Question about Frigidaire Heating & Cooling
Compressor temp overload trips and eventually trips circut breaker
  • 24 Answers
Could be several issues causing this problem. Let's start with some basic observations.
Is the condenser fan running?
Is the condenser coil dirty? (Not only the outside but all the way through the coil. Check by looking for light coming through coil. You can even try shining a flashlight through the coil to see if it is clean.)
If the fan is running and the coil is not plugged up or covered with dirt, or other obstructions (air is freely able to move through the coil), then it could be an issue with the system being over charged.
Another possibility (but not highly likely) is there may be non-condensables in the refrigerant system. Usually these will only be present if the system was recently serviced or charged and air and moisture was allowed to enter the refrigerant system (piping).
More information is required to try and diagnose this further.
Posted on Sep 04, 2010
True model t-19f freezer trips breaker as soon as it is plugged in.checked compressor. Good. Wired in hard start kit. Still tripped breaker.defrost? Or thermostat temp control?
if it is an immediate trip prior to the compressor attempting to start, you will have to start tracing the wiring and look for the cause. These issues can sometimes be very troublesome and difficult to find. If the compressor is tripping the breaker, the winding can be shorted internally to each other. Also, be sure the current relay is functioning properly. A generic 3-in 1 kit has a relay, overload, and capacitor and is easy to install. Cheapest way to replace start components.
Jun 10, 2017 | True Refrigerators
At times it starts and runs fine.Then at times it starts and stops because the circut breaker in my house has been tripped.
Check the amp rating on the circuit breaker. It's probably 15 amps. Find another line with a 20 amp breaker, and see if it still trips.
May 31, 2015 | Air Tools & Compressors
Main residual circuit breaker trips fridge approximately every 12 hours
normal fridge takes 7- 12 amps to start, if after 12 hours it trips i would lean towards a compressor issue. once it heats up the comp. may draw alot of amps causing it to trip. is it the only item on that circut? does it still trip being alone on the circut?
Apr 06, 2014 | Admiral 26 cu. ft. Side-By-Side...
Compressor will not start without tripping breaker?
Circut breakers trip due to a short circut or an overload. In this case the likely cause is an overload. If your compressor is drawing more amperage than the breaker is designed to allow, the breaker trips for safety. Possible solutions. Try using a different outlet with fewer appliances or tools on that circut. If the outlet you are using is on a circut that also has lighting, appliances etc, each item is drawing amps, the addition of the compressor to the circut is pushing the amp limit over the top. You can also try a heavier duty extension cord. If you are using an extension that is rated too low for the required amperage your breaker will trip. If you are not using an extiension cord you may need to talk to an electrician about adding another circut to service your tool and garage needs.
Another possiblity is that your service is not upgraded enough. If you have a 60amp service for the house you might want to talk to an electrician about upgrading to 100amp or more.
Jan 04, 2011 | Garden
Air Conditioner trips the 110v breaker, only when the outside temp is above 90 degrees. Unit has been checked several time and the circuit board has been replaced, but has fixed the problem of tripping the...
'Breakers' - are tripped because they are exceeding their amp limits.
The 'hotter' it gets outside - the 'harder' your AC has to work - and under normal circumstances this is not a problem - but when you have a fan motor or a compressor that is starting to 'break-down' (electrically) - often the AC's amp draw will exceed the limits of the breaker - thus 'tripping' the breaker.
I would suspect either the fan motor or the compressor is causing your breaker problem.
Eventually - the component (either the fan mtr or compressor) that is 'going bad' will go out completely and your breaker will 'trip' and not stay on when you try to reset it.
At this point you will need a Service Tech to determine which one is bad.
There is a possibility that your condenser coil (the one that blows hot air) is 'dirty' which will also cause a problem similar to the one you have - but it is less likely.
Also - if you've had the AC 're-charged' lately - it's possible you are in a 'over-charged' condition - but again, this is not very likely.
hope this helps.
Jun 06, 2010 | Dometic Rooftop RV Air Conditioner
Have a electric carry type 4 gal air compressor. As soon as I turn it on it trips the reset button. After a few trys, then its ok.
This is caused by the "Inrush" current at startup. Overloading the Breaker/Reset until the motors windings "Warms up" and the very low start resistance slightly increases, to where the "Load" will not trip it. You may need a better quality breaker as the one you have is too sensitive. but it should do no real harm, well it will eventually burn out the breaker, eventually I guess.
Feb 16, 2010 | Air Tools & Compressors
The compressor gets hot and trips the breaker
More than likely what happen was the internal overload in the compressor was tripped and didnt reset for 5 hrs and when it did it popped the breaker. The compressor was probably already shot. Sorry
Apr 29, 2009 | Amana AFD2535DES French Door Refrigerator
While waiting for replacement bags... air pump slowed then quit
Yes the compressor motor does contain a thermal overload circuit breaker.It will automatically reset if tripped by excessive heat.
Mar 13, 2009 | 1996 Mercury Grand Marquis
Heating & Cooling Logo
80 people viewed this question
Top Frigidaire Heating & Cooling Experts
Dan Webster
Dan Webster
Ronny Bennett Sr.
Ronny Bennett Sr.
Bill Long
Are you a Frigidaire Heating and Cooling Expert? Answer questions, earn points and help others