Heat does not come on. Furnace light blinks 3 times, indicating faulty pressure switch. I jumped the pressure switch, which caused the ignition filament to light up. However, it quickly shut off again. No gas comes out so the blower never starts up. Have checked the lines, they appear to be clear. Furnace is only about 6 years old. Any idea what is causing this and how to fix it?
  • 2 more comments
  • mbt110 Sep 17, 2010
    Thanks for the feedback; is there a test I can run to test if the exhaust fan circuit is the problem?
    Heat does not come on. Furnace light blinks 3 times, indicating faulty pressure switch. It does not appear that the exhaust flue motor turns on when the furnace turns on. I jumped the pressure switches, which caused the ignition filament to light up and the gas flames to ignite (normal operation). All pressure hose lines appear to be clear and there does not appear to be a drainage backup. Furnace is only about 6 years old. Am I right in thinking that the problem is either a bad exhaust flue motor or the connection to the motor? How do I isolate one or the other?
    Thanks. I have made sure all connections (including that probe) are clean and free of debris. I actually got the furnace to fire up after jumping both pressure switches (I was previously only jumping the first one). The exhaust flue fan/motor does not seem to be coming on when it should - I think that may mean it is faulty. Or, that the connection to that is bad. Do you think that's right?
  • mbt110 Sep 19, 2010
    Thanks, much. Some additional information - the fan doesn't come on at all, regardless of jumpering sequence. Also, when I jump the pressure switches correctly (in the order you mention), the system fires up normally.
    These things lead me to believe that the flue fan motor (or possibly the connection to it) is bad. Can you confirm if this sounds right?
  • 43,501 Answers
When jumpering the pressure switch ...you need to let the blower start and then apply the jumper... the brain needs to see the proper sequence or it will not allow the gas valve to open...
and when it shuts down the jumper must come off of the switch and be reattached at the proper time for start up to happen again... this is done for safety reasons...
heatman101
Posted on Sep 18, 2010
  • 11,896 Answers
Check the inside of the pilot. There is a probe inside. This probe needs to remain clean. It provides a certain temperature that is needed to keep the pilot lit. Make sure that probe is clean.
Posted on Sep 17, 2010
  • 560 Answers
I believe your problem might be your exhaust fan circuit . A exhaust flue fan turns on when the heat demand circuit is closed. The fan usually will be running for about ten seconds before enough pressure is built up in the pressure diaphragm assembly . It is connected to the exhaust fan by a small vacuum hose . Sometimes debris will accumulate in the hose itself preventing the pressure build up in the diaphragm switch assembly . It is important that the circuit operates correctly as to not allow carbon monoxide to Backdraft into your home .
  • 7 more comments
  • Cool Blue Services
    Cool Blue Services Sep 17, 2010
    try disconnecting the hose between the pressures switch and the fan assembly . Blow through the hose to make sure it is free and clear . Then check the small connection on the motor to be sure the hole is clear . You can use a paper clip or a piece of wire to clean it out . I'm assuming that the exhaust motor is functioning correctly . If it is not , replace the exhaust flue motor.
    regarding testing the circuit itself , it only has two parts . The exhaust flue motor / blower assembly and the pressure switch assembly which is nothing more than a diaphragm and a switch . Of course , there is the little vacuum hose that connects between the blower case and the diaphragm switch which is also called the pressures switch . When the heater first comes on , the exhaust blower motor should come on first. Once enough pressure is built up , the diaphragm presses against the switch closing the pressure switched circuit . The fan runs continuously as long as the heater is running . Do not confuse the exhaust fan with your air Handler blower which circulates the air through your home . Either the pressure circuit works or it doesn't . If the exhaust fan works , it can only be a plug vacuum hose or a bad diaphragm pressure switch .
    Ok, checked all the lines. They seem clear, no apparent leaks in the hoses or anything either. I don't hear a fan turning on when I turn on the furnace, either. I believe I was improperly jumping the pressure switch (there are two on my model). I was previously only jumping the first one, which I believe may be why the ignition turned off. I tried jumping both, in the proper sequence, and the system fired up just fine. Am I right in thinking this points more firmly to the exhaust flue motor being the problem?
    CHECK THE PRESSURE HOSE BETWEEN THE FLUE EXHAUST BLOWER AND PRESSURE DIAPHRAGM ASSEMBLY. MAKE SURE IT IS CLEAR- YOU CAN BLOW THROUGH IT...CHECK THE BLOWER HOSE NIPPLE TO BE SURE IT IS CLEAR. USE A PAPER CLIP TO CLEAN THE HOLE OUT. NOW, HOOK THE HOSE BACK TO THE PRESSURE SWITCH (UNIT OFF AND NO POWER TO UNIT) BLOW INTO THE END OF THE HOSE AND CHECK THE 2 TERMINALS WITH A OHM METER SET ON RX1 OR LOWEST SCALE...IT SHOULD READ "0 OHMS (CLOSED CIRCUIT) WHEN YOU BLOW INTO IT--- AND INFINITE (OPEN CIRCUIT) WHEN YOU TAKE YOUR MOUTH AWAY. WHEN ALL IS HOOKED UP AND RIGHT, THE BLOWER COMES ON FIRST, THEN AFTER A FEW SECONDS, WHEN THE PRESSURE IN THE BLOWER BUILDS UP, THE SWITCH CLOSES AND THE IGNITER FIRES UP. THEN THE GAS VALVE OPENS AND GAS IGNITES. WHEN THE SET HEAT IS REACHED IN THE BURNER BOX, THE AIR HANDLER BLOWER COMES ON TO HEAT THE HOME. SOME UNITS HAVE A THERMOCOUPLE NEXT TO THE IGNITER. IF THE UNIT FAILS TO STAY LIT, BUT EVERYTHING ELSE CHECKS OUT, REPLACE THE THERMOCOUPLE.
    Cool Blue Services Sep 18, 2010
    Good evening to you . I believe we have isolated the problem . Yes , your exhaust fan motor is probably faulty . However , as you seem to be knowledgeable in the AC electrical areas , I will walk you through one more test before we condemn the motor. The motor is either 110 or 220 VAC. I'm sure you can read the label on the motor to determine the voltage . Regardless , using your DMM or voltage meter, test the leads the supply the voltage to the motor for voltage when the unit first comes on (heat demand as energized by the thermostat). It is important to take his reading when the unit energizes as the failsafe features will cause it to shut down within seconds . If you read the proper voltage then yes replace the exhaust motor assembly. To purchase a new motor , you'll need the model number off of the air Handler / furnace to be sure and get the right part . Sometimes you can use the motor tag number itself , but I would recommend using the air handler model number. Good luck & make sure you disconnect the power to the unit before replacing the motor .
    Cool Blue Services Sep 20, 2010
    I posted a comment yesterday but I don't believe it went through . Any ways , you can test for voltage at the connector for the exhaust motor . There should be an inline connector you can test for voltage at when you first turn on the furnace . There should be line voltage to that motor soon as there is a demand for heat from the thermostat via the circuit board controller . If you have line voltage to that motor , and the motor is not operating , replace the motor . Use the model number of of the furnace air Handler unit to be sure you get the correct replacement motor .
Goodman gmp0503 unit has status light blinking slowly all the time. The indoor blower wont even come on when you switch from auto to fan on thermastat. The status light says for one blink to check gas...
Take a jumper wire and jump out the R and W terminals on the furnace. The heat should come on. If it does not, you have a bad board. A steady blink indicates no call for heat. You may have either a broken thermostat wire or a bad thermostat if unit fires when you jump it.
Mar 20, 2011 | Goodman Heating & Cooling
My mhu45lp mr heater ceiling mount won't start. the green light is blinking steady and exhaust fan is running but burners will not ignite.I did jump the brown and red wires on the pressure switch which did...
Check the electrode is clean and sparking , clean flame sensor and check connections are tight . check hi and low limit switch . check pilot is not blocked .
Jun 24, 2017 | Mr. Heater MHU45LP
I have an amana dms 90904cms furnace ..the fan runs but no heat. I opened cover and saw the red led blinking 3 times code says open pressure switch. what does that mean?
Open pressure switch is when your vent motor comes on it has to get a certain vacuum pressure or it won't ignite furnace. There should be some little black hoses connected to vent motor and maybe into heat exchanger, running to these pressure switches. Pull hose off one end and make sure hoses are not kinked or some times if hoses have sag in them they can fill with water. Other causes are if venting is obstructed or pressure switch is defective, especially if it got moisture in it.
Jan 26, 2011 | Heating & Cooling
I installed a new goodman unit this past spring. It seems to work ok to good in the day time but the tempature is warmer so we do not need as much heat. At night I know the thermostat is coming on. I...
Heating Mode (Goodman Service Manual)
· The furnace control checks for an open main limit (this
limit is normally closed). If the limit is open, the furnace
will remain inoperable until the limit is closed. During
an open limit the circulating air blower will be
energized. The status light will blink four (4) times.
· The room thermostat reacts to a demand for heat.
· The control will then check to insure that the vent
pressure switch is open. If, at this point, the vent
pressure switch is closed the control will blink two (2)
times and will remain inoperable until this situation is
corrected.
· The venter blower is energized.· The vent pressure switch will close when it detects a
pressure in excess of its setting. If the pressure switch
fails to close the status light will flash three (3) times.
The sequence cannot continue until the pressure switch
closes.
· After a pre-purge of about ten (10) seconds the electronic
ignition device will be energized.
· After a slight delay the gas valve will open.
· The burners will ignite and the flame sensor will detect
the presence of flame. The ignition device will
deenergize. If the sensor does not detect the burner
flame, the gas valve will close and the ignition cycle
will be repeated for a total of three attempts. If, after
the third attempt, the presence of flame is not detected,
the furnace will go into a lockout condition for one (1)
hour. It will then repeat the ignition cycle. This one (1)
hour lockout and retry will occur indefinitely.
· Thirty (30) seconds after the main valve is energized
the circulating air blower will be activated.
· The furnace will remain in operation until the demand
for heat is satisfied.
· Once the demand is satisfied the venter will shut off,
and the circulating air blower will shut off after the field
selectable time off is attained.
· The furnace will remain dormant until the next demand
for heat.
Dec 03, 2010 | Goodman GMS80903BNA Heater
Coleman echelon 9.T furnace will not turn on. Red light blinking
sounds like it is the pressure switch try jumping it out on some models you fool the heater in too working or see if the tubes are blocked , there should be some codes on the front panel or the fan panel
Apr 27, 2010 | Coleman Propane Forced Air Heater...
My furnace tries three times then red light blinks once
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Your furnace has a diagnostic chart on the reverse of the lower panel incorporated in the wiring diagram. One blink tells you that it is a failure but wont tell you where to start looking.
Nov 27, 2009 | Goodman GMS90703BXA Heater
Ducane high efficiency propane furnace, pressure switch problem
A short cycle heat cycle indicat a pressure switch replacement was needed. This did not fix the problem. the problem was in PCV line since the end was filled with slugs and cause the line to backup with water. When this happen the system would stop asking for gas. the water would leak out and it would restart. The problem was fixed by cleaning value at end of PCV. This released the water, two quart of water, that was back up causing problem. Curious if a filter change indicator was providing a clue that was missed?
Jan 28, 2009 | Ducane 436 inch 2 - 2 burner Grill
Goodman GMS90904CXA Wont ignite, light blinks 3 times
I had the same problem, I had to remove the lower black rubber stopper right next to the exaust fan and hook up a drain to the unit, as soon as the water drained out the furnace fired right up.
Nov 19, 2008 | Heating & Cooling
Ok, you either have a inducer fan issue or a pressure switch issue or a plugged vent pipe. The inducer turns on to establish a draft for the exhaust. If it is not working you will get this error code. If the pressure switch does not sense pressure caused by the inducer, it will give this code. If either the intake pipe or exhaust pipe is blocked (even y just a little) it will give you the same error code. If the condensate hose or receptical is plugged, again it will give you this error code. Good Luck!
Oct 20, 2008 | Goodman GMS90703BXA Heater
Heating & Cooling Logo
22 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Donni Steen