Heil outside fan motor 3 wire rd/blk/br new dayton motor 4 wire blk /br /purpule /brown with white strip Need help on wiring
  • a87turbogn Sep 09, 2010
    There was more to my previous post but it did not print....Any how all are connected as stated but, still nothin. So I carefully depressed at contact and comp
    President:
  • 1,515 Answers
Hi, the new motor takes its own capacitor to run it. This is what the 2- brown wires are for, one will have a white stripe. You will need to but a seperate run capacitor for this motor, a 5 uf, 7.5, or what ever it calls for. they should have told you when you bought the motor. It will have to spade connectors on it where the brown wires connect alone. Use the dual capacitor if that is what you have for the other 220 volt wires.Black and purple will be your 2 hot wires.You can connect either one to the old capacitor on the fan terminal and the other to the load side of the contactor, so when the contactor closes it will energize the motor.Or, take both the black and the purple wires and to the load side ( outlet side ) of the contactor, connect one to one side and the other to the other side. The line side is where your 2 hot wires that connect to the contactor from the incoming wires from the electrical box, you want to be on the other end. I would connect the black to the contactor load side and purple to the old capacitor as long as the old wiring is still on it as it has to be fed by a hot wire from the contactor. Each wire, blk, and purple has to have 120 volts to each one and you can get this a couple of ways. The contactor has several terminals that are not used and if you wire them on the outlet side, they will only be energized when the contactor is closed on a call from the stat, very easy to do. You will have to get a coulple of crimp on connectors to put on the ends of the wires, but the brown ones should already have them for this capacitor. Do not try to put the brown wires on the old run capacitor as you will burn out the new motor! Go get the small run cap for these 2 wires for about $10. I know that you can do this wiring change just remember the blk is hot 120, and purple is hot 120, = 240.volts. If you have removed all of the wires from the old capacitor, then use the contactor to connect to. The compressor wires must stay on the old run cap on the hermetic side and this old cap. must be fed by a hot wire from the contactor to the common terminal, that is marked with a C..If you look at the new motor diagram, it will show you also. Please dont forget to rate me as I know you will be kind, and I will check in on you to see how you are doing. Get this capacitor and it will run. This is a must!! Please keep me posted.
Sincerely,
Shastalaker7
A/C, Heating, & Refrigeration Contractor
Posted on Sep 07, 2010
Testimonial: "Very knowledgeable. Easy to follow directions. Truely knows their field."
  • 6 more comments
  • a87turbogn Sep 07, 2010
    Thank you for your help. The old 3 wire motor had the blk wire conecting to the defrost circuit board. How does the new 4 wire motor connect to this? 5 days in FL without a/c is brutal..
  • Robert Horton
    Robert Horton Sep 07, 2010
    Connect the blk wire to this defrost board as it is half of your 220 volt circuit to run your motor. I am glad you told me this. Now, you have the purple wire to deal with, You can connect it to the load side of the contactor or if the old capacitor is wired up to run the compressor, you can get the other 120 volts from there.
    Please let me know. I will be home from work at 5:00 P.M., which would be 6:00 your time, I believe.
    Shastalaker7
  • Robert Horton
    Hi, am am home early. Just keep in mind that the 2- brown wires, one with white stripe, stand alone on the new capacitor to run it. So that just leaves the black and purple. Now that I know you have a heat pump, one lead will go to the defrost board to stop the condenser fan motor when it goes into defrost mode in the winter months. So, all you need to deal with is the purple wire which is the other half of the 220 volts to run the motor along with the new 2- wire run cap. You can either put it on the contactor ( part that has points in it on 2- sides ) that closes when the thermostat calls for cooling and sends 220 volts to all high voltage motors, or if you had a dual capacitor on this unit with 3- sets of terminals coming out the top, marked Herm, Fan, and C for common, you can connect the purple to one of those terminal as you are only using the terminals for the compressor to run now. The fan will not be connected there as you removed the motor terminals. This will give you full 220/240 volts or what ever it may be to run the new motor. Just remember, you will HAVE to add this new 2- terminal capacitor for this motor to run properly, or it will burn out.
    Sincerely,
    Shastalaker7
    A/C, Heating Contractor
  • Robert Horton
    Robert Horton Sep 08, 2010
    Connect the 2 brown wires to the single run cap alone, do not tape off one and connect the other to the fan connection on the old cap. You can connect the purple to the C or common terminal if you haven't removed the compressor wires from it, but like I said before, you can look at the motor and it will show you how to wire it.
    Shastalaker7
    Bought new run cap.connected brn/wht
  • Robert Horton
    Robert Horton Sep 09, 2010
    Good, now connect the black to the defrost board and the purple to the common on the other cap if all the wires are still there and if is hot, or connect it to the contactor, one terminal on the load side for 120 volts and it will run when you turn on the stat.
    Shastalaker7
  • Robert Horton
    Thank you for your the awesome rating and I am glad you were able to follow my instructions as I tend to write out long statements so the person I am helping can get the most from them. I am glad it worked out for you,
    Shastalaker7
  • amazer Oct 09, 2012
    Very helpfull thank you
I have a ge used good motor for a ac unit that has 3 wire,black,yellow/brown.. the old motor is out need to wire the used motor whitch i know is good but,old heil motor has 4 wire black,brown,purple/blue and red and the other is a ge motor that has just 3 wire how do i wire this in please help Daniel
Posted on Jul 25, 2011
  • 674 Answers
This motor can be connected using just three of the four wires. Put a wire nut on the brown/white wire. Connect the brown wire to the fan terminal on the capacitor. Connect the purple to the common terminal on the capacitor. Connect the black to the defrost board. There should be instructions printed on the motor label for connecting the motor this way. The brown/white wire is the same as the black wire electrically. If you connect an ohmmeter between the black and brown/white wire you should read close to 0 ohms.
Posted on Sep 08, 2010
4 Suggested Answers
  • 143 Answers
SOURCE: CHANGING OUT A FAN MOTOR
The black and white wires get 220 from the contactor. The brown and brown/white go to the capacitor. I do hope you bought a matching capacitor to go with the new motor. They don't cost much and make the hook-up way easier.
Posted on Jul 25, 2008
burzerko
  • 254 Answers
SOURCE: HELP!!! Help wiring new motor for CKL60-1
  1. This is what your wiring should look like if you are using two caps. then you should be using a potential relay as well. This is the diagram for using a potential relay. Hope it helps you.
Posted on Aug 28, 2008
Sea Breeze
  • 4654 Answers
SOURCE: replacing old 3 wire condensor fan motor with new 4 wire
The extra wire is a additional speed wire and the existing model that you are installing is possibly not set up for that additional speed. It depends on the exact model of air conditioner that your post says you have, but we can never be sure until you confirm the model number of your Goodman, if its a split unit, a package unit or condenser fan or evaporator fan. Let me know all of those answers and I will help you determine the answer, Thanks, Sea Breeze
Posted on May 08, 2009
Replaced a ge condensor fan 3 wire with new dayton the wires are different...old fan has a wire connectort mouted to it orange,black yellow, the new one 2brown 1 with white stripe, purple, black, i have...
the new ge fan requires its own capacitor, the brown and the brown/white go direct to new fan capacitor. black to relay (leg one of power) purple to relay (leg two of power. the compressor will have a wire to the relay and the other to the herm terminal. you now will have nothing to the original capacitor fan terminal.
The new motor will have the diagram showing this. you need the capacitor that goes with the new motor. the grainger guy should have sold that to you with the motor.
Apr 11, 2013 | Heating & Cooling
I need a wiring diagram for a dayton 120/230 v capacity start motor model 6k157 or equivalent
I have dayton motor 3/4 hp 120-240v it has 3 contacts 1-2& 4 it has 5 wires 2 white 2 red 1 blue. I want forward rotation! what do I do?
Jan 14, 2011 | Dayton Permanent Split Capacitor Motor Fan
I have an old york unit model #HICF030506a and just replaced the fan unit but forgot where to connect the 4 wires . I have a tan, tan w/white strip , black , and purple wire. Can anyone help???
Did the old fan use 4 wires or 3 wires. If it used 4 then connect the brown and brown/white to the capacitor. Then connect the Black to L1 and Purple to L2. If it used 3 wires then tape up or put a wire nut on the brown/white wire. Connect the brown wire to the Fan terminal if the capacitor has 3 terminals or to either side if it only has 2 terminals. Look at the motor data plate. It should have the wires labeled on it. Purple should be the run wire, connect it to the Comm terminal of the capacitor if it has 3 terminals or the opposite side from brown if it has 2 terminals. Another wire should go from this connection to L1. Then connect the Black wire which is common to L2. I hope this isn't too confusing. Let me know if I need to explain it better. Also if the motor data plate says that Black is run and Purple is common just adapt the instructions above to the wire colors.
Aug 27, 2010 | Heating & Cooling
Replaced old Ge 1/2hp fan blower motor w/ emerson motor wire not the same couldnot get to work. motors has blk,blue,red,white/brown, brownw/white strip/furance wires are blk,red,white could some tell me...
I am assuming you still have both motors, if you look on the side they will show you what wires go to what. Your Brown/white should be for the capicator. blk should be blk, blu might be white and red be red. I couldn't really say for certain with out looking at the diagram on the side of the motors. I hope this helped Tim
Aug 02, 2010 | Heating & Cooling
"i'm replacing my Rheem RBGC 08KA FAU blower motor. My dayton 3lu83j 4 speed motor has white, black, red, yellow,orange, brown, and brown with stripe wires. My old westinghouse motor has only one brown...
There should be a wiring diagram on the side of the new motor.
The brown and the brown w/ white go to the new capacitor you should have bought with the motor.
The black and white go to your L1 & L2 power source. The remaining wires must be capped off.
Feb 25, 2010 | Dayton Heating & Cooling
EMERSON FAN MOTOR WHICH HAS A BLK WIRE PURPLE WIRE AND A BROWN WIRE WENT DEAD. SO I BOUGHT A NEW FAN EMERSON CAME WITH 4 WIRES BLK ,WHITH, BR AND BRW AND BRW WITH WHITE STRIPE. I WIRED IT BLK TO THE...
The two brown wires go to the fans capacitor. The capacitor should always be changed with the fan motor.
It sounds like your unit has a dual capacitor. One side for the fan and the other for the compressor. All you will be doing (After rewiring the compressor wires as they were originally.) is abandoning the fan side of the capacitor, and wiring your new capacitor to the brown and brown with stripe wires. It does not matter which terminals the brown wires go on.
Oct 11, 2009 | Dometic Rooftop RV Air Conditioner
THE WIRING ON THE FAN CLUTCH GOT CUT AND THE WIRES FROM THE TRUCK ARE YL/RD,BLK/RD,GREEN/GRAY,RD/GREY,GREEN THE WIRES FROM THE CLUTCH ARE RD,GREEN,WHITE,ORANGE,BLACK. TRYING TO BE SURE BEFORE I CONNECT...
1) ECM Fan Clutch 1) K160 18BR/OR Park Lockout Solenoid Control Green
1) BR / OR = Brown/Orange unit with Green
2) K900 18DB/DG Sensor Ground 2) Black
2) DB / DG = Dark Blue/Grak Green unit with Black
3) K161 18BR/LB Fan Speed Sensor White
3) BR / LB = Brown/Light Blue unit with White
4) Not Used
4) Not Used
5) F856 18YL/PK 5 Volt Supply Orange
5) YL/PK = Yellow/Pink unit with Orange
6) F504 20GY/PK Fused Ig. Sw. Output Red
6) GY/PK = Gray/Pink unit with Red
With this, you have 5 due color cables unit to the 5 full color cables. Run.
Good luck, and rated this help (and us chat).
Aug 27, 2009 | 2004 Dodge Ram 3500 Truck
Condensor fan runs after compressor shuts off
If new motor is 4 wire verses 3 wire use seperate capacitor between brown wires and don't use terminal on 3 pole cap. If this motor has a white strip on one brown wire you can wire it the old way using only 1 brown wire and tape off the other. Can't remeber this morning which brow wire to use . I need to leave. Goole replacemotor with 2 brown wires for more info or call where you bought it. Sorry got to run.
Jul 01, 2009 | Weather King 12AJA4801AH Air Conditioner
Wiring a 220v single phase motor and capacitor
Black and white are usually power. an ohmmeter will confirm. Brown are for capacitors. There is almost always a diagram on the motor someplace. Eric
Jun 17, 2009 | AO Smith A O Smith Motors Century 1hp 115v...
Trying to install a fan motor for my outside ac unit replacement motor has 5 wires on it. my old on had only 3 driving me nuts
Your old moter had three wires. Common High and brown for capacitor. This one sounds like a two speed. Dont worry Now you have two brown wires for you capacitor instead of one. Tape off brown wire with white strip. Connect other brown to cap. You should have a white or yellow for common wire and black for high. Tape of the other extra wire and wire in like the three wire. Rusty
Jun 03, 2009 | Continental CE-PAC1163 Air Conditioner
Goodman CLQ36AR49 Air Conditioner Logo
1,491 people viewed this question
Top Goodman Heating & Cooling Experts
Dan Webster
Dan Webster
paulcarew
Brandon Berry
Brandon Berry
Are you a Goodman Heating and Cooling Expert? Answer questions, earn points and help others