Question about Ruud UAKA037 Air Conditioner
Air conditioning unit
What steps might i take to check on the blower fan indoors to my unit.
It seems to have stopped running.
Its a rheem air conditioner..i can't find it listed
    Scholar:
  • 57 Answers
Have someone turn the thermostat to fan on. stand by the air handler. listen for a click. There is a fan relay or a stack switch both click when power is sent to them .
If you do hear a click that is good. should be good part.
No click means the relay or stack switch may be bad.
also look at the capicator. it's a little silver oblong or round component with 2 wires to treminals on the end. These wires are usually brown. The top of the capicator where the wires attach should be flat. if it is a little rounded the cap is bad.
If the cap is good and the relay is good.
SECURE POWER to the Air Handler. At the breakers
touch the side of the motor. BE CAREFUL it could burn.
touch lightly... if real hot motor is more than likely bad.
The Motor has the specks on the side of it. and can be read after the motor is removed.
Two screws must be removed to remove motor.
If you must disconnect wires to remove. write down where they connect and there colors Before disconnecting.
Good luck
Posted on May 20, 2008
My Goodman heat pump doesn't blow air through the vents into the house, but the fan comes on when the thermostat is turn on for the air conditioning
Check first that
  • the air conditioning equipment is turned on,
  • the thermostat is calling for cooling, and that
  • the blower unit or air handler is actually blowing air through the ductwork.
Here are the details of what to check in what order if your air condtioner or heat pump doesn't start at all when you set the room thermostat to call for cooling:
  1. Check the Room Thermostat Temperature Setting: Set the thermostat to at least 5 degrees below room temperature. Our elderly mom has no patience with switches and controls. She regularly calls her air conditioning service company with a service request, sometimes late at night, because she has simply failed to set the temperature on the thermostat lower than the room temperature. Don't drive your A/C like our mother.
  2. Check that the Room Thermostat is set to "Cool" not "Off" or "Heat". If the thermostat is not set to "cool" it is simply turning off your A/C. If the thermostat display is blank then it's not receiving power (for modern digital thermostats). Check that electrical power is on at the air handler and to the the low-voltage transformer that supplies power to the thermostat.
    If the thermostat has power, check that when you set the thermostat temperature down at least 5 degrees below room temperature the thermostat calls for cooling. If it doesn't then check for broken or shorted thermostat wires anywhere between the wall thermostat and the control board at the air handler.
    You can easily eliminate possible thermostat problems as a cause of failure of the air conditioner to start by simply eliminating the thermostat from the picture: disconnect the thermostat wires at the blower unit's control board and instead connect the two thermostat terminals directly together with a jumper wire. If the system starts then the problem is in the thermostat itself or in its wiring.
    If the thermostat is working but the compressor condenser unit won't start, you could skip ahead
    to COMPRESSOR / CONDENSER DIAGNOSTICS but I wish you'd double check the remaining steps in this article first because there are some sneaky snafus listed below that might still be the problem.
  3. Check that electricity is on for the equipment. Check all of the electrical switches and controls that can turn electrical power off at the indoor air handler or at the outdoor compressor/condenser unit. There are more of these switches than you might guess. Here's a list of what to check:
    Electrical power switches and service switches outside by the compressor, inside at the air handler, and fuses or circuit breakers in the electrical panel. Don't forget to check that the access covers to the equipment are properly closed and latched. Otherwise a
    BLOWER DOOR SAFETY SWITCH could be keeping the equipment from running.
    There are several other safety switches and controls, both manual and automatic that can leave an air conditioner or heat pump turned "off" such as a blower compartment door interlock safety switch, an electric motor overload or overheat switches, and a condensate tray spillage detector switch.
    Some hard-to-find electrical switches on an air conditioner or heat pump could be keeping your air conditioner from starting, such as
    a FLOAT SWITCH on Condensate Tray that could
    be
    causing CONDENSATE PAN SWITCH LOCKOUT - condensate spilling into an overflow pan that uses a sensor switch can be enough to shut down your air conditioner.
    or
    a blower MOTOR OVERLOAD RESET SWITCH could be keeping a fan motor from starting.
    A bad or failed starter capacitor could also be leaving your system shut down, failing to start a blower, fan, or compressor motor.
    See CAPACITORS for HARD STARTING MOTORS
    Watch out: See A/C - HEAT PUMP CONTROLS & SWITCHES to be sure you have found and checked everymanual or automatic electrical switch on the system.
  4. Check the electrical supply voltage. Even if electricity is on, if the supply voltage has fallen too far below the operating voltage range of your air conditioner it's likely that the system will not operate, particlarly, you may note that the compressor motor won't start.
    See VOLTS MEASUREMENT METHODS
Aug 22, 2017 | Goodman Heating & Cooling
I have new blower motor. it dosen't stop running
Could be a bad blower motor resistor,mounted by the blower.
Sep 28, 2016 | 2002 Dodge Ram Pickup 1500
Mitsubishi timer light 6 times blinking
Indoor unit indicator
RUN lamp = 6 time flash
TIMER lamp = Comes on
Outdoor unit indicator (LED5) = Stays off
Description of trouble = Indoor fan motor error (2)
Cause = Defective fan motor, Connector poor connection
Conditions of flashing = When air conditioner is operating and indoor fan motor is turned ON, indoor fan motor speed of 400 rpm or under continued for more than 30 seconds. (Air conditioner stops.)
May 29, 2016 | Mitsubishi Heating & Cooling
Rheem error codes
error code 29 is a high pressure open. possible causes are dirty indoor or outdoor coil. indoor or outdoor fan not running, liquid line Freon restriction, or to much Freon in the unit.
Jul 30, 2014 | Rheem RPRL048JEC 4 Ton 16 SEER Heat Pump...
I've got a Air condition unit model BV124 30-10L16, which is the part of Lennox furnace unit. The indoor fan stops working now. The outside fan works fine. I checked the capacitor, fine too. Cooling...
Hello, a blower motor will not run for one of theese three reasons 1) No power to motor 2) bad capacitor 3) the motor itself is bad. One test you could do is take the wire of the L1 terminal on the control board and use a jumper wire and connect it to the wire on the high speed motor tap , if this gets the unit running then the control board must be replaced if it does not work then the motor is shot......make suremwhen disconnevting wires the power is off.
Sep 04, 2011 | Heating & Cooling
Inside motor not running and will not run on just fan. cage turns easily by hand
If the out door unit is running without the indoor fan running, you could possibly have a motor burned out or your indoor unit.
If nothing is running, check to make sure all panels are on inside, and that you have electricity to the indoor unit. Some air handlers and furnaces are equipped with a safety switch on the access door to the motor assembly. Also , there may be a switch that looks like a light switch beside the indoor unit.
Once again, check and see if the outdoor unit is running. It will eventually freeze up without the indoor fan. Hope this helps. Please email me if you have any more questions , I will try to step you through. Mark
Jul 11, 2011 | Ruud Heating & Cooling
Coils freeze up
The first thing to do is see if the indoor (evaporator-air handler) fan and compressor are both running at the same time, then turn the unit off and let all the ice melt.
If the compressor is running and the evaporator fan isn't, you've already found the main cause of your air conditioning freezing problem.
The indoor coil will freeze up if the compressor runs without the evaporator fan running.
Check to see if ice has built up enough to stop the fan.
If it has, (and it's possible with wall mounted ductless mini split units and some window units), the fan may run normally once the ice melts, and the cause of your air conditioning freezing problem could be something else.
If you are the equipment owner trying to take care of this air conditioning freezing problem yourself, and you get to the point that you have to call in a technician, it could save him time, (which saves you money) if you have already verified whether the evaporator fan was or wasn't running with the compressor, and if ice had built up enough to stop the fan.
Once the ice has melted, check the fan or blower blades, and see if they're clean and not obstructed by something like a plastic bag, other debris, or mould growth.
Remove any obstructions, and if necessary, remove the blower and clean it.
Before tearing into the rest of the unit, check the thermostat and make sure it's working right.
Do the cool contacts open when the t-stat is turned up to a higher temp than the room temp?
If not, the thermostat has failed, and never turns the unit off, which can definitely cause an air conditioning freezing problem.
Do the fan contacts open and close when the thermostat setting is turned higher and lower than the room temperature?
If the fan contacts never close but the cool contacts do, the thermostat has failed and caused your air conditioning freezing problem.
If the fan contacts close, but the fan doesn't run, check the fan relay in the air handler.
If the fan relay is not getting control voltage, the circuit is open between the thermostat and the fan relay.
Look for a loose connection, wrong connection, dis-connection, or broken wire.
If it gets control voltage but doesn't energize, it has failed, and must be replaced.
If it energizes but the fan doesn't run, check for line voltage on the load side of the relay.
If there is line voltage on the load side of the relay and the fan doesn't run, you'll have to troubleshoot the load side circuit and the fan motor as detailed further on.
If the thermostat checks out ok, set the thermostat to "fan on" and make sure the blower runs in the correct direction and at the proper RPM, that it is installed in the housing correctly, and is the right size.
If the blower is installed backwards or is running in reverse, the coil can freeze up. (Although I have seen several units that didn't freeze up with reversed blowers.)
You will need to turn the blower around, reverse the rotation of the motor if it is a reversible rotation motor, or install a motor with the correct rotation.
A blower that runs too slow can cause an air conditioning freezing problem.
You'll need to install a motor that runs at the correct speed.
A blower that is too small, or that is installed in the housing incorrectly, can cause an air conditioning freezing problem.
You will need to install the correct size blower, and be sure it is installed correctly in the housing.
This means centered, with volutes installed, and the curve of the vanes matching the outlet of the housing.
If the blower motor is the wrong size, if the bearings are failing, or if it has an open start winding or a failed run capacitor, it could be overheating and stopping intermittently.
A motor that is overheating and stopping intermittently can cause an air conditioning freezing problem.
To check out the evaporator fan motor:
Check the resistance readings of the motor windings.
If you get a readable resistance between all three windings, the motor windings should be ok.
Turn the shaft. If it turns free and easy, the bearings should be ok.
If the shaft is hard to turn, lube the bearings with 20 SAE electric motor oil if there are lube ports.
If that frees the shaft, it should run ok for a while, but the bearings or bushings may be deteriorated to the point that they'll sieze again soon.
If the shaft doesn't free up, replace the motor.
If the shaft turns freely, check the capacitor.
The best way to check the capacitor is to replace it with a new one of the correct rating.
If the motor runs, close the air handler panels, and take an amp draw on the motor.
If it's normal it should run OK, and if the motor was the problem, your air conditioning freezing problem should stop.
Ok, if you've verified that the controls and fan are good, take a break for a diet soda, and then we'll see if the evaporator coil or ducting are the cause of your air conditioning freezing problem.
Take a look at the evaporator coil.
Is it clean? Can you see your flashlight shining through from the other side?
If the coil's dirty, you'll have to do some air conditioning coil cleaning.
If your air conditioner is a window type, our page about how to clean window air conditioners has some pointers you might find useful.
A dirty evaporator coil is a common cause of air conditioning freezing,
And it's one of the problems that can be prevented with regularly scheduled air conditioning maintenance.
If the coil is clean, check the ducting to make sure nothing is blocking air flow.
Blocked ducting will stop air flow through the evaporator coil, and this will cause the coil to freeze up.
If your coil is clean and the ducting is clear, let's run the unit and check the operating pressures and temperatures.
If your discharge and suction pressures are low, with a low compressor amp draw, low subcooling, high superheat, and low temperature splits accross your evaporator and condenser coils, you probably have a leak.
Shut the unit down, find the leak and repair it.
Once the leak is found and/or repaired and you're ready to run the unit, our Charging Air Conditioning Systems page offers some tips that you might find helpful.
If you are totally unable to locate the leak with a bubble solution or electronic detector, you'll have to charge in refrigerant to correct pressures, temperatures, and superheat and subcooling values, and it would be a good idea to add some air conditioning leak detector dye so the leak can be found later on.
You have to use some common sense about leaks.
If the leak is so small that you can't find oil or any other sign; unless the customer agrees to pay you for all the time you spend, it's more cost effective to charge in the small amount of refrigerant it will take to get the unit running correctly, finish the service call, and be on your way.
I can't imagine that there's a service technician out there who hasn't run into the same problem many times.
Use some common sense, be up front with your customer, and if you've done your best not only to find the leak, but to get the unit running right and save your customer unnecessary expense, consider it a job well done.
If your suction pressure is low enough to cause the evaporator to freeze up, but you have high subooling and high superheat, either your metering device is restricted or the wrong size, your drier is restricted, or your liquid line is restricted.
Evaluate all of the system's operating characteristics to isolate the restriction.
Copied from the following web site:
http://www.air-conditioning-and-refrigeration-guide.com/air-conditioning-freezing.html
Jun 30, 2011 | Heating & Cooling
I have a blizard split model 10.5 years old in a caravan. model sa101 the air feels cooler but seems to have no noticable difference in actual temperture and compressor seems to run continuously ...
Please understand first, air conditioning system not only cooling the area but also removing the heat. If heat in the room stays constantly, even 24 hrs running a/c couldn't cool the room.
Now, why the a/c could not cool the room or remove the heat from the room.
Check air filter, evaporator coil and blower wheel for clean. If not service the unit immediately. And also check indoor fan motor rpm. If rpm is low, replace fan capacitor. Check for gas pressure to confirm no leak or running with short of gas. It's advisable to service both indoor and out door once in 6 months at least. Otherwise, your electric bill will kill you lot. Thanks.
Jan 31, 2011 | Electrolux Heating & Cooling
Indoor fan blowing cold air when on heating
The indoor fan will continue to run. When heat pump goes into defrost the outdoor fan stops, the reversing valve switches and the unit is basically working in the cooling mode. In order for you not to feel a blast of cold air in the winter the electric strip heat also comes on so the indoor fan must run while the strip heaters are on.
Jun 03, 2010 | Heating & Cooling
Air conditioner
Turn off unit supply and check the blower wheel inside the indoor unit by rotating it manually by your finger if the blower wheel rotates freely then there is something wrong with your fan motor or fan motor capacitor. But if the blower wheel is not rotating freely try to check the fan motor for lubrication or some bushing dried of and no oil
Dec 10, 2007 | Heating & Cooling
Ruud UAKA037 Air Conditioner Logo
96 people viewed this question
Top Ruud Heating & Cooling Experts
Bill Long
Tim Whalen
Dennis Boxerman
Are you a Ruud Heating and Cooling Expert? Answer questions, earn points and help others