Where does the 3 prong inducer plug into? Carrier Weathermaker Model 58SXAO80-GG Serial 1490A02296
    President:
  • 1,515 Answers
Hi, it would either plug into the circuit board/control board, or have a connector of the same, either male or female it would plug directly into. This is a 120 volt inducer motor. Look for the other end of the plastic plug.
Sincerely,
Shastalaker7
A/C, & Heating Contractor
Posted on Sep 29, 2010
Is it correct that Carrier had 5 year waranty back in 2007?
Try looking up your own warranty. Check carrier warranty on your model and serial number located on data plate on machine
Dec 10, 2016 | Carrier Heating & Cooling
Heat exchanger replacement for carrier weathermaker 8000
After 18 years of service, it is not cost effective to just replace the heat exchanger. Go the complete replacement route. There may be a utility company incentive to do it.
Jun 06, 2016 | Carrier Weathermaker 8000 Gas Furnace 125k...
Carrier weathermaker 8000
Check to see if anything has built nest in the inducer motor assembly...or a bird worked its way into it.
Dec 10, 2013 | Heating & Cooling
Furnace gas valve is not opening
YOUR FURNACE IS IN LOCKOUT MODE DUE TO A SAFETY FEATURE OF UNIT. USUALLY THE HIGH LIMIT HAS BEEN TRIPPED, OR YOU PRESSURE SWITCH FROM DRAFT INDUCER MOTOR FAULTY OR PLUGGED. IT WILL CONTINUE LOCKOUT MODE UNTIL THIS IS FIXED.
Dec 23, 2012 | Carrier Weathermaker 8000 Gas Furnace 125k...
Flame sensor dirty
Sandpaper lightly scrubbed over the sensor tip to remove any contamination.
Sometimes cleaning is not enough and the sensor must be replaced.
Jan 30, 2010 | Carrier XHB123D X/Y Series Heat/Cool Air...
I have a Carrier Weathermaker 8000 VS furnace that intermittently has frozen up (the inducer blower stops spinning). Do I need to replace the blower or is there something else that can be done? What is the...
If you can get to the shaft of the motor, oil it using electric motor oil. If the motor spins freely, you just may need to replace the start capacitor, however if it is binding; you will need to replace the inducer as an assembly.
Jan 18, 2010 | Carrier XHB123D X/Y Series Heat/Cool Air...
Weathermaker 8000 furnance flashing code 31 blower comes on for 90 sec .. then shuts off .. then other fan goes on.. don't see any flames or lighting goin on can you help?
31 PRESSURE SWITCH DID NOT CLOSE OR REOPENED - If open longer than five minutes,
inducer shuts off for 15 minutes before retry. Check for: - Excessive wind
- Proper vent sizing - Defective inducer motor
- Low inducer voltage (115VAC) - Defective pressure switch
- Inadequate combustion air supply - Disconnected or obstructed pressure tubing
- Low inlet gas pressure (if LGPS used) - Restricted vent
If it opens during blower on-delay period, blower will come on for the selected blower
off-delay.
33 LIMIT CIRCUIT FAULT - Indicates
Nov 04, 2009 | Carrier XHB123D X/Y Series Heat/Cool Air...
Furnace won't work because of a loose Inducer Motor Connector
Cut power to the system at the main disconnect.
Turn the gas off at the unit.
remove the panel, andsee if the stakon conection is intact. Chances are its just a loose connection from your description.
If the problem is not obviose, let us know what you did or did not find.