Question about Coleman Powermate Powermate 5000W Generator
I need a wiring diagram for coleman pm04350001 generator. the 220 recept. is not working and am trying to troubleshoot.
    Scholar:
  • 97 Answers
High no-load voltage Capacitor with high capacity
Check and replace. Low no-load voltage Speed to low Check and adjust rpm Faulty rotary diodes Check and replace Breakdown in windings Check winding resistance Capacitor with low capacity Check and replace. Proper no-load but low loaded voltage Capacitor with low capacity Check and replace. if wires are connected start with the Diodes first electronics parts stores will have these in stock as well as cheeper. hope this helps
Posted on Sep 02, 2010
The 220 plug has 4 leads and my 220 compressur has 3 wires how do i make the conection
The four wire 220 twist lock receptacle Two hot wires, one neutral, and a safety ground. Depending on your generators setup the neutral and ground are bonded as one; unless, it setup for a floating neutral.
You would normally connect the two hots and neutral. and leave the ground open on the four prong twist lock plug. Just make sure the compressor is earth grounded on its end.
Feb 12, 2015 | Coleman Powermate Powermate 5000W...
Need a wiring diagram/schematic for the power output end/recepticals for the coleman powermate 5000 model pc0545305.01 generator
Couldn't get you a wiring diagram but the contact info should get you to someone who can. The other links will get the manual and parts breakdowns.
http://www.powermate.com/contact.php
http://www.powermate.com/pdfs/2007/11/12/manual_pc0105000.pdf
http://www.powermate.com/pdfs/2007/11/12/parts_pc0105000.pdf
Oct 01, 2012 | Coleman Powermate Powermate 5000W...
I have a coleman powermate maxa 5000 er Generator. Model # PM0525202. The powercord plug came loose and burnt the plug and the receptical(240). I replaced the plug and receptical and I am not getting...
If this is the model I am thinking of, there are 3 outlets. One 240V (L1, L2, Neutral and Earth ground. Some models use a 3 terminal receptacle that combines Neutral and earth.), one 120V receptacle (L1, Neut, earth) and another 120V receptacle (L2, Neut, earth).
If you verified fuse and circuit breakers are good, turn on the generator and verify you get 120V on each of the two outlets. Measuring between the narrow blades of the two 120V outlets should be 240V.
***Shut off the generator.
With a test light or ohmmeter, check continuity from the earth terminal of 120V outlets to 240V outlet. Likewise for neutral (wider blade on 120V outlet). Lastly, check continuity from Narrow blade of each outlet to the 240V outlet.
I suspect that you miswired neutral and earth. On a 4 wire PLUG, it is customary to connect earth and neutral.
Work safely so you can give feedback.
Aug 30, 2017 | Coleman Electrical Supplies
"I was welding with a
Your generator is a welder?? Yikes, the 220 volts coming out of the genny is not the same as the 220 volts running a welder, it is, but it isn't, the 220 volts used to run the welder are transformed into DC, in the 50 -150 amp range, the 220 volts coming out of your genny is 220 volts, AC, at 30-40-50 amps. Now exactly how were you welding with 220 volts AC? Remove anything plugged into the genny, check the oil, check the gas, make sure it is fresh, check the breakers, check the fuses, get it running, now don't try to weld with it again. Unless you have a big welder to plug into it and I wouldn't even do that because of the generator spikes. I might be wrong, but I have never seen a genny with a welder on it for home use.
Feb 06, 2011 | Coleman Powermate Powermate 5000W...
Coleman powermate 4000 pops circuit breaker on the 220 side.
Don't know what you mean by "on the 220 side".
The generator has two joined circuit breakers that each are 110 volts. Between the two is 220.
If just one of those is opening WITH NOTHING PLUGGED IN, then there are only a few explanations.
1. There is a short in the wiring or the wiring has been tampered with and connected incorrectely.
2. The switch that switches the mode from 120 to 240 has gone bad, possibly with a welded contact. This would occur if the switch is changed with load on the generator. This could put a driect short on half the generator winding and cause one of the breakers to blow.
3. Worst is a winding short in the generator. Fortunately this is the least likely.
4. The 220 receptacle has been broken and insulation failed shorting one terminal to another.
Nov 14, 2009 | Coleman Powermate Premium Plus 6250W...
Coleman 5500 watt output unbalanced
Get on their website and get the wiring diagrams. They should also have the resistances of the windings. Checking these resistances, may indicate a stator problem. Give the model number and it will be easier to help.
Jul 29, 2009 | Coleman Powermate Powermate 5000W...
Runs great but will not produce electricity
To flash the excitor circuit on a coleman ( the generator is built by generac) you need a 12 volt battery. You quickly apply 12 volts via your 120vac recepticals. NO MORE THAN ONE OR TWO SECONDS! Then check you ac voltage. Most of the time the brushes are burnt up when voltage is low. Check the brushes first. You can access them by taking the end cap off of the generator via two to four screws. The brush holder is easy to spot, two wires leading to the front of the amature. Hope this solves your problem.
Mar 29, 2009 | Coleman Powermate Premium Plus 6250W...
Colman powermate 5000 no putting out any electric
If you are getting some power, even if it only 2vac then you may have to flash the excitor circuit. If nothing then take the end cap off the generator and clip your meter to the metal portion of the brush holders or exposed wire from them. Start the generator and see if any voltage is coming from the brushes. Even if there is nothing try flashing the excitor.
Give this a few attempts and if this does not do it, I would say the winding repair did not work. Buy another generator and use the engine for a go cart or backup engine since this generator is so cheap.
Mar 17, 2009 | Coleman Powermate Powermate 5000W...
Generator plugs doesn't match cord
Hey steve. do you really need 240 volts for 120 v. circuits. the reason you have to have an adaptor plug is because on your 220 volt plug in , 2 of tthose prongs are hot and 1 is ground. for safety you need to get a plug adapter ( a regular 120 volt plug end ) run a ground from adapter to ground on 220 adapter. same with nuetral. you also need to ground your generator. there is usaully a ground lug on the bottom of the gen. Another way. if you dont really need 220 v. is to use both 120v. recepticals on gen. Run 2 chords to tranf. switch. and hard wire it in to switch. another way i did mine . when i lost power in this hurricane. i ran two # 10 chords from my 2 120v. recept on my gen to my breaker panel. when you do this you have to pull the service meter, if you dont when power comes back on it would backfeed through your gen.then i turn all my 220v. breakers i was able to run lights ,ciling fans, freezer, ice box,washing machine and gas dryer , tv's computors etc. . but to do this, you probably need someone that knows what they are doin.
Sep 18, 2008 | Coleman Powermate Premium Plus 6250W...
Coleman Powermate Powermate 5000W Generator Logo
768 people viewed this question
Top Coleman Electrical Supplies Experts
John Trevino
Phil Walker
Phil Walker
Tim Garcia
Tim Garcia
Are you a Coleman Electrical Supply Expert? Answer questions, earn points and help others