I have a furnace 90+ . I have no power at the t-stat..no led, blank screen, and the blower will come on. The furnace is tied into a control panel. I can jumper the the unit at the furnace to have the A/C to come on. It will go thru shut down cycle and stop. 5 min. later the blower comes on.I've cut power to see if it will reset the board, no change in operation. control board has 24 volts with status light on but other lights off. All limit switches closed. I,m in need of sugestions Thanks.
Either a thermal switch is open or the pressure switch is closed at start up the system checks all of these before sending power to the T-Stat
Posted on Oct 06, 2010
Rheem Classic 90 FURNACE. Blower motor constantly running, even if t-stat is removed. Led blinks four times. PS closed, is the code. Not a psycho problem, I think it is the voltage transformer.
An LED that blinks four times followed by a two-second pause is signaling the pressure switch is closed when it should be open. The switch itself might be stuck, or the tubing that attaches the switch to the furnace's draft inducer might be blocked
Jul 13, 2016 | Heating & Cooling
Screen went blank looks like this hard wired for power ac unit has power but won't come on due to thermostat not working
T-stat take batteries? The furnace should/may have a circuit board which should have a 3 to 5 amp fuse that is/may be open. You can try checking that first. If the fuse is open there is probably a short in the control wiring or components. Check the wires at the o.d. unit(small control wire). Chewed on, pulled on, sun baked? If you see any lights on the board, with the furnace powered up, then its not the fuse. Jump R to G at the tstat, should start the cooling, blower or both. If it works by jumping replace the tstat. Work safe!!!
Aug 03, 2015 | Heating & Cooling
HELP!! New install of GMUH75-E3A - Main blower starts immediately on power up/ thermostat turn on. Burner never turns on/ignites. AC power is wired correctly and gas supply is connected. Switch is in the...
You need to find out if the problem is in the T-stat, T-stat wire or in the furnace you can do this in a few easy steps
Step 1- Unwire the low voltage from the furnace. Then turn the power back on and see if the blower comes on if it does then the problem is in the furnace and you will need to troubleshoot the furnace (see bottom of page for troubleshooting furnace) if it does not then proceed to step 2
Step 2- Wire the low voltage back up to the furnace (follow the wiring diagram below). And unwire the T-stat, make sure that no wires are touching each other, then turn the power back on to the furnace, if the blower starts then you have a short in the T-stat wire and you will need to pull a new wire. If it does not then proceed to step 3
Step 3- Turn the power back off at the furnace and wire the T-stat back up (follow the wiring diagram below). Turn the T-stat to auto heat 90 if the heat does not start but the blower just runs then you need to replace the T-stat.
http://www.hvac-for-beginners.com/furnace-troubleshooting.html
wiring diagram
Nov 24, 2010 | Comfort-Aire Heating & Cooling
Goodman furnace
double check your wiring. R terminal on the furnace will provide 24 volts to the t-stat. W terminal in the t-stat will send 24 volts back to the furnace W terminal to turn on the heat. G terminal in the t-stat will send power to the G terminal in the furnace when the t-stat is switched to fan on. Y terminal in the t-stat will send power to the Y terminal in the furnace which in turn will send 24 volts to the A/C outside. The C terminal in the furnace should be connected to the c terminal in the A/C outside as well as to the T-stat. Check the fuse again
Jun 02, 2009 | Goodman GMS90703BXA Heater
Blower fan wont shut off
Try cycling the switch at the furnace to reset the blower board. If this doesn't work remove the green wire from the blower board(computer board) to eliminate a shorted t-stat or shorted wire between the furance and t-stat. If blower remains on, then blower board is shorted. I've seen all these problems.
May 04, 2009 | Heating & Cooling
Goodman GDS80904BNA w/ HAI Omnistat model 80
This sounds like a pressure switch problem,alot of the time condensation gets into them and cause the problems you are describing...if you can take them off and shake upside down untill water is out of them...also check to see if anything is biocking intake or exhast
Dec 11, 2008 | Goodman GDS80904BNA Open Flame Heater
FURNACE DOES,T WORK
START WITH THE THERMOSTAT ,MAKE SURE YOU HAVE POWER COMING AND GOING BACK TO THE UNIT .COULD HAVE BAD T-STAT OR BROKEN T-STAT WIRE.
Nov 22, 2008 | Electric Circuit Breaker Kit for Furnace
Thermastat and furnace
you should have 24 volts between yellow and white wires at the stat when the stat is set to heat and set as hot as it will go. burners should light first then 3 to 5 minutes later the fan motor should fire up. if burner doesn't light check the wires going into the top of the gas valve see if you have 24 volts arriving there from the stat. if you do then the gasvalve is probably bad. you can bypass the action of the stat by jumping red to white on 90 percent of the stats made and in a few seconds the gas valve should click open gas flow to main burner where pilot ignites it. another easy check you can do is flip stat fan switch to on. fan should come on at once. if not then you have either no high voltage to unit or no low voltage ( as in a bad transformer). if the fan comes on you know you have high volts and low volts...by cover i assume you mean the decorative cover but there second cover with the mercury bulbs and all is still there. if you have only the bare subbase then new stat time. sounds like an old furnace if it has a standing pilot, it should be checked for cracked heat exchanger by a pro with a n electronic carbon monoxide detector. NOT a diy item due to the real danger of co poisoning.
Oct 02, 2008 | Kitchen Appliances - Others
Ruud achiever 90 plus blower not working
does the furnace ignite?? your system may not have been lighting and has gone into ignition lockout count the codes of the led lights then remove panel led diagnostic codes are listed there.
if led codes indicate no problem verify capacitor is good and that mtr is getting 115 volts.
Sep 15, 2008 | Ruud UBHC Air Conditioner
Heating & Cooling Logo
32 people viewed this question
Top Heating & Cooling Experts
paulcarew
Dan Webster
Dan Webster
Donni Steen