Question about GE Circuit Breaker THQB BoltOn 1 Pole 15 Amps 20 Amps 30 Amps 40 Amps
GE THQB 1 pole 20 Oily liquid appears to be seeping from multiple breakers, different panels but not all breakers. Breakers installed 1992. Any thoughts?
  • GE Master
  • 43,501 Answers
There is no liquid in those breakers to seep out... my thought would be that some one used an anti oxidate compound on the wires when they installed them and that is running a bit as the breakers and wires heat and cool....
I would just check the wire connection for tightness and as long as the connections are tight I would not worry about it...
heatman101
Posted on Sep 03, 2010
I have 110 volts n each leg but not 220 across both why??
In a traditional North American residential electrical panel (120/240 volt, single phase), installing a single width or single pole circuit breaker, you would expect to read 120 volts from the breaker terminal screw to either ground or neutral. A double width or double pole breaker would provide 120 volts from either of the breaker terminal screws to ground or neutral AND it will provide 240 volts BETWEEN the TWO breaker terminals.
A single-width circuit breaker case that contains two handles is NOT a two pole circuit breaker (these are called "tandem" or "1/2 size" breakers). This is because a single width breaker engages only one "line" in the panel. A double width breaker will engage 2 "lines" as a triple width breaker would engage 3 "lines" of a 3 phase panel. A single wide breaker can not physically engage more than 1 "line" so it will never be able to pass 240 volts.
You must install a double width / double pole breaker to safely supply a 240 volt circuit / device.
Mar 15, 2014 | GE 20 Amp 1 In Double Pole Circuit Breaker...
Lost power to two rooms and no tripped breaker.
More information is needed.
What have you tried so far?
http://waterheatertimer.org/Troubleshoot-household-electricity.html
What kind of breaker?
Have you fully reset breakers?
Gene
g
Nov 24, 2013 | General Electric 20 Amp, 1 Pole Thick Type...
I need a 2 pole half size arc fault breaker
If you are pressed for space in your panel, it would be easier to free up space in the panel by replacing some of your standard breakers with half size--or "piggy back"--breakers. The freed up space will permit you to install a standard arc fault breaker.
Aug 20, 2013 | GE Circuit Breaker THQP PlugIn 2 Poles...
There is the liquid seeping out of the breakers, it is not water the box is dry and it feels like an oil of some kind. breakers are working and are not hot. i have not seen this before. what is it and what...
It is oil. It's used to extinguish the arc.
When a circuit breaker trips, there is an Arc of electricity made inside the breaker, due to the contacts.
The contacts are instantly brought away from each other.
There are three methods employed to extinguish that arc.
[Extinguish the arc. Non-technical explanation. With out some medium to extinguish the arc produced inside, it would go Z-z-z-z-z-z-z-z-z-z-z-z-zap, instead of z-zap]
Oil, Air, and Sulfur Hexafluoride.
So yes, as long as the circuit breaker doesn't have to trip, and produce the arc inside, it is a working circuit breaker.
Is it a safe unit?
NO
The method employed to extinguish the arc if the breaker trips is leaking out.
Replace all breakers that are doing this.
Average cost for a GE single-pole 15, or 20 Amp is around $11 here. A few dollars more for 30 and 40 Amp, but usually double-pole breakers are used for 30, and 40 Amp.
Nov 18, 2010 | GE Circuit Breaker THQB BoltOn 1 Pole 15...
Double 20 breaker switch slot in the back is to short and it won't seat right.
Are you installing it in a GE panel? Look on panel cover and it will list the compatable breakers. Even though some breakers "fit" different brand panels, they ar not approved if not listed by manufacturer of the panel to be used in that panel
Aug 06, 2010 | GE 20 Amp 1 In Double Pole Circuit Breaker...
I need to install a GFI breaker on a Baptistry.
You could install a standard GFCI in line at each component ( heater, pump & timer) or you could install AFCI breakers similar to what are required in many residential codes (provide the same protection at the panel not at the location... http://www.cpsc.gov/CPSCPUB/PUBS/afcifac8.PDF
The AFCI breakers will need to match your panel type (siemens, GE or Square-D) and the amperage/configuration.
I would install them at the lowest level (closest to the components) in the system to reduce possibility of fire in the wiring between the components and the afci breaker.
Jan 04, 2009 | Electrical Supplies
Arc fault trips under load
Arc fault breakers are definitely a pain. First make sure the receptacles are made for a 20 amp circuit. Second vacuums, Curlers,and most appliances will trip your breaker since they create an arc or a short if you will to operate. That is exactly what these breakers are made for. To stop the arc. Apparently they never really thought the whole arc fault thing through. As per code in most of arizona you only need this breaker in bedrooms where this type of appliance is not used. They also are more prone to popping so make sure you aren't running something on each of the receptacles at the same time
Dec 18, 2008 | Siemens 20Amp 1-pole arc-fault circuit...
GE Circuit Breaker THQB BoltOn 1 Pole 15 Amps 20 Amps 30 Amps 40 Amps Logo
122 people viewed this question
Top GE Electrical Supplies Experts
Steve
steve morris
steve morris
ray gallant
Are you a GE Electrical Supply Expert? Answer questions, earn points and help others