after 8 to 10 seconds the hissing sounds stops with no ignition of gas to heat your home. Your furnace shuts down and goes into a lock out condition until you turn your power switch back off and on again. Then the sequence starts all over again with no ignition of the gas. Solution:You probably need to purchase and install a new ignitor. I would suggest that you inspect your ignitor closely for cracks.Make sure you do not touch the ignitor with your bare hands. If you do not visually see a crack, then you could have a furnace control board problem or a limit, rollout switch problem. Please see "limits, rollout switches & furnace control boards" further down on this page. The furnace's control board might not be supplying the voltage to the ignitor. If your furnace lights and the gas stays on for 8 to 10 seconds, then shuts right back off, then you need to clean your flame sensor with light sand paper or steel wool. You might need a new flame sensor, but most of the time they can be cleaned an will work well after cleaning. Please see the pictures below to help you identify a flame sensor.
Thanks and I hope this helps. Feedback apprec.
Jan 28, 2011 | Honeywell Electronic Programmable...
Furnace will run, put out heat, turn off and doesnt start again.
What is model # & serial # of this furnace, it may have a diagnosis led indicator light located on the control board, behind bottom door of furnace which will blink and tell you a fault code. Also check furnace filter, make sure its clean, check through out the house to see if all registers are open and not blocked by any objects, make sure cold air return grill is not blocked, the unit could be over heating and shutting off on high limit, good luck.
Feb 15, 2010 | York Furnace Draft Inducer Blower Fasco #...
Model #GMPN100-4 Goodman furnace. Vent fan
The sequence of events for furnace operation is -
Fan purge for 30-45 seconds. During this time, a pressure switch is actuated by the running of the purge fan, proving the control board the purge fan is running.
After purge and purge prove, the hot surface ignition and or spark begins. After a few second delay, the gas valve will open. The control board then monitors for flame prove through another sensor located near the burners. If there is no flame within 3-5 seconds, the gas valve closes. It will repeat this process, usually 3 times, before it shuts the system down, which requires a power down of the system to reset.
I have seen trash get into the hose between the purge blower and the purge switch. But you could be having other problems.
Dec 17, 2009 | Goodman Heating & Cooling
Coleman gas furnace. Burner will re-fire for a few seconds during the cooldown. Model G8C07512MUB12A
This is a little complicated because it can be several things and you need to provide more specific info....It could be your furnace is shutting off on the High Limit...which means your furnace is running too hot...check the filter , return air vents etc would be an airflow problem...dirty blower....Furnace can be too big for your house....when the furnace shuts off on High LImit , the fan will continue to blow air , cooling it down as usual and once the furnace cools enough to reset the high limit trhe furnace will Ignite again as long as the thermostat is still calling for heat . The furnace could also be running too long and getting too hot....your Ductwork can be too small...many factors come into play
Oct 25, 2009 | Heating & Cooling
Furnace runs OK, but blower runs again a few seconds later
Could be a defective thermostat in the plenum.
When a gas furnace shuts down the fan(blower) will run until the plenum cools to the safe range. Usually 1 and 1/2 minutes.
Intermittent operation is a defective thermostat or relay.
Mar 11, 2009 | Carrier Heating & Cooling
Duct fan comes in, igniter lights, but no flame
Remove the front panel. Tape the door switch to the closed position. If the thermostat is calling for heat the furnace should do the following: a light on the circuit board will flash and then the exhaust blower will start. A few seconds later (10-15) you should hear clicking at at the circuit board and an orange glow should be seen thru the small viewing port. A few seconds later the gas valve should open and the orange light will turn blue. If the blue flame only lasts a few seconds and then goes out, their may either be a blockage not allowing the flame to travel to all the burners and not allowing a flame sensor to sence flame, shutting down the unit. After a few cycles of not starting, the circuit board will flash a series of codes that you can read if you look on the back of the front cover. It will give you a starting point where we can research and come up witha more difinitive answer. Let us know what you find for codes.
Oct 26, 2007 | Goodman GMS90703BXA Heater