Question about Goodman Heating & Cooling
I have a Goodman heat pump and the condenser fan and compressor will not switch on. The board green light says improperly grounded or flame sensor not sensing flame (both are incorrect). The AUX heat (gas) fires up and runs as it should. I can press the contact relay switch down and the fan and compressor both will turn on. I have 240v going into the contacts but no voltage to the 24v side of the contacts. Any ideas where else to look?
  • 674 Answers
Does the indoor fan run? Place the fan switch in run. If it doesn't run then the transformer could be bad. Also, there could possibly be some high and low pressure switches that would keep you from getting the 24vac to the contactor. First rule out the thermostat by removing the face and installing a jumper wire between the R and Y terminals. This should make the outside unit run. If it does then your thermostat is not passing 24vac to the unit and should be replaced. If it doesn't run with the jumper in, then your problem is in the outside unit. Trace out the yellow wire from the thermostat in the outside unit and check the components that the wire goes through (high and low pressure switches). Let me know what you find so I can offer more help if needed.
Posted on Sep 16, 2010
What would keep fan from coming on if unit lights off. fan works if manually ingaged at relay.
Flame sensor dirty or out of position, , check pressure switch .
loose connections to fan . rollout switch not working .
Oct 30, 2016 | Goodman Heating & Cooling
Will not come on but emergence heat works
Check contactor that operates compressor and condenser fan. Does it try to come on when you first turn it on, or just sits there? If it tries to come on, it could be the capacitor.
Jan 25, 2014 | Goodman Manufacturing Goodman GPH1348H41...
GMNT080-4B Goes into lock after 20 minutes or so of operation
Hi jump out the presure switch see if it lights check fan control is clean at the back of it check air filter is clean
Feb 22, 2010 | Goodman GMS80904BNA Open Flame Mid-Size...
Goodman model gms8 will not light fan comes on then turns off
On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
What could go wrong? The unit will not run if there is no signal from the thermostat (bad thermostat or broken wire), the control module does not sense a signal from the thermostat (bad control), the inducer does not energize (bad motor), the pressure switch does not close (blocked vent piping, bad switch, plugged condensate hose), the igniter does not energize (bad control, bad igniter), the gas valve does not open or there is no gas (bad gas valve, broken wire, no gas), the pilot does not light (dirty pilot), the burner does not light (bad burner, plugged orifice, not enough combustion air), the flame does not spread to each burner (bad flame spreader, dirty flame spreader, more bad burners), the flame safety sensor does not detect flame (dirty or bad flame spreader, bad flame sensor, broken wire, bad control), or the room air blower does not energize (bad fan motor, bad control).
Jan 26, 2010 | Goodman GMS80453ANA Open Flame Mid-Size...
I have a goodman 6mnte080-4. Home had power failure and furnace went to working intermittently. led is on 8 flash- ignitor or improper ground.. sometimes runs through full cycle--sometimes hot surface...
Check out the green wire going to the gas valve for proper ground,and also check all wires for good connections......... for the intermitting start / stopping and sand the fame sensor pin, this should do the trick.
Dec 13, 2009 | Goodman GMS90703BXA Heater
Goodman GMP 125-4 one blinking light code. Gas valve has been replaced (at cost of $443). Didn't fix problem. Same co wanted $415 to replace circuit board. I did it myself for $99 part. Still same problem!...
One blink means it didn't light after a number of attempts. You replaced the circuit board and gas valve. Read on for some suggestions. On a call for heat, the 24 volt thermostat sends a signal to the control module. The control module will indicate a call for heat with a light on the control either blinking or remain solid depending upon model. The inducer (exhaust) blower will purge all gasses from the furnace and pressurize a pressure switch. Once the pressure switch tells the module to continue, the electronic ignition will energize and send 120 volts to the igniter. The igniter will glow and you will be able to see it if viewed thru the small inspection port. Once the igniter gets hot enough, it sends a signal to the module opening up the gas valve (24 volts). Either a pilot will come on or the burner tube will ignite then spread the flame to all burners. Lastly a safety sensor will be looking for a certain temperature within a few seconds and the furnace will continue to operate and the room air blower will turn on in a minute or two.
Nov 18, 2009 | Goodman GDS80904BNA Open Flame Heater
15 year old goodman heater is cycling. heating element glows red and the burners turn on for 20 seconds and then goes out. fan is in the on position . after the first light the element turns red but...
Sounds like the flame is either not traveling to the flame sensor or the flame sensor is dirty or bad. Look to the far left of the burner box for a probe near a burner. Lightly scrape and debris from the probe. The probe will have only one wire going to it. Do not touch the igniter or it will break.
Dec 09, 2008 | Goodman GMS90703BXA Heater
Copleland scroll compressor failure
I have scroll chiller contains scroll compressor tandom circuit. One of the compressor failure from it due to unbalance of the winding. Previously compressor thermistor opens two to three times. Also one phase open in contactor of the compressor. Can you guide me regarding the reason of compressor failure and what is the next step for the replacement of compressor. Also give guide line for the points take care.
Nov 02, 2008 | Goodman Heating & Cooling
Goodman heating element does not light
The flame sensor is not sensing flame. Inspect the system as it is tying to start and see if the flames are traveling to all burners and hitting the sensor. If not, clean the burner flame rail (the trough the allows the flame to travel from one burner to the next) or if it is hitting the sensor, clean the sensor with steel wool and check all connections from the sensor to the control board.
Jan 20, 2008 | Goodman GMS90703BXA Heater
Heating & Cooling Logo
120 people viewed this question
Top Goodman Heating & Cooling Experts
Dan Webster
Dan Webster
paulcarew
Brandon Berry
Brandon Berry
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others