Just installed new Goodman 95% updraft furnace with 3" supply and vent lines going out through wall. Gas valve won't open. Circulation blower runs in manual on, A/C system runs fine. I have used an ohmmeter and voltmeter to do checks. The entire series of safety switches are closed. When the small blower is running, both pressure switches close. The igniter comes on but there is no voltage to the gas valve. Just after the igniter goes off, I hear a relay click, the circulation blower seems to be starting and I get voltage to the gas valve for about 1/2 second. The circulation blower is not coming on at all in the ignition cycle except "trying" after the igniter goes off. There are no flashing codes except a single flash after 3 tries. Should I ask for a new circuit board or are there other things to check?
  • 407 Answers
Make sure you have bled your gas lines. If any air is in the lines, it will cause the unit to do exactly what yours is doing. The relay "click" you hear is the gas valve opening, but if there is no gas, it will not ignite. This is common for a new install. I hope this helps or at least points you in the right direction! Good luck!
Posted on Sep 28, 2010
  • Brandon Berry
    Brandon Berry Sep 28, 2010
    Also.....Sometimes I even forget to make sure the gas valve switch is in the on position, you might check that also!
  • jdwright81 Sep 28, 2010
    I had to install an LP kit (nozzles for the burners and springs for the gas valve) and the instructions for initial setting of the hi and low screws were VERY unclear. I tried a different interpretation of the screw setting instructions and was able to get it to light and then adjust with a manometer. Your comments were right on - there was no gas - but I had totally forgotten about the LP conversion and the confusing regulator setting instructions.
New furnace, Water In Induction Motor, Yellow Flame
The problem is too much gas as opposed to not enough air. It is still running rich. Did you take into account the elevation of the location your furnace is installed at. The higher above sea level the less air that you have to aid in cumbustion. The condensation is from excess gas being cold and causing water to accumulate. Can you run it like this? Yes but it will cause issues with soot and carbon deposits. It will also cost you more money in the long run.
Dec 23, 2013 | Goodman Manufacturing Goodman GCH950453BX...
Model #GMPN100-4 Goodman furnace. Vent fan
The sequence of events for furnace operation is -
Fan purge for 30-45 seconds. During this time, a pressure switch is actuated by the running of the purge fan, proving the control board the purge fan is running.
After purge and purge prove, the hot surface ignition and or spark begins. After a few second delay, the gas valve will open. The control board then monitors for flame prove through another sensor located near the burners. If there is no flame within 3-5 seconds, the gas valve closes. It will repeat this process, usually 3 times, before it shuts the system down, which requires a power down of the system to reset.
I have seen trash get into the hose between the purge blower and the purge switch. But you could be having other problems.
Dec 17, 2009 | Goodman Heating & Cooling
Goodman furnace no gas , 3 blinking
3 blinks is a pressure switch error clear the hose going to the inducer housing you may need a paper clip to stick into the barb fitting on the motor housing
Oct 02, 2009 | Goodman GMS90703BXA Heater
Goodman forced air gas furnace not firing
if your power vent moter is not running you should not have have glowing ignitor.Frist the vent moter must close an air prove switch in series with the idnitor .seems you have a stuck air prove switch.Its the one with a hose attached
Apr 04, 2009 | Heating & Cooling
Goodman GMP075-3 ignition problem
bad board,i have had several board failures on goodman
Dec 18, 2008 | Goodman GDS80904BNA Open Flame Heater
Furnace won't stay running
1 FLASH
Furnace fails to operate.
• Integrated control module
diagnostic LED is
flashing ONE (1) flash.
• Furnace lockout due
to an excessive
number of ignition
“retries” (3 total)1.
• Failure to establish flame.
Cause may be no gas to
burners, front cover
pressure switch stuck open,
bad igniter or igniter
alignment, improper orifices,
or coated/oxidized or
improperly connected flame
sensor.
• Loss of flame after establishment.
Cause may be
interrupted gas supply, lazy
burner flames (improper gas
pressure or restriction in flue
and/or combustion air
piping), front cover pressure
switch opening, or improper
induced draft blower
performance.
• Locate and correct gas
interruption.
• Check front cover
pressure switch
operation (hose, wiring,
contact operation).
Correct if necessary.
• Replace or realign
igniter.
• Check flame sense
signal. Sand sensor if
coated and/or oxidized.
• Check flue piping for
blockage, proper
length, elbows, and
termination.
• Verify proper induced
draft blower performance.
Nov 23, 2008 | Goodman GMS90703BXA Heater
Ignitor glows, but no gas
Most likely either a bad board or no gas to gas valve. Bleed out all air in the gas line. Check for 24 volts at both gas valve and circuit board terminals leading to gas valve. No voltage = bad board.
Jul 23, 2008 | Goodman GMS90703BXA Heater
Goodman furnace model #GPO 125_4 REV 8 Installed 6/2/2002
Have you measured the temperature in the suppy plenum? Should be 140 to 160 max. If hotter, you have a blockage in the ductwork or vents closed. If within spec, bad circuit board.
Jun 05, 2008 | Goodman GMS90703BXA Heater
Heating & Cooling Logo
125 people viewed this question
Top Goodman Heating & Cooling Experts
Dan Webster
Dan Webster
Paul Carew
Tim Whalen
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others