Question about Carrier 38CKC036 Air Conditioner
The amp meter reading jumped to over 20 A and then back to 0.5 A, repeat again and again. The compressor did not start and no cool air was available What could have been the problem of my Carrier split type home unit.
    President:
  • 3,773 Answers
Check inside and outside coils for cleaning with coil cleaner spray
purchase a hard start kit compressor relay from Appliance parts store (instructions to install are on the pkg)(easy job)
Check capacitor(remove and take to appliance parts dealer. They will checkit)(easy job)
If this was helpful please rate me.
Leo Ponder Appliance-Tyler,Texas
imufo2@sbcglobal.net
Posted on Sep 04, 2010
Likely cause??? Upright 2006 Frigidaire freezer quit cooling. Only slightly cool air coming into the freezer box. READING 45psi ON THE LOW SIDE of the compressor. Frigidaire model PLFU1778ES2.
Troubleshooting Thermistor Problems in Refrigerators FREEZER /FRIDGE NOT COOLING: Optimum refrigerator temperature at or below40° F(4° C). The freezer temperature should be0° F(-18° C). Check temperatures periodically. Appliance thermometers are the best way of knowing these
Check ur cold control thermostat, ur thermistors in both fridge and freezer ( they should be checked for both ohms and for amount of current being put out as per ur model ), ur air flow vent from freezer to fridge.( to make sure it opens and closes without any restrictions) On thermistors check for A close circuit and amount of ohms not just an Ohm reading. As per ur model. Most should atleast show 1200 ohms. Also Check door seals for leakage.
Evaporator coils
Poor cooling is often the result of a heavy frost build-up on the evaporator coils. You can't see these coils without removing a panel on the inside of your freezer. A sure sign that there is a build-up is the presence of any frost or ice build-up on the inside walls, floor, or ceiling of the freezer. Such a frost build-up usually indicates a problem in the self-defrosting system or damaged door gaskets.
If one of the components in the self-defrosting system fails, the refrigerator continues to try to cool. Eventually, though, so much frost builds up on the evaporator coils that the circulating fan can't draw air over the coils. There may still be a small amount of cooling because the coils are icy, but with no air flow over the coils, cooling in the refrigerator compartment is quite limited.
FAN check to see if it is operating or restricted A fan that is not blowing or restricted will not circulate the cold air properly.
Often, the first thing that folks do when their refrigerator starts to feel warm is turn both controls on the coldest settings.This is exactly the WRONG thing to do.Turning the cold control to the coldest settingwillkeep the compressor running longer and make lots of cold air.
But turning the air door to the coldest settingclosesthe airway to the food section. Lots of cold air is made, but most of it stays in the freezer section, and the food section actually getswarmer.
Condenser
Self-defrosting refrigerators all have a set of coils and a cooling fan, usually under the refrigerator, that need to be cleaned regularly. If these coils get coated with dust, dirt or lint, the refrigerator may not cool properly. The coils may appear to be a thin, black, wide radiator-like device behind the lower kick-panel. To clean them, disconnect the refrigerator from the power source, use a refrigerator condenser brush and your vacuum cleaner to clean the coils of any lint, pet hair, etc. You may not be able to get to all of the condenser from the front, it may be necessary to clean the remainder of the condenser from the rear of the refrigerator.
May also need to check the defrost timer, u can get by and test manually by placing a small screw driver into the tiny slot or hole underneath the timer and turn slowly clockwise till u hear 1 click. this will engage ur defrost cycle in about 15 minutes u should be able to come back and feel the heat in freezer as it melts the ice providing ur terminator is not bad?
Another way to test it is with a multi meter. Remove timer it from fridge and you will see 4 prongs numbered 2,1,4,3 in that order. Place ur meter prong on prong 1 & 3 (if your fridge has a capacitor wired in series with the windings, then u check for micro fares rather than OHMS) If u cannot confirm this test, still try the next.
Take ur meter prong and connect to prong 1 & 4, it should read resistance or ohms ( closed) now remove prongs and place on prong 1 & 2, this should now read infinity or open (no ohms) now take a small screwdriver place it in the tiny hole or slot under the timer. Turn it clockwise slowly till u hear 1 click. Now ur 1& 2 should read closed ( showing ohms or resistance) now place meter prongs on 1 & 4 and you it should now show open ( or no resistance - no ohms) this is how u know ur timer is good, Remember when testing for ohms ADJUST meter to use a high ohms rating in the thousands as the resistance is very high in OHMS. And adjusting to low ohms rating may give a false reading or not show the proper resistance..
THE COMPRESSOR:
If you hear a clicking sound coming from the back of your refrigerator/freezer, then the problem is most likely the compressor, relay and or capacitor is overheating or not getting proper power and will not start.The compressor is the component on your refrigerator that allows your refrigerator to cool. If this component is not working properly your refrigerator will stop cooling. Most of the time the compressor is not the component that has failed.
To check ur compressor with multi meter:
Disconnect and remove the relay and capacitor from compressor, some located next to compressor in a casing.
You wills see 3 prongs coming out of compressor. 1 goes to ur srtart winding, 1 goes to ur run winding and the center goes to ur ground.
Place ur meter connector or prong on the start prong and the other on the ground (center prong) take note of the reading in OHMS for example 5 ohms.
Next place meter prong on run prong and the center ground prong agin. Take note of the reading in OHMS. Example 4 ohms
Next place meter prong on the start prong and the other on the run prong, now take note of the reading example 9 ohms. Now match the total of this ohms test with the total of ur two separate test. 9 ohms, if they match ur ok give or take 5 percent plus or minus. One more test to make to test of there is a short in compressor attach meter prong to ground prong and rub the other end of meter prong to metal ( scrape the metal clean of paint and test on metal surface not painted surface. If it shows continuity or ohms , u have a short in ur compressor. It should show infinity
TO REPLACE RELAY AND CAPACITOR WITH A HARDSTART KIT YOU CAN USE
A 3 in 1 start kit for compressors sizes 1/4 through 1/3 HP. And a 5 in 1 for higher H.P. (BE SURE TO MATCH WITH UR COMPRESSOR MODEL NUMBER AND TYPE) The kit includes relay, capacitor, and overload device, pre-wired. The kit will replace all 3 electrical components on capillary refrigeration systems. For newer systems with a run capacitor use proper kit. For smaller horsepower compressors useTJ90RCO810.
The wire set up is as follows the red wire goes to the right side of compressor prong, the white wire to the left side prong, the black wire to the center prong, and the 2 other black wires go to the power and the ground connection
Lastly you should also check ur THERMISTORS in the freezer and fridge section for continuity OHMS and for amount of OHMS current being put out. In most models around 13000 ( give or take 150 ohms) ohms is required.
1-3 TEMPERATURE CONTROL
As the food in the fridge gets colder, it gives off less heat, and the air inside the fridge will remain colder. A thermostat called aCOLD CONTROLwill cycle the cooling system on and off to keep the temperature inside your fridge within a certain range. You can adjust that range using one of the dials within your fridge.
On most fridges, all the cold air for both the food compartment and the freezer compartment is produced in one evaporator. Since the freezer is so much colder than the food compartment, most of the cold air that is produced circulates to the freezer compartment. Only a small amount is needed in the food compartment to keep it down to the proper temperature. This amount is adjusted by a smallAIR DOORin the duct between the evaporator and the food compartment. The control for this air door is the other of the two dials within your fridge.
If you hear your compressor "short-cycling" (starting and stopping at short intervals) try jumping across the two leads of the cold control thermostat ( in the fridge compartment) with an alligator jumper. You can also check both for live voltage current and ohms- If there is a greenthirdlead, ignore it for this test; it is the ground wire. If the fridge starts running constantly, the cold control is bad. Replace it.
To test or change the cold control, first Pull the knob off it and remove any plastic cover plate or housing from it.
You will see two wires leading to it. There will also be a thick, stiffCAPILLARY TUBEattached. The capillary tube is the liquid-filled temperature-sensing element of the cold control, and operates in the same manner as a thermometer
Read more:
http://removeandreplace.com/2013/10/31/fix-refrigerator-freezer-wont-cool-freeze/#ixzz3WDEo5NDJ
http://www.appliancerepair.net/refrigerator-repair-1.html
https://www.youtube.com/watch?v=KqXN-ZCuptk THIRMISTOR CHECK
https://www.youtube.com/watch?v=53ZFeiWgtuk
REMEMBER GOD IS THE REASON FOR GOOD ADVICE"
Refrigerator Is Not Cooling What To Check And How To Fix Refrigeration System Basics Chapter 1 Troubleshooting Thermistor Problems in Refrigerators Top Freezer Thermistor Testing Replacement
Dec 29, 2016 | Frigidaire Refrigerators
Tip
Checking out a air conditioner compressor and compressor problems FIRST...
FIRST DISCONNECT ALL ELECTRICAL POWER
Ohm the windings
C to R = example 1.2
C to S = example 3.2
R to S = example 4.4 total of C to R and C to S or very close.
Then ohm each terminal to ground you shouldn't get any reading
If the compressor is hot or you tried to start it, the ohms will be close but not exact.
No reading from C to R or C to S open winding or thermal overload.
Let compressor completely cool down then ohm the C to R and C to S again
If it’s an open overload, you will get an ohm reading after it cools down and the overload closes,
you may just need to add refrigerant.
No reading from R to S and C to S open start winding.
In case of any open windings the compressor will have to be replaced.
If the compressor is getting the proper voltage and won’t start, it could be locked up.
You need an Ammeter to check this to see if it’s drawing locked rotor amps (60 amps or above)
You also need to check the run and start capacitor.
A bad run or start capacitor, the compressor won’t run, it will just hum.
If the compressor will run, but quits after a while and all of the above checks out OK.
It could be drawing high amps ( you will need an ammeter to check this out). Dirty condenser or condenser motor not running, overcharge of refrigerant, shunted windings, bad bearings in compressor.
The compressor gets hot and Suction or big line coming in to outdoor unit is warm or slightly cool, you are low on charge or metering device bad or stopped up.
If compressor runs for a while and quits and the suction line is frozen, cold or cool, then the filter, evaporator or condenser coils are dirty or plugged up, blower or fan motor not running and unit going off on high or low pressure switches.
on Dec 29, 2009 | Heating & Cooling
Cooling Problem with side by side refrigerator & freezer
Check ur cold control thermostat, ur thermistors, ur air flow vent from freezer to fridge.( to make sure it opens and closes without any restrictions) On thermistors check for A close circuit and amount of ohms not just an Ohm reading. As per ur model. Most should atleast show 1200 ohms. Also Check door seals for leakage.
Evaporator coils
Condenser
THE COMPRESSOR:
Disconnect and remove the relay and capacitor from compressor, somes located next to compressor in a casing.
Read more:http://removeandreplace.com/2013/10/31/fix-refrigerator-freezer-wont-cool-freeze/#ixzz3WDEo5NDJ
Mar 25, 2015 | Refrigerators
What is the easiest way to diagnose a nissan 3.3 eng. Injector, on a road trip just a few tools available.
You need a volt/ohm meter to check the injectors. The injector should ohm out between 11 and 15 ohms(leads on both ends of the injector). Set the meter to the lowest ohm reading. On the plug end you should have a jumping reading, when cranking the engine, set it to dc volts.. It never gets to 0 volts or 12 volts, Just jumps between them. If you have no voltage from the plug end, then the wire is broke. Usually by the plug. Set it back to ohms and check the plug and pierce the wire about 3 inches back. See if you get a reading. Should be close to 0 or .05 ohms. If not, fix the wire. You may have to go further down on the wire. You can get a cheap ($20) meter at any parts store.
Oct 04, 2014 | Cars & Trucks
My PLHS269ZCB2 side by side only cools to 20 degrees in the freezer
Evaporator coils
Condenser
THE COMPRESSOR:
Jul 09, 2014 | Frigidaire Refrigerators
I recently purchased a 20 gal/1.5 HP, model 921.166420. The reset button on the side of the motor, (thermal overload Protector?) cuts out repeatedly. The few times where the motor did run and the pr
Could be weak thermal cutout or actual problem with unit. Thermal cut out easy to check with amp meter. Connect meter as required to monitor draw as unit fills and make sure that it stays at or below usage stated. If amp draw stays below stated usage and thermal cuts out, replace the part. If amp draw goes over amount stated turn off compressor and listen for air leaks (usually check valve will leak back pressure to pump causing extra load on motor).
Nov 29, 2011 | Craftsman 150 PSI Air Compressor
I have a 1HP/7 1/2 gal. Craftman air compressor( about 20 years old). I was using it to spray paint lawn chairs. The compressor stopped. I was to use it the next morning but for only a short time and it...
1) Check that it is not already at full pressure
2) Check that you have power coming in to the switch (20 year old power cord)
3) Bypass the switch and, briefly, plug it in.
4) Look for a fuse or breaker.
5) With the motor leads disconnected from the switch, check that you have resistance across the motor (0 ohms would be bad).
If you are not comfortable doing any part of this, don't. Check with friends & neighbors for a reputable local appliance repair company.
Jun 13, 2011 | Craftsman 1 hp Air Compressor, 4 gal. -...
2002 VW Beetle 1.9 TDI Air Conditioner
the resistance should have a reading in the compressor drive clutch
if it has a 0 reading it has failed
no compressor drive =no cooling
Mar 11, 2017 | Volkswagen New Beetle Cars & Trucks
Air compressor won't stay running even with resetting
How quickly does it shut off? Is it reaching the turn off psi? or is it immediate.
If it is immediate then it is probably a power supply issue.
Air compressors are power hogs. For instance, a compressor may work fine on an outlet using the supplied power cord, but plug it into an extension cord that is insufficient for it and a repeat of your problem will occur. If you use an extension cord make sure it is made just for this kind of application. Also, if possible, give the compressor a dedicated circuit.
Another problem might be your unloader valve not working correctly. This reliefs the pressure inside the pump after the motor has stopped. it would sound like the pump is working extra hard at start-up.
May 19, 2009 | Dewalt 2 Hp 4 GAL Air Compressor
Refrigerator cools as normal. Trips 15 AMP circuit breaker.
a full size refrige has to be on a 20 amp circuit, a 15 amp is just not big enough.. you should also know that this circuit has to be on a 12-2 gauge wire.. I also highly recommend installing a 20 amp HD receptacle
Mar 19, 2009 | Refrigerators
Carrier 38CKC036 Air Conditioner Logo
54 people viewed this question
Top Carrier Heating & Cooling Experts
Dan Webster
Dan Webster
Donni Steen
Bill Long
Are you a Carrier Heating and Cooling Expert? Answer questions, earn points and help others