Furnace glow plug lights but main burner doesn't go on
    President:
  • 1,515 Answers
Hi, on a call for heat from your thermostat, you get a signal to your ignitor module to send voltage to your pilot glow plug. As it glows it sends a signal back through the flame sensor to tell the MGV, (main gas valve) to open and start the burners. When this glow plug glows, you should here a click at the gas valve as 24 volts is sent to it to open. Unless the gas is off for some reason, which I doubt you turned it off, the gas valve is shorted out. You might want to try this first, with the power off the flame sensor that is beside this glow plug as we call it may be dirty and not sending a signal back to open this valve. It is about 4 to 6" long and round, made of porcelin with a metal tip on the end. Take a piece of sanding cloth or steel wool and clean the tip, so it gets nice and hot from the glow plug. Turn the power back on and cycle the thermostat on heat again. The inducer motor will start first, then close the pressure switch and the plug will glow. After this, it will send a signal back to the module to open the gas valve. Hopefully this is the problem, just a dirty flame sensor. If that didn't do it, the gas valve is bad and will need to be replaced. Please rate me on this as I know you will be kind. If its a dirty flame sensor, you should be up and running in no time at all.
Sincerely,
Shastalaker7
A/C, & Heating Contractor
Posted on Sep 28, 2010
  • Robert Horton
    Robert Horton Oct 01, 2010
    What you have is called a hot surface ignitor, that's what glows. When it glows and lights the pilot, it heats up the rod I was talking about sending a signal back to the module telling the gas valve to open. If this sensor is dirty, it will not start the burners/open the gas valve. If you clean it and you still have no gas valve, The valve is defective. Please rate me and let me know how you are doing on this. I am not asking for any charges for this information to you.
    Shastalaker7
Light pilot reset
If yours is a high-efficiency furnace, you should hear the stack blower start running when your thermostat calls for heat. Next, the igniter should start to glow and remain glowing until the thermocouple opens the gas valve and allows gas to flow to the main burner. The main burner lights and burns until sufficient heat is generated for the main blower to turn on and blow warm air through your house. If any action does not occur in the order described, repairs are in order.
Dec 08, 2013 | Kitchen Appliances - Others
Our Gibson KG7TC060D24B "tries" to start, but the shuts off before ignition. Technicians have replaced the control panel and other components but the problem persists, with the furnace working for a few...
This is possible, however it is possible they are missing something simple. I hope you can follow along.
1) Is this a Sealed Combustion Furnace, meaning you cannot get to the burners even after you remove the Door Panels?
2) If yes, is this furnace vented with pvc/plastic piping?
3) If yes, do both pipes go outside?
4) If yes then try this.
1) Turn the main power off to the furnace
2) Remove the Door Panel to the burner section.
3) Turn Furnace back and turn the thermostat all the way up.
4)Look into the burner compartment and tell me if the igniter glows red. If it does and the goes out with the burners not coming on.
5) If you feel comfortable or know of someone that is.
6) Turn the furnace off, remove the panel that conceals the burner compartment.
7) Turn the furnace on, if the igniter glows red and the burners ignite. Your problem is in the venting system. Most likely the intake pipe if it goes outside. It could be plugged or something is blocking it. If the burners do not ignite the next thing to make sure that is happening is that the Exhaust blower is operating and you can feel air outside where the pipe terminates. If you it is but no very strong, then your problem could be the inducer motor or to small of vent pipe.
If you could, send me some information about how it starts up
1) Main blower may come on and shut off, make sure the blower runs in on position 1st then back to Auto position. If it does not, you have another problem.
2) The Exhaust blower should come on next
3) About 17secs. later the igniter should glow red.
4) You will here the gas valve make a click
5) The Burners will ignite
6) The flame sensor rod on the far left hand side of the burner will keep the burner lit. If it is dirty the burners will shutdown.
7)About 90secs. later the main blower will come on.
Oct 26, 2013 | Gibson KG7TC060D24B 60,000 BTU 95.1% Gas...
Why heater coils glow?
It sounds like you're describing one of two things. The hot surface ignitor in a gas-fired furnace, or the resistive heat strips in an electric furnace.
The hot surface ignitor in a gas-fired furnace lights the burners. This ignitor in modern furnaces serves the same purpose as the standing pilot flame did in older furnaces. It provides the required heat to ignite the gas at the burners. Without an ignition source, a gas-fired furnace cannot provide heat. When the ignitor is activated it will glow bright orange or yellow.
The resistive heat strips in an electric furnace actually provide the heat to a home or building. When the furnace turns on, the heat strips are activated and usually glow orange when they reach peak temperature. In almost all cases, the heat strips are not easily seen or accessed without removing covers or panels inside the furnace.
Feb 28, 2011 | Heating & Cooling
I have a Goodman gas furnance. The furmance kicks on the glow rod lights and then the furnance shuts down after about 60 seconds it goes through the same cycle. The burners never come on. What's wrong?
Let's trouble shoot a few possibilities:
Can you confirm that your gas pressure/ supply is correct-- by lighting all of the range top burners at the same time-- Do they all light quickly, and burn to full height, without much of any yellowing at the flame tips? That should indicate you have god gas pressure and supply.
Now-- in the Oven itself-
When you light the BROIL burner-- does it's glow ignitor light up, and does that burner light off OK?
If it is only the main oven burner that is not lighting, are you able to remove the cover plate that covers it, and watch it light off? -- Any clues on whether or not the gas valve even open?
If NO gas flow, likely you need a new Main Oven Gas Valve-- Probably need to call your Gas Appliance service person.
Let us know if this helped
Mack B
Jan 23, 2011 | Goodman GMS90703BXA Heater
I have a Rheem Furance that has turned off. Just a few hours ago the main fan turned off. The Furnace doesnm't light even the draft fan does turn on and then the main fan blower motor turns on. I can hear...
You will need to reset the furnace by turning the power off to it. Then as the furnace tries to light, watch the LED for blinking. Hopefully it will give a code other than 1. Try checking the air filter for blockage, make sure all hoses are free of moisture and any drains are not blocked. Check the air intake and exhaust pipe for sags where water could block it.
The sequence of operation is this:
Thermostat calls for heat, the LED may blink telling you it registers the call. The inducer (exhaust) blower starts closing contacts in the pressure switch (small disc shaped thing), the igniter glows orange (seen thru a small window high up on furnace front), gas valve opens allowing main burner to light, flame travels to all other burners, flame rod senses flame within a few seconds and keeps gas on. Room air blower starts within 90 seconds.
Any deviation or delay in this sequence and it goes into lock-out.
Jan 22, 2011 | Heating & Cooling
80% ducane furnace makes several attempts to ignite then shuts down. glow stick lights but no ignition to main burners. any ideas?
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Check for 24 volts across the gas valve terminals!
Mar 04, 2010 | Heating & Cooling
Janitrol furnace-circuit board code giving 3 blinks vent pressure switch or vent blockage where do i check on system / furnace was running fine up to this point /turned it off for about 1hr. and when i...
f this is a metal vent 80% furnace,Turn Furnace off
and remove the vent that connects to furnace and see if it is plugged.
If this is a High Eff furnace witrh pvc vents for
exhaust and intake air make sure they are not plugged on the outside.
Turn thermostat all the way up,turn furnace off and
wait a few minutes.This should reset any control
board fualt.
Turn the furnace back on, if you have a glow coil
ignitor it should glow red and then the burners should
ignite. If this doesnt happen then:
On High Eff Furnace if the glow coil does not glow red, remove the combustion door to the burners,
turn furnace back on, if the glow coil glows and
burner ignites, you have an obstruction in the intake
air side. If it still does nothing then:
Use caution and remove the exhaust vent from furnace, start furnace, if furnace runs then you
have a problem with the vent system
Feb 13, 2010 | Heating & Cooling
I hope that I can get this problem resolved. Can there be a thread started to help me through this? I will try to keep this as short as possible, I have a Ducane Mod. CMPB050C3A Nat. gas furnace. The...
say that you have the glow bar (Hot surface igniter) working
if the flame starts make sure you don't trash on the orifice of the burner, you can try to use a piece of wire or someting small to pick on the orifice of the burner, also make sure is not rust bewteen the burners gap where the flame spread to all the burners because if the flame sensor don't feel flame don't stay light up
hopes this help
Oct 09, 2009 | Heating & Cooling
Main Fan won't turn off even with thermostat removed. Burner not
There is a chart with the wiring diagram and othere charts that will tell you what the 6 blinks are for. That should tell you what is wrong and what part you need. Sounds to me like the board has an issue or the gas valve is locked out.
Jan 10, 2009 | Goodman GDS81155CNA Open Flame Mid-Size...
Heating & Cooling Logo
106 people viewed this question
Top Heating & Cooling Experts
paulcarew
Dan Webster
Dan Webster
Donni Steen