The model # A-VMC18SB & serial # 801kaed00172 condenser unit & the model of the indoor unit is B-VMC18SB comfort aire inverter series. The inside unit runs but the condenser wont run there is power on the outside unit & a code is giving me on the inside unit the code is CH 05 I don't know what that code means i don't have the instruction manual of the outside unit. The outside unit send the power to the inside unit it's 240 volts single phase it's a R410-a refrigerant. Any information that can solve this problem will be helpful.
    President:
  • 1,515 Answers
Hi, I can tell you this that you may not no, is the condenser gets its 240 volts ac from a 240 volt breaker in your main breaker box, not from the indoor unit. The only voltage that comes from the indoor unit to the outdoor unit is from the thermostat and control board on the indoor unit to operate the low voltage controls on the condenser. I have know idea what this code means either, but there should be a chart glued to the indoor panel telling you what it is. Remove a panel and look for this. You should also by code, have a disconnect box at your outdoor unit that may or may not have 2- cartridge type fuses inside that may have blown. If you can't see them, look behind the plastic cover to see if they are there. Replace them if you are not sure if they are blown. Do these checks, breaker, fuses, and look for a chart that has the codes on it, and you and I can go from there. Please let me know. I will check back in the morning as it is 12:05 a.m. here.Please do not forget to rate me if you have found the problem as I know you will be kind. Keep me posted and I will check in on you.
Sincerely,
Shastalaker7
A/C, Heating, & Refrigeration Contractor
Posted on Sep 12, 2010
  • Robert Horton
    Robert Horton Sep 12, 2010
    Remove the panels at the indoor unit and you will have a chart glued to it telling you what the code CH05 is. Then you will know. This is just a regular central heating and a/c unit . They all are 240 volt, single phase units, the new ones have the R-410A freon and the older ones have the R-22. If you are sure you have 240 volts to your outdoor unit by checking it with a meter, then this code will tell you what the problem may be. You will need to remove the panels to find the chart that tells you. The manual may be tucked inside the indoor unit also, you will have to look. There is a low voltage control on the indoor or outdoor unit keeping it from coming on. Look for this chart or manual inside the indoor unit and let me know.
    Shastalaker7
I have two flashes on the timer light of my indoor unit of Fujitsu Inverter ASU9RLS
Serial signal (reverse) error, at operation start up. operation led - off, timer led - 2 flashes, coil dry led - off, check wire between indoor and outdoor
Jul 10, 2015 | Fujitsu ASU9RLS2 Single Zone Wall Ductless...
Tempstar Air Conditioner wont come on
Sounds like you need a new contactor in the condenser. The low voltage is grounded. Remove the low voltage (likely 2 wires) at the condenser and wire nut the wires leading inside. With an insulated screwdriver manually push in the contactor and be sure both compressor and fan run. Then replace fuse and turn power on to air handler with a call for cooling. Obviously the outdoor unit won't run because you unhooked the low voltage but if fuse doesn't trip then it's likely the contactor. Good Luck
Apr 10, 2017 | Heating & Cooling
I have a LG Inverter Art cool and after about 5 minutes it stops and C5 shows on the panel Kerrie
Fault Code 05.
This fault code indicates a communication error between the indoor and outdoor units; this is usually caused
by wiring errors or condensate pumps connected to the inter-connecting cable.
The communication between the units is a fluctuating DC voltage commonly called a serial signal, it can be
easily lost if the wiring is not done correctly. If there is a communication error fault CH05 will appear within 5
mins of powering up the system.
Testing
• Check Outdoor and Indoor Power Supply Voltages ( 230V ±10% ) and correct as necessary.
• Check for any mis-wiring or loose connections and correct as required.
• Check the resistance between communication line and GND. (Normal: Over 2M).
• If one Indoor unit operates normally Outdoor PCB is generally normal.
Turn on the power and start the indoor unit in cooling, set the temperature to 18ºC; the serial communication
signal will only be present for the first 3 mins of operation.
Set your meter to DC Volts, Test between terminals 5 (Red probe) and 2 or Earth (Black probe) of the outdoor
unit, you should see a fluctuating 0-72 Vdc.
If the Voltage is not present disconnect the terminal 5 cable, test the Voltage between this wire (Red probe)
and 2 or Earth (Black probe), you should see a steady voltage in the range of -0.1 to -10.0 Vdc. If No Voltage
is present either the cable or Indoor PCB must be faulty. This can be determined by checking the voltage
output on the Comms terminal of the Indoor unit, with the Comms wire disconnected. If No Voltage is present
the Indoor PCB must be faulty, if present, cable must be at fault. Helpful?
Jan 19, 2011 | LG Art Cool LA121CNP wall/window Air...
When the ac unit is on the water comes in the house
The condensate drain line is clogged, causing the condensation water to overflow. You can use a shop vac to clear the line. attatch it to the outlet side of the line. also clean out the condensate drain pan located at the bottom of the indoor coil.
Sep 25, 2009 | Amana MH09A3PA235 Comfort Zone Room Air...
Mitsubishi wall unit srk50zg condenser src50zg air con not heating new install
Double check your wiring .if the indoor fan is not blowing then you either have an electrical issue OR bad blower motor .
May 24, 2017 | Refrigerators
Heating & Cooling Logo
167 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen