I removed the Ground Fault Interrupter plug from my new GE window air conditioner to fit it in my camper, i put a normal AC plug on it now the thermostat stays on all the time. David
    Habit-Forming:
  • 156 Answers
First, the GFI was placed in the system for a reason. On ANY part of an HVAC system, if it has a safety, you NEVER remove it. If you place a regular plug on it, I would replace the breaker that feeds that circuit with a GFI breaker. This will still give you the protection it needs without compromising safety at all. As far as your thermostat, does it have batteries in it or is it ran off your power input. If you have no power to your system and your thermostat was off before, but now you removed the GFI and the thermostat stays on, I would think you have a battery back up that will lock out the thermostat on a ground fault.
Posted on Sep 28, 2010
Coleman mach rv ac unit tripping breaker
If it trips the circuit breaker as soon as you turn the FAN on, suspect either a bad fan motor or a failed fan motor start capacitor. If you are able to turn the fan on but the circuit breaker trips as soon as the COMPRESSOR starts, it is possible that the compressor is seized.
If, on the other hand, the unit is tripping a GFCI (Ground Fault Circuit Interrupter) breaker or GFCI utility outlet, it is possible that neutral and hot are reversed at the outlet into which the trailer is plugged (happened to me this year at an RV park).
May 14, 2015 | Coleman Heating & Cooling
The gfci tripswhen i turn my ptac to heat what is my problem?
The gfci is short for the ground fault circuit interrupter. This prevents voltage from the hot side of your AC circuit to feed through to the case. This would mean somewhere within, a wire may be touching the frame. You should not try to live with this situation. One quick check might be to reverse the plug in the receptacle. If this does NOT cause the GFIC to trip, then the short must be found and insulated with electrician's tape.
Oct 04, 2013 | GE Zoneline AZ55H07D Air Conditioner
Installing arc fault interrupter with ground fault
If you meant arch fault with ground fault then no, the two types interfere with each other and trip the breaker as one senses an arch and the other grounding.
If you meant ground fault breaker with a GFCI. receptacle, you only need one of the two, either GFCI. breaker or receptacle.
and for circuits, you can put up to 12 devices (i.e receptacle, light)assuming they consume 1 amp each. Anything over 12 amps or 80% of the rating on the breaker, it will trip/reset.
Or if your talking about wires on a breaker then no more than 2 wires recommended. Try adding a junction box outside the panel if your trying to add other branch circuits or tap off of a receptacle.
Apr 21, 2013 | Siemens Seimens Arc Fault Breaker
Location of freon in carrier air conditioner camper
They are a closed system, meaning they shouldn't need re-charge unless a leak has occurred, and to Have an AC repair person come and evacuate, cut lines, add fitting and re-charge, could get pretty expensive. Most people find it smarter just to buy a new unit but get an estimate on repair and decide for yourself. Why do you think it needs freon, not cooling enough, or at all?
Feb 23, 2013 | Dometic Rooftop RV Air Conditioner
My dometic unit is less than a year old. The unit will kick on but in just a few seconds the breaker trips for the entire camper. This does not occur when just the fan is running.
It sounds like a problem in the main breaker, assuming the unit is on it's own circuit. Is the main a gfci (ground fault circuit interrupter)? If so I'd guess something was wet or malfunctioning inside the unit. Has it been properly draining? If not I'd guess the connections to the main breaker may be loose....hopefully. Unplug the trailer and remove the panel cover and test it's torque. You may see visual damage to the conductors from arcing. Be careful not to over torque. That's probably not a cheap breaker. And don't spray any WD40 in there. If you repair the damage I'd retorque every thing else inside the panel. Constant heating and cooling, expanding and contracting, of the conductors can cause the screws to loosen. Best of luck.
Jun 15, 2011 | Dometic Rooftop RV Air Conditioner
Have a 93 airstream camper with a Dometic AC unit . When I tuun the unit on either to heat or air,it brings the house voltage down to the red zone but does come on but seems to be draining the power.
Does the fan seem to labor when starting up. (basically starts up but seems slow to get up to speed?) Then when fan is turning at normal speed, the power inside seems to go back to normal?
May 09, 2010 | Dometic Rooftop RV Air Conditioner
Do i use 10-3 withground?Im hooking a 18000 BtU Ac heater
A normal 2phase 220 or 240 V unit usually requires
2 wires and a ground. If you know what a contactor
is you will notice that only two line voltage wires can
be inserted into it and the ground wire to the equipment ground.
If you have a 3phase unit you would need 3 wires and a ground. Usually on the back cover of the unit it will
show the wiring diagram
Jan 12, 2010 | GE Quiet-Aire Ductless Split System Air...
Help, Brand New A/C unit drippin inside camper
they do that its normal operation, you will get varying amount depending on your location and humidity. If it is not balanced or installed right it drips in the camper.
Aug 16, 2009 | Dometic Rooftop RV Air Conditioner
I bought an older camper with a colman roof unit ac. My question is do I need to put small filters under the intake grates inside the camper below the ac cover. There is nothing in there. (bought it this...
its good to put them in, as it will keep dust from building up on the coils, thus reducing cooling.just buy some filter material at any hardware store, coarse, like a sponge, not fine paper stuff.
Jul 30, 2009 | Dometic Rooftop RV Air Conditioner
WILL NOT RESET
You might be plugging it into an ungrounded outlet. Or if you are plugging it into an outlet that has a ground fault interrupter, and it is THAT that is throwing, then you have a short somewhere.
Jun 21, 2009 | Haier hwr10xc6 Air Conditioner