Raypak 2100 r405 wiring? has one red, one white and red, one black, one white and black and green ground. How do I wire for 120
  • 990 Answers
Wire the red and red tracer toghther and the black and black tracer together then wire these to your 110v lines then green to your green.
Posted on Sep 06, 2010
I have a new heater with diferant terminals from the old one so not sure how to atach the wires
There is no need to rewire the internal of the heater!
Just bring in the electrical supply to the heater, it can be either 120 or 240 volts.
If the heater you have is like the picture associated with your post, then all then have to do is change the supplied plug from 240 to 120. It comes pre set for 240. That plug is inside the cabinet.
If any other brand, then you need to change the wires at the transformer of the heater. All heaters need to be supplied with primary voltage: 120 or 240. Then the control system is supplied with secondary voltage out of the transformer. The secondary voltage is no more than 28 volts. and these wires are normally colored as blue or yellow.
Secondary power is already wired within the heater. NO need to change where they are. You will only need to deal with the Primary wiring.
There are many varieties of transformers that transform high primary voltage to a low secondary voltage of 28 volts. and these transformers have many wires: primary & secondary.
I will try to make this easy to understand.
If you have a Gas Heater Transformer with these colors:
  • Red
  • Black
  • White
  • Green
Or...
  • Red
  • White with Red Stripe
  • Black
  • White with Black Stripe
  • Green
These are Dual Voltage Transformers, you can bring in either 120 Volts or 240 Volts
If you bring in only 120 Volts...
1st example:
The Red wire will not be used! Hot wire to the Black, and the Neutral/Common, to the white wire. Green to ground.
2nd example:
Connect the Red wire with the White with Red Stripe together and connect these to the incoming Neutral/Common wire, normally White.
Connect the Black Wire with the White with Black Stripe to your incoming Hot Wire, which is normally Black.
Green to ground
If you bring in 240 Volts...
1st example.
1 Hot wire to the Red, the Other Hot wire to the Black, and White wire is not used. Green to ground
2nd Example:
Wire nut the two Striped wires together. then one incoming Hot wire to the Black, the other incoming Hot wire to Red.
Green to ground
Or This is only a Low voltage - 120 Volts Only
  • Black
  • White
  • Green
Or either any of these combinations...
  • 2 Blacks w/Green
  • 2 Reds w/Green
  • 1 Black, 1 Red w/green
This type will only be a high voltage, 240 volts only
Picture below is what a transformer looks like and it is where your incoming supply wires go. The smaller leads with the spade connections will go to a specific location & is the 'Secondary" .
Good Luck
Mar 14, 2015 | Pool & Spa
Tip
How to wire Intermatic T103 and T104 timers
These instructions are for USA residential wiring only.
VERY IMPORTANT: Understand that in US residential wiring the WHITE wire is _NOT_ ALWAYS_ the neutral wire. Additionally, prior to 1999 the National Electric Code (NEC) did not require that these white wires be re-identified with black tape or similar means when used for purposes other than neutral. The white wire is sometimes used as a hot, especially when wiring Intermatic T103 and T104 timers.
Also understand that the WHITE neutral wire and the bare (or green) equipment grounding wire are connected together ONLY at the main electric power panel and must _never_be connected together _again_. Once those two wires leave the main electric panel, the WHITE neutral wire must _always_ remain insulated from the bare or green equipment grounding wire. This is very important for safety considerations.
If your wiring is very old and does not have a bare equipment grounding conductor, you _must_ protect the circuit with a GFCI (Ground Fault Circuit Interupter). GFCI wiring is not difficult but is beyond the scope of this post.
DETERMINE WHAT CABLE YOU HAVE:
Usually one will find one of the three following scenarios for the incoming supply cables when wiring a T103 or T104 Intermatic timer:
1...A 120 volt cable with 3 wires: black, white, and bare. The black is LINE (hot), white is neutral and bare is equipment grounding. Black to white is 120 volts. This scenario can be used with the T103, but not the T104.
2...A 240 volt cable with 3 wires: black, white, and bare. The black is LINE(hot), the WHITE is LINE (HOT), and the bare is equipment grounding. Black to white is 240 volts. This scenario is used with the T104 ONLY.
3...A 120/240 volt cable with 4 wires: Black, red, white, and bare. The black and red are (LINE) hot, white is neutral and bare is equipment grounding. Black to red is 240 volts. Black to white is 120 volts. Red to white is 120 volts. This scenario can be used with either the T103 or the T104.
The only difference between the T103 and the T104 is the timer motor voltage rating. The T103 uses a 120 volt timer motor and the T104 uses a 240 volt timer motor. The T103 timer motor is connected to terminal "A" and terminal #3 during manufacturing. The T104 timer motor is connected to terminal #1 and terminal 3# at the factory.
Also, when connecting the bare or green wires to the "GR" terminal, it is best to wirenut the wires together with a pigtail, then connect the pigtail to the "GR" (GRound) terminal, WHICH IS THE GREEN SCREW ON THE LOWER PART OF THE CASE.
WIRING THE TIMER:
The wiring diagram for the T103 is here:
http://www.progressive-growth.com/wiring/T103.pdf
___________________________________________________________________
WIRING THE T103 USING AN INCOMING 120/240 VOLT CABLE WITH 4 WIRES (scenario #3):
Incoming (LINE) wires from 240 volt circuit breaker:
Connect the black (LINE)(hot) wire to terminal #1. Connect the red (LINE) (hot) wire to terminal #3. Connect the white (neutral in this case) wire to terminal "A".
Connect the bare equipment grounding wire to the "GR" terminal, which is the green screw on the case.
Outgoing wires to 240 volt load:
Connect one (hot) wire to terminal #2 and the other (hot) wire to terminal #4. The bare or green wire goes to the "GR" terminal.
WIRING THE T103 USING AN INCOMING _120_ VOLT CABLE WITH 3 WIRES (scenario #1):
Incoming wires from 120 volt breaker or source:
Black (LINE) to terminal #3. White (neutral) to terminal "A". Bare to the "GR" terminal.
Terminals #1 and #2 are NOT used in this case.
Outgoing wires to 120 volt load(s):
Black(hot) to terminal #4. White(neutral) to terminal "A". Bare to the "GR" terminal.
The wiring diagram for the T104 is here:
http://www.progressive-growth.com/wiring/T104.pdf
WIRING THE T104 USING AN INCOMING 240 VOLT CABLE WITH 3 WIRES (scenario #2):
Incoming (LINE) wires from breaker:
Connect the black (LINE) (hot) wire to terminal #1. Connect the white (LINE) (hot in this case) to terminal #3. Connect the bare wire to the "GR" terminal.
The "A" terminal is _NOT_ used.
Outgoing wires to load:
Connect one (hot) wire to terminal #2 and the other (hot) wire to terminal #4. Connect the bare or green wire to terminal "GR".
WIRING THE T104 USING AN INCOMING 240 VOLT CABLE WITH 4 WIRES:
Same as above, except the white wire is not used. Just tape or wirenut it off.
on Dec 28, 2009 | Hardware & Accessories
I have a Raypak RP 2100 R405 pool heater. When I
Yes its faulty PC board.As no Power Coming from the board.Click this link directly to get PC board. http://www.a1poolparts.com/-strse-Heaters--dsh--Parts-cln-Raypak/searchpath/1015892/start/61/total/103/Categories.bok ------------------ To confirm the fault in PC board. Check for exact 24 volts on PC board. One yellow and One Blue wire. --------- For checking transformer check 120/240 volt to transformer(time clock circuit breaker wire connections). Thanks. Keep updated for any more query. You can rate this solution and show your appreciation.
Jul 10, 2010 | Raypak Rp2100 Pool & Spa Heater Lonox 407k...
Need wire configuration for pioneer deh 2100 cant figure out what color wires are what?
red- accessory
yellow-constant power
black -ground
blue with white stripe-romote ''if any
blue- power antenna
speakers wires'''''''''''''''''''''''
white - postive
white with black stripe-negative]-left front
gray-positive
graywith black stripe-negative]right front
purple-positive
purple with black-negative]right rear
green-poditive
green with black-neegative]-left rear
white
Oct 13, 2009 | Pioneer DEH-2100 CD Player
Jenn air model JED8430bdb
A similar concern on a different model (8230):
To my knowledge, the:
green - ground
white - neutral
black - 120 to ground
red - 120 to ground but between red & black, it should be 240. A Jenn-Air JED8230 requires a 3-wire, 120/240 Volt, 60 Hz Outlet.
Pls consult/confirm with your local electrical utility/codes the availability/applicability of this power/wiring system or reference National Electrical Code, NFPA No. 70
Hope this be of initial help/idea. Pls post back how things turned up or should you need additional information.
Good luck and kind regards.
Thank you for using FixYa.
Mar 12, 2008 | Jenn-Air JED8430 Electric Cooktop
I am trying tochange my
This is common issue. Due to some building codes the 3-prong configuration is no longer used in homes. The wiring is similar with one exception. The 4-wire plug uses an additional (WHITE) NEUTRAL wire.
Here's a brief explanation of how the plugs are configured:
Dryer 3 prong wire configuration:
RED - 120 VAC
GREEN - GROUND
BLACK - 120 VAC
Dryer 4 prong wire configuration:
RED - 120 VAC
GREEN - GROUND
BLACK - 120 VAC
WHITE - NEUTRAL
BOTH plugs provide the SAME source voltages to your appliance:
220 VAC - provided across the RED and BLACK leads are what drives your heating circuitry.
120 VAC - usually tapped of the BLACK wire is used to run the drive motor and timer on MOST dryers.
The wire terminal block in the back of the dryer should have a black, white, and red wire running to it from the dryer wiring harness. With the 4 prong plug, simply attach the BLACK, WHITE and RED wires at the terminal block ensuring that you match the RED and BLACK wires as they are configured and attach the WHITE wire at the remaining terminal lug. Make sure you screw them all down securely. Attach the remaining GREEN wire to chassis (dryer frame) ground. I hope this helps you.
Feb 29, 2008 | Dryers
REPLACING DRYER 4 PRONG PLUG
This is common issue. Due to some building codes the 3-prong configuration is no longer used in homes. The wiring is similiar with one exception. The 4-wire plug uses an additonal (WHITE) NEUTRAL wire.
RED - 120 VAC
GREEN - GROUND
BLACK - 120 VAC
RED - 120 VAC
GREEN - GROUND
BLACK - 120 VAC
WHITE - NEUTRAL
The wire terminal block in the back of the dryer should have a black, white, and red wire running to it from the dryer wiring harness. With the 4 prong plug, simply attach the BLACK, WHITE and RED wires at the terminal block ensuring that you match the RED and BLACK wires as they are configured and attach the WHITE wire at the remaining terminal lug. Make sure you screw them all down securely. Attach the remaining GREEN wire to chassis (dryer frame) ground. I hope ths helps you.
Feb 14, 2008 | Dryers
Wiring installation
You do need a 208/240 volt supply from your service panel. The green is ground, white is nuetral, and the red and black should measure 120 volts each to ground or 240/208 between each other. It is normal for most breaker panels to supply 208/240 between adjacent insulators. If you are only getting 1/2 of that then the circuit breaker may not be straddling the insulator bar but be 1/2 notch out and both breaker pins contacting the same 110 supply.