Question about Panasonic Heating & Cooling
All our our Panasonic Split Type air conditioners in our plant do not operate when power source is taken from a power generator set but the Carrier brands operates well. What could be the reason for this problem?
  • Panasonic Master
  • 3,740 Answers
The genset power most likely is 220V line to ground power. You utility power is 220V line to line but uses 2ea 110 VAC line inputs to get that 220VAC. The only way to correct this is to reconfigure your generator connection to 220V line to line IF possible. Some generators that only have a 220V output. Re-configuration is not possible
Measure power at the breaker on gen power as the source and again with the utility as the source. You will see the difference in voltages. Utility power.... each side of the Breaker output to ground = 110V across the 2 terminals 220V
Gen power one side of the breaker output = 220V other side = ZERO.
You can make it work but it would take some heavy duty relays in a power sub paenl so that when the generator is running one side of the power is 220V and the other side is Ground. Once utility power is restored the relays would disengage and power would again be 220 VAC line to line.
You will need a licensed electrician and a PERMIT to install a relay panel such as I mentioned above. Improper wiring of the power relay swtitching panel can cause major power problems in any given installation and trip the MAIN PWR breaker.
Thanks for choosing FixYa.
Kelly
Posted on Sep 05, 2010
WHAT IS FAULT CODE 00 01 Ad on Teco LU160DHRA1 Air Con
Carrier Split Air Conditioner Error Codes - AC Error Code
acerrorcode.com/carrier-split-air-conditioner-error-codes.html
Jan 25, 2015 - REMOTE CONTROLLER FOR AIR CONDITIONER (SPLIT TYPE). Carrier Split Air Conditioner Error Codes. 00-01-02-03. 11-12-04-05.
Nov 25, 2015 | Heating & Cooling
The indoor of carrier split type aircon is having a heating function, if they have , how can I set in the remote control
The Split system control is not working and you need to check thermostat wirings and the control on the splitter
Jan 12, 2015 | Carrier Heating & Cooling
Split type aircon
It sounds to me that the air con is on auto fan, as the room gets hotter or colder the fan will slow down and stop. keep the fan on low,med or high fan speed
Apr 02, 2014 | Carrier Heating & Cooling
Need to know the tonnage ofCarrier s/s Model #38ARZ008, ser # 1404G20031
Brand: CARRIER Manufacturer: CARRIER CORP SYRACUSE Model Number: 38ARZ008(5/6)0 Condenser Type: air-cooled Coil Model Number: 40RM-008--B5/6GC System Configuration: Split System Air Conditioner Energy Efficiency: 10.6 EER Cooling Capacity: 90,000 BTUs / hour ARI Type Code: RCU-A-CB Electrical Service: Triple-phase Electrical Input: 8,490 watts per hour Voltage: 230 and 208 and 460
12000 btu's per Ton, equals to 7.5 Tons.
Sep 29, 2010 | Carrier 38CKC042 Air Conditioner
Where can I get mode control sw.
You might have to source the same type only from Carrier without trying to put in a replaccement type.
so check on their main website
www.carrier.com
Sep 15, 2010 | Carrier XCD121D Air Conditioner
My carrier split type non-inverter aircon always blinking
It indicates afault within the unit. Give Carrier a call and get it serviced.
Mat
Jul 01, 2009 | Carrier 36KCARMS Air Conditioner
Not turning on
Hi
Try to reset the unit by disconnecting the power supply for 10sec. and operate the unit. If it wont work replace your Room Air and Coil Thersmistor or test the thersmistor with mulitester. The resistance reading of thermistor is 10 kilo ohms @25deg. C room temp. If it is shorted or open the unit wont operate.
Hope this can help :)
Dec 30, 2008 | Carrier 36KCARMS Air Conditioner
Heating & Cooling Logo
100 people viewed this question
Top Panasonic Heating & Cooling Experts
Bill Long
Fotis Papastamatiou
Dennis Boxerman
Are you a Panasonic Heating and Cooling Expert? Answer questions, earn points and help others