Question about Goodman GMS90703BXA Heater
I turn the thermostat on and the furnace tries to turn on three times before it turns itself off. The first time I see the gas blower turn on but it does not light the furnace up. The next two times I do not see the gas blower turn on at all. After the third try the furnace shuts down. The LED light is blinking once. Is this an expensive fix?
    Novelist:
    Champion:
  • 266 Answers
This on blink of the light is a system lockout. It is caused when no gas is released to light the burner. The first thing to try is to turn the power off to the unit make sure your thermostat is off also. Turn the unit back on and make sure your gas is turned on. Then turn on the thermostat. Try this 3 or 4 times to make sure there is not air trapped in the gas line preventing ignition. If it lights after doing this you should check for a small gas leak at all fittings and shut off valves. The reason for this is to make sure you do not have a slow leak. If you smell gas turn off the furnace and your gas main valve and call a repair person. If you are unable to turn off the gas you should call the utility immediately. The cycle for your furnace is as follows. When your thermostate demands heat a signal is sent to your circuit board in the furnace and it turns on a exhaust fan to cause a draft to push air out the flu. (this fan is on 92% and higher funaces) This fan has two vacume lines that run to two vacume switches one is for the presence of vacume the other is for sensing the release of vacume. These are low voltage switches hooked into the 24v system. If the fan works and the switches sense vacume it then turns on the gas igniter this will be a glow bar and you will see it glowing. This in turn has a sensor that near it that can sense the heat from the glow bar igniter and it in turn turns on the gas by sending the 24v signal to the gas valve. If after 8 to 15 seconds the flame does not come on the system will reset and try again for a total of 3 times. If any of the above systems do not work your furnace will lock out because it thinks there is gas being dumped into the furnace. If the exhaust fan comes on you have 24v going thru your thermostat to the furnace. Then the vacume switches have to work. One is normally open the other normally closed. If you have a volt/ohm meter which can be purchased for as little as 10 to 15 dollars at a hardware store you can check these switches. You will need to set the thermostat to off and turn off voltage to your furnace for safety. Then locate the two switches by following the black rubber vacume lines from the exhaust fan housing to the switches. Pull the wires off the switches and with the meter set on ohms place the leads on the two terminals. While the meter is hooked up pull the vacume line off the fan housing and **** air in and out of the line the meter should swing back and forth as it senses vacume and the lack of it. If it does it is working. Then do the other vacume switch. Make sure to keep your wires and where the vacume lines go straight. You will also see a sensor mounted above and center where your burners are at it will have two wires going to it and it will be round it should show continuity ck it by removing the wires form it and touching the meter leads to the connectors the meter should respond showing continuity. There are two others under the burners on each side ck them the same. If any of your sensors have a pop ot button in the center press in on it yours should not this is an older version yours should be self reseting. The only other sensor is located in the blower for circulating the air. It is located on the right hand side of the blower housing with a red and yellow wire going to it. It has a reset in the center this sensor is used to trip if the heat in the blower housing gets to hot. This happens when the blower motor quits or is not able to move air fast enough due to restrictions. If the sensor has tripped you will feel and should hear an audible click when you press on the center button also if you check it for continuity it will show none and when you press the button it will show continuity. The next thing is the gas valve If all of the above work it is either the gas valve not opening or your circuit board. All of the parts are inexspensive until you get to the circuit board and the gas valve. The gas valve should be replaced by a repair person. You can replace everything else just make sure you turn off the power and pay close attention to the wiring. I hope this helps good luck. But not to down play the above make sure te top panel is in place put your hand on the gas valve and have someone turn on the thermostat. If the exhaust blower comes on and the ignitor glows you should then feel a click from the gas valve if you do not it us normally the circuit board. If you do and it still doesnt light you have no gas coming to your furnace. I hope this helps good luck
Posted on Sep 11, 2010
If I shut off the blower on my gas furnace do I have to shut down the whole furnace
Turn of the system at the thermostat. If you turn off the blower, assuming you mean at the tstat, there's no need to turn off the pilot. If blower is running and won't stop, even if turned off at tstat, turn off power by any means necessary, and pilot does not need to be turned off. A "standing pilot" is made to stay lit at all times, running or not.
Mar 07, 2017 | Heating & Cooling
I have a coleman furnace model 4066A656
Make sure your air filter is clean. Is the thermostat satisfied? or is the room temp. still below the thermostat setting? When ever you have to turn the power off and then back on to a furnace that usually indicates that the furnaces ignition control locked out. The first thing that I would try is cleaning the flame rod.
Mar 02, 2017 | Coleman Heating & Cooling
Intertherm furnace burner comes on, but blower does not. If I turn thermostat off then back on until it clicks the fan will then come on. It does not do this all of the time, just now and then.
Furnace burner and heat element are not the same. I think the fan time delay, a sensor that turns the fan on when this sensor senses heat, is shot and needs replacing, for a furnace type heat ( gas heat)
Aug 08, 2017 | Intertherm E3EB010H Electric Furnac
I have goodman GMP series furance the furnance and gas comes on and fires up then goes out flame sensor is good what else could be wrong
Improper ground from control to burner.
Incorrect electrical wiring, check polarity.
Tubing partially clogged between inducer and proving switch.
A sampling of various failure codes on a furnace:
Read one LED flash that stays on continuously to mean your furnace has no signal coming from the thermostat and will not operate. Turn the power off and check the thermostat for improper settings or connections.
Interpret one LED flash that blinks on and off to mean your furnace has locked out because it could not ignite after three tries, and must be reset. Interrupt power to your furnace for 20 seconds or lower the thermostat so your furnace does not try to heat, then reset the thermostat to the previous setting. After one hour of lockout, your furnace will automatically reset itself and try to operate as usual.
Decipher two LED flashes to mean the draft blower is not working, or your furnace has a short in the pressure switch circuit. Turn off the furnace power and repair a short or replace the pressure switch.
Read three LED flashes to mean your furnace has an open pressure switch circuit or it has an induced draft blower operating. Check the pressure switch hose of your furnace for blocks or an improper connection. Also, look for blockages in the flue, and tighten any loose wiring.
Translate four LED flashes to mean your furnace has a primary limit circuit open, possibly from loose wiring or blocked filters. Check and clean filters, tighten wiring and check the flue for blockages.
Interpret five LED flashes to mean your furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.
Read seven LED flashes as a warning of a low flame sense microamp signal. This could happen with a coated flame sensor or a lazy flame from poor gas pressure. Turn off the power and adjust the gas pressure according to the information on the rating plate.
See eight LED flashes as meaning an igniter circuit problem due to a bad igniter or an igniter connected improperly. Replace the bad igniter or check the ground wiring, making necessary corrections.
Decipher nine LED flashes to mean the high-stage pressure switch circuit will not close during a high-stage-induced draft blower operation. Your furnace may have a pinched or blocked pressure switch hose, a blocked flue or loose wiring.
Read continuous flashing on the LED to mean your furnace has a reversed polarity of 115 volts. Turn off the power and correct the wiring polarity after reviewing the wiring diagram.
Oct 18, 2011 | Goodman GMS90703BXA Heater
Goodman furnace GMP075-3 The thermostat was in the off position over night and sometime during the night, the induced blower and blower motor came on. The trouble light on board blinks 5 times. I checked...
Need your model # to check the codes but, this coming back on after turning the t-stat off is rare. You may have been in a lockout and the furnace re-started. Some furnaces try to start three times , then lock out. Time out, then re-start. The codes should be on your furnace blower door. Write back with this info and i could help.
Oct 12, 2011 | Goodman GMS90703BXA Heater
I have a Johnson aire ease ultra 90 gas furnance. I also have a outdoor wood furnance that has its own thermostat. On the original thermostat I turn the blower in the on position. I then set the outdoor...
I would first eliminate one furnace from the equation, the exterior wood furnace... turn its tstat down. Will the gas furnace then operate normally? Can you run the blower manually, as in summer mode? Make sure your filters are clean also... that can sometimes overload the blower.
Apr 12, 2017 | Heating & Cooling
My furnace the burners light and come on and heat up the unit. But the fan never kicks on and blows. The fan itself works because I can turn it on manually so I know it's not that. The trouble code...
The manual selection on the thermostat bypasses the fan relay. When in Auto, the fan relay turns on the blower. You are probably looking at replacing the circuit board. As far as the three blinks, on the reverse side of the front panel there is a wiring diagram and error code chart. It will give you a starting point where to look for a problem. The three blinks could indicate an open limit because the blower is not operating. Keep the blower on manual and let the furnace run normally until you can figure out what the problem is.
Feb 23, 2011 | Intertherm Heating & Cooling
Suddenly not working im not sure if there even is a pilot to be lit
Goodman have troubleshooting idiot lights on the board. Look for flashes and count em.
The flash explanations are printed on the backside of the blower cover on most models.
Feb 03, 2011 | Goodman Heating & Cooling
My central heating is on lockout and the burner is with red light
A sampling of various codes on a furnace
Interpret five LED flashes to mean your Goodman furnace senses a flame without a call for heat. This could be from a gas valve closing slowly or a burner flame lingering.
Dec 02, 2010 | Heating & Cooling
I have a Carrier 58SX060 Furnace with air. I turned the thermostat to heat and the exhaust comes on and runs and the pilot comes on but the burner never light s and the blower never comes on. If I turn the...
carrier gas furnaces will try to light three times then will usually go on a lockout for one hour you can bypass the lock out by resetting the power, turn furnace on, remove wires from gas valve, you will need a multi meter to check for voltage to valve, if control board sends a call to the gas valve the valve is bad, if voltage is never present during the lighting cycle your control board is bad
Sep 30, 2009 | Heating & Cooling
Goodman GMS90703BXA Heater Logo
286 people viewed this question
Top Goodman Heating & Cooling Experts
Dan Webster
Dan Webster
paulcarew
Brandon Berry
Brandon Berry
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others