Our total line thermostat was set on 73 degrees and all of a sudden it went to 99 degrees and I counld not turn it off, it just kept running. So I turned off the breaker and turned in back on and now I can't set the temperature. It's just set on 99 and won't do anything. When I turn the fan on, the air won't get cold.
    President:
  • 1,515 Answers
Hi, it sounds as though you have a faulty thermostat that failed before your eyes. The circuitry in the sub-base has failed. If the stat is set in the off posistion and you turn the fan switch on, just the fan will run. If it is on cool and you turn the fan to on and not auto, it should bring on the compressor. You will need to get a new thermostat. Kill the breaker and remove the cover to the stat and expose the wiring. This is a 24 low voltage stat. It will have terminals rh and rc with a red jumper connecting the 2, and your red hot wire connected to either one.Y, yellow for cooling, G, green for fan control, and white , W for heat control. Y yellow may be using a blue wire instead. They sometimes do this. Write this down and pick up a stat at Home Depot, Lowe's hardware This will solve your problem. Please don't forget to rate me as I know you will be kind. I will check in on you as I keep files on all of problems I have solved to help people. You can also get back to me by my user name below.
Sincerely,
Shastalaker7
A/C, Heating Contractor
Posted on Sep 03, 2010
The unit is on Heat, Fan Auto it's 36 degrees outside, Thermostate set on 73 Actual temp inside 70. Unit runs continuously. How can I get more heat. I tried Emergency heat and that doesn't help.
Have you cleaned the air return filters ? Wash them, don't vacuum or brush them. It damages the filter screen. Sometimes a thermostat will be out by a few degrees. If the filters are clean, try turning the temp down a bit to 65 degrees and see if the air con shuts down. ( If your room temp is showing 70, it should switch off the machine) If it doesn't turn off, keep reducing the temp by 5 degrees at a time and wait a few minutes each movement to see if and when it shuts down. If the machine keeps running, I would suggest your thermostat is shot and you will need a new one.
Jan 04, 2016 | Heating & Cooling
How do i adjust AC temperature variance on a Honeywell TH5220D1003 thermostat
If you are talking about the difference between heating mode and cooling mode and the room setpoint, you can not change it. It comes from the factory with a 3 degree difference. In other words if you raise the heat setpoint until it is within 3 degrees of the cooling setpoint, for every degree you raise the heat setpoint the cooling will raise a degree.
About all you can do is increase the distance between the heat and cooling setpoint. To do this either lower the cooling setpoint to 3 degrees higher than the heat setpoint you want and then increase the cooling setpoint the desired setting. For example heat and cool setpoints are 67 and 70 respectively, and you want 65 and 73. Lower the cooling setpoint to 68 and then raise the cooling setpoint to 73. Now your heating will come on 3 degress lower than 68, the 65 you wanted and cooling will come on at 73. Remember, the thermostat new setpoints will turn on the cooling at 75 and turn back off at 73 and heat will turn on at 63 and turn off at 65.
You can perform the same using the heating setpoint, just have to look at it backwards. If you need to lower the difference I recommend a 8000 series thermostat. They are the most functional thermostat that Honeywell makes, be in mind they are about 3 times more expensive and many of the setting require a well trained tech to interpret and set properly.
Hope this helps.
Aug 24, 2014 | Honeywell Th5220d1003 Non-programmable...
Rth9580wf1005 changing setting on own
There may be a sudden weather change or heat change that may set it of. Also it might help to double check your settings just in case one of the buttons or dials have been knocked.
Mar 01, 2014 | Honeywell Electronic Programmable...
Honeywell emm-3 goes to high heat when thermostat does not call for heat
Replace it (thermostat), but first make sure its in a good location to read the space temperature.
Nov 29, 2013 | Heating & Cooling
Freezer thermostat was set at 0 degrees unit went down to -30 degrees. I increased temp on thermostat 3 degrees 3 times each over a 3 day period. The thermostat is not responding. I have the thermostat set...
I would start there. If the thermostat has an off setting, turn it there and see if it goes off. If not, try turning it to it's warmest setting while the box is cold to see if it turns off. To test to see if the relay/ contactor is stuck/bad, kill power to the unit (Unplug or turn off breaker). Disconnect one wire to the thermostat. Restore power. If unit runs, bad relay/contactor. If unit does not run, I'd replace the thermostat. Make sure the sensing bulb of the thermostat is in the conditioned space of the box or in the return air (intake) side of the evap so it can sense the box temp.
Aug 02, 2010 | Nor-Lake KLF7766C Commercial Freezer
My thermostat is set to 73 degrees when i get home at six it is set at 75 during the day when im not home the past couple of days it wont get to 73 it actually goes up to 76 77 it is working cool is on why...
may need charged a out of adjustment can cost lots is it old unit is outdoor temp. very hot may have trouble catching up to setpoint.on a 95 degree day good luck.
Jul 07, 2010 | Honeywell Electronic Programmable...
Temp shows 2 degrees warmer than what is was set to
sometimes the furnace does a better job than anticipated, i wouldn't worry about it, especially if the furnace shuts off.
the setpoint is the temperature you want it to be
cycle lenghts are determined by how much recovery you are requesting. for instance, in the morning when you wake up, you want the temperature to be at its setpoint. what the thermostat will do is make the furnace run a limited lengths during the recovery process.
Nov 11, 2008 | Honeywell Programmable Thermostat Heater
Cooling Problems
Your filter is clogged. Not the one at the bottom of the unit.The one above the unit. It is like a raditor coils, kind of a bear to get to. We have cats and dogs the filter gets most of the hair but not all.Usualy about 6 bolts to take out.The proublem will be at the bottom of the top filter.
May 09, 2008 | Honeywell Electronic Programmable...
Heating & Cooling Logo
118 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Tim Whalen