Question about Dometic Rooftop RV Air Conditioner
Heat pump heats with ac cool mode on dometic rv rooftop.
  • 24 Answers
Sound like the change-over valve on the heatpump is not switching. Could be the valve is stuck, or bad. Or the thermostat is bad and will not send voltage, or is sending voltage to your change-over valve.
(Some systems energize the CO valve to cool, while others de-energize the valve).
Usually the color coding for the thermostat wires on a heatpump are orange and yellow. The yellow wire usually energizes the compressor contactor, and the orange wire energizes the changeover valve. Now depending on what your system does in terms of energizing or not energizing the CO valve to invoke heating or cooling mode is not known. You can try jumping across the thermostat to see if the CO valve is working. Or you can even try placing the stat in heating mode and see if you hear that loud "Woosh" when you switch between heating and cooling modes at the stat.
What often happens is the cylinder inside the CO valve gets stuck, especially if the system has sat off for an extended time. By workign the stat from heating to cooling (reversing the porting on the CO valve) will cause the valve to free itself up.
If you cannot hear that woosh as the changeover valve switches between heat and cooling, it is possible the CO valve is bad, or there is an issue in the electrical or control side of your system. Such as a bad base or switching circuit in your stat, or control issues other places.
Posted on Sep 04, 2010
I have a Dometic DuoTherm AC/furnace in my RV. Thermostat got knocked off the wall. Now only thing that will work is the fan in the Manual mode. Heat nor air will come on. What could this be.
If you have properly re-attached all the wires to the old or newly installed thermostat, then I would suspect that one or more of the control wires to the heat pump have either been severed or pulled loose from the heat pump.
Feb 15, 2015 | Dometic Rooftop RV Air Conditioner
Is this a thermostat problem or system failure?
it sounds like no communication from stat to board. cable connections
Jun 03, 2014 | Dometic Rooftop RV Air Conditioner
Reversing vavle is not switching. rooft top dometic ac w/ heat pump ac is heat pump , heat pump is heat pump, everything is heat pump .any help?
Try lightly tapping the reversing valve in heat and cool mode. If the problem still exist replace reversing valve
Sep 03, 2010 | Dometic Rooftop RV Air Conditioner
We have a 2005 Country Coach Allure with 3 Dometic rooftop air conditioner/heat pumps. One of the units will come on start to cool then quickly turn to heat then cool then heat. What could the problem...
Hi; Sounds like a problem with the tstat or the defrost sensor. Also have these units been cleaned yearly. Also if the differential between heat and cool is small this will cause the unit to cool then heat due to the low differential at the tstat...alpharome416
Feb 23, 2010 | Dometic Rooftop RV Air Conditioner
How can we tell if our dometic rooftop air conditioner/furnace has a heat strip or not.
Hi; If You have a heat pump then yes on heat strips. Does Your RV have a gas heater. If You gently remove the cover some times You can see the heat coils in the metal air flow tube...Also does the compressor run in heat mode ,if not then best guess You have heat strip capability...alpharome416
Feb 22, 2010 | Dometic Rooftop RV Air Conditioner
A/C starts, goes immediately to heat
Unfortunately, your rear unit is calling for heat. If you put the rear unit on heat pump mode, does it then cool?
moz-screenshot-2.jpgmoz-screenshot-3.jpgThe reversing valve is energized in the cool mode of these AC's. So there is no real way to bypass it. I would check the thermostat and the control board in the unit to make sure that the switches are set correctly.
In the service manual section of the dometic/Rooftop RV Air Conditioner section. I have posted service manuals for the Heat Pump and the Comfort Control.
Hope this helps,
Jeff
Rate me please.
Jul 06, 2009 | Dometic Rooftop RV Air Conditioner
Heat Pump and fan work fine, but will not blow cold air on AC setting
The reversing valve coil may be bad or no power to it during cool. Most heatpumps are set to have the coil of the reversing valve energize in the cool mode. The heating mode is the fail safe mode if the rev valve fails to energize. Check this and let me know.
Jun 18, 2009 | Dometic Rooftop RV Air Conditioner
Dometic ac/heat pump
Would suggest it is drawing excessive current, make sure both fans are going, (inside will cycle low/high), or possible faulty reversing valve solenoid, or could be as simple as loose wire connection, how long does it run for and is it on the same 20amp breaker as the rear?if so start by running only the front unit in cooling 15/20min, check fans running, no unusual bearing noises, switch off for 60 sec then back on heat mode, if unit runs without stopping rewire onto separate circuit, if inside fan not working on heat check bi-metal switch in the airway, if running for a while, fans going but not very warm, check reversing valve.
Note, electrical's should be tested by someone who are qualified in the field.
Nov 05, 2008 | Dometic Rooftop RV Air Conditioner
Dometic Rooftop RV Air Conditioner Logo
206 people viewed this question
Top Dometic Heating & Cooling Experts
Bill Long
Donni Steen
mike cooper
Are you a Dometic Heating and Cooling Expert? Answer questions, earn points and help others