We have a new 12 room motel addition we are wiring. There are two bathrooms in which the arc-fault breakers are trippping. The loads are - two three lamp incandescant wall fixtures, and two GFCI receptacles per 20 amp circuit. The breakers do not trip until approx 10-15 minutes after they are energized. There is nothing plugged into the outlets, only the light fixtures are "on". Gary Travis
  • 487 Answers
Hi, I know it sounds simple but sometimes its the simplist things that get you. Check your earth, as it sounds as if this may be causing the problem.
Posted on Sep 28, 2010
Installing arc fault interrupter with ground fault
If you meant arch fault with ground fault then no, the two types interfere with each other and trip the breaker as one senses an arch and the other grounding.
If you meant ground fault breaker with a GFCI. receptacle, you only need one of the two, either GFCI. breaker or receptacle.
and for circuits, you can put up to 12 devices (i.e receptacle, light)assuming they consume 1 amp each. Anything over 12 amps or 80% of the rating on the breaker, it will trip/reset.
Or if your talking about wires on a breaker then no more than 2 wires recommended. Try adding a junction box outside the panel if your trying to add other branch circuits or tap off of a receptacle.
Apr 21, 2013 | Siemens Seimens Arc Fault Breaker
Question is vague. Arc fault and ground fault are slightly different.
Are you installing arc fault breaker?
http://waterheatertimer.org/How-to-wire-GFCI.html#arc-fault
http://waterheatertimer.org/How-to-replace-circuit-breaker.html
Code says Maximum 12 boxes per circuit breaker.
Arc fault breaker and GFCI outlet in bathroom?
>>> do not connect this way.
Do not install 2 fault protections on same circuit.
Install the arc fault circuit breaker, and then remove bathroom GFCI, and replace with ordinary outlet, or switch-outlet.
How many outlets can be connected to a bathroom GFCI?
It depends on total boxes on circuit.
Count the boxes. Max 12 boxes per circuit breaker.
How many amps can be connected to 15 amp device?
15 x 80% = 12 amps
Electricians use 80% rule to calculate safe maximum
http://waterheatertimer.org/Color-codewire.html
http://waterheatertimer.org/See-inside-main-breaker-box.html
Add a comment
I have bedrooms with arc fault breakers in them. Randomly, the breaker will trip for no apparent reason. Usually only the lights are on in the bedroom, and nothing is plugged in to the outlets. The room...
If your arc fault breakers are tripping, then there is an arc developing somewhere along the line from the panelboard to the rooms that the breakers cover. If they are breaking in more than one room, then the fault lies in the lines somewhere between the panel and junction to these rooms.
You would have to trace the line from the panel to each light/outlet until you find the problem. Remember the arcing could be occurring anywhere, in the line, at the light, or at the outlet.
Your brother should be able to check each section of wire for continuity rather than ripping out all the wires in those circuits.
Hope this helps. If it does, I'd appreciate a 4 thumbs up. Thanks,
Handie Andie
May 27, 2011 | Siemens Seimens Arc Fault Breaker
Have three 20 amp Eaton Arc Fault Breakers Type BRAF and two have tripped and cannot reset. What is the solution? Do I need to replace?
If you disconnect the load wires on the breaker and it will not reset, the breaker has a fatal flaw.
IF the breaker ONLY fails to reset with the load wires connected EITHER there is a wrong connection like servicing a shared neutral 3 wire cable from the breaker, or there is an electrical fault OR there is interference from a source that couples radio-like noise onto the wires to this.
Mar 12, 2011 | Eaton ARC FAULT CIRC BREAKER
Wiring a bathroom in cellar need diagram for 2light switches 2lights and 2 recepticals
Set your boxes where you want them do be (be sure to check local codes for maserments and how many you need for want size room).
When you have that done go to the wiring.
Pick your power source and run a line 12/2 with ground to the room (again check codes for how many reseps and switches, lights you can have on one breaker).
You should have ground fault reseps any where you can reach a switch or plug from a water sources.
Don't put more then one ground faults one circuit they will fight each other and trip.
With the below drawings you should ready to go.
Good luck
http://www.bing.com/images/search?q=wiring+a+three+way+switch&view=detail&id=9C33873D5318C49207657934B6F2A7FEEC2C4EE9&FORM=IGRE1
Feb 01, 2011 | Home
Eaton Arc Fault Breaker type BRAF tripped. I reset it but lights will not work. Ideas please?
My arc fault breaker trips in my bedroom when ever a load is put on line. The trunk line comes into a three gang switch box and feeds the entire room. At times I can turn my ceiling fan and light on for 10 to 20 minutes before the breaker trips. Other times the breaker will trip when either switch is first turned on. I plugged a 4 watt night light in a wall receptical, without the ceiling light or fan on, it also trips the breaker. I have had other plug in lamps, 60 watt, work in other recepticals for a while. The problem seems to appear in all recepticals and lighting in the room.
Feb 19, 2010 | Eaton ARC FAULT CIRC BREAKER
Arc fault breaker trips sporadically
Are there any heaters anywhere in the circuit for this breaker? (ie: bathroom fan w/light and heater) If yes, I would suspect and inspect them first. Also,any type breaker will trip more easily if the electrical connection screws on the breaker are not tight enough...check to make sure that's not the case.
Jul 31, 2009 | Eaton 20A ARC FAULT BREAKER
Blown breaker
It sound like all of those go through your bathroom GFCI. I would recommend moving your outdoor circuit breaker indoors if possible or enclosing it to make it water-proof. You may also do some rewiring from your main breaker box ( if you are handy) to eliminate the outdoor box completely considering you have 100 amp / 200 amp breaker box inside your house. If you still have an old FUSE BOX with 60 amp service, I would recommend replacing it with a 100 amp or 200 amp breaker box depending on the size of your house. I would separate the laundry room by itself with 12/2 gauge wire with ground on a 20 amp breaker. You can then take your bathroom (using 12/2 gauge wire with ground keeping your gfci ) and run it to another breaker in the house with a 20 amp breaker or add a new one if there is room in your main box. Now all you have left is the porch light. You can run that separate from everything to your main breaker box using 14/2 gauge with ground to a breaker in your main box by adding a new 15 amp breaker or adding it to another 15 amp breaker that does not have a very high load such as a bedroom. In general Kitchens, Bathrooms, Laundry rooms should be on there own separate 20 amp breakers. Most every other room can be 14/2 with ground on a 15 amp breaker... hope this helps....Joe
Dec 17, 2008 | Prime 10 Amp Circuit Breaker
3 combination arc fault breakers tripping under load
What is happening is the white wire that comes off the breaker is probably too close to another neutral or too close to a hot wire that is on one of the other circuits that will make it trip when you use a drill etc... Check to see if the coiled up white wire off of the breaker is not near a hot in the panel. I have had lots of arc fault breakers trip for that reason.