I need a wiring diagram for the 24 volt transformer and RBM relay, thank you
  • 2 more comments
  • ballfan58 Sep 01, 2010
    I need the wiring diagram for a Coleman AH16-0 240V input, 24v output on transformer and the wiring for the RBM relay, runs blower fan. Thanks
    Still no help on wiring diagram, keep looking I have received no help so far.
    Guru:
  • 402 Answers
I do not have a wiring diagram to give you. If the one that was on the furnace has disappeared, you may be able to find one on the manufacturer's web site. A local dealer may help too.
The colors I have are not follow the right codes.However, I traced them and I conntected them.The problem was solved.Here were my measured voltage on each wire: Thin black: 110vac (coming from input power supply) thick black: 0 vg (is coming from inducer motor) thick Gray : 0vg (is coming from pressure swtich) thick red : 25 vac(is coming from sensor) thin red : 25 vac ( is coming from the output of the transformer) white : ground ac ( is coming from the transformer as well)
I connected the relay as follow:
1. the input of the relay should be 25 vac so I connected the thick red which is coming from the sensor on one leg, and the other I connected to the white as a ground. 2.When the sensor get the signal the 25 volt will swtich the relay,so the connected the thin red(25) and the thin balck(110) to the swtiched legs. 3. I connected the thick black and the thick gray to the unswtiched legs. So when the relay swtiched the gray will have the 25 volts to close the pressure swtich which will feed the TH leg on the module to generate the spark, and the thick black will get the 110 vac to get the inducer motor the power to run.
the furnace is working perfectly now.I have some troubles after connecting every thing because I lost the 25 volts, and I got only 13 volts which was very unusual.However, I found the reason that the cover of the wall sensor unplaced.When i put it right, I got the 25 volts back.
I'm sorry that my english is not that great, but i tried to explain what i did to help any other if they face the same problem.
Thank you Ben
Posted on Sep 02, 2010
  • 944 Answers
This is the only site which provides wiring diagram related to Coleman.
Coleman does not provide any online diagrams...
http://colorcodes.flagsolution.com/colemanwiringcolorcodes/
For 24 volt transformer:
http://www.google.co.in/images?um=1&hl=en&biw=1912&bih=825&tbs=isch:1&aq=f&aqi=&oq=&gs_rfai=&q=coleman%2024%20volt%20transformer%20wiring%20color%20codes
For RBM relay:(Common not specific to Coleman)
http://www.google.co.in/images?um=1&hl=en&biw=1912&bih=825&tbs=isch%3A1&sa=1&q=RBM+relay+wiring+color+codes&aq=f&aqi=&aql=&oq=&gs_rfai=
Hope this can help you.
post a comment for further assistance.
Thank you for using fixya have a nice day:-)
Posted on Sep 01, 2010
  • Natarajan Ramasamy
    Natarajan Ramasamy Sep 02, 2010
    you can't find Coleman wiring diagrams in online.It is the company policy to post there product wiring diagram in online.You can have sample diagram as above.
  • 857 Answers
Follow these steps
•1
Connect the input wiring. The input to your transformer should be marked 120 volts. Many transformers come with the input wires already attached. All you need to do is connect a standard two-pin wall socket to the two wires. You may need to splice if there is no wall socket close by. Of you can connect them to a junction box if you are skilled in house wiring.
•2
Connect two wires to the output of the transformer. Loosen the screw terminals, strip the wires about half an inch, place them under the screw terminals and tighten them.
•3
Connect the output wires from the transformer to your HVAC unit. Look at the owner's manual or the HVAC unit itself to find the terminals. If they are screw terminals, loosen the screws, strip the wires about a half an inch, place them under the screws and tighten them.
IMPORTANT: lOOK INTO THE LINK BELOW FOR WIRING DIAGRAM:
http://www.galco.com/techdoc/hde/e500wb_wd.pdf
?Location and photo of the transformer for a gaffers and sattler wall furnace model S 90 FE.
No. The transformer "transforms" 240 volts to 24. Meaning the high voltage coming into the machine. Normally has a "c",208,240 written on one side. Follow your main power wire into the machine. Branches to heater and transformer. Look at wiring diagram
Mar 01, 2017 | Heating & Cooling
How to wire a MY2NJ 110V relay
http://www.instructables.com/id/Space-heater-controlled-by-digital-thermostat/step2/Schematic/ The transformer in this diagram is a little high on the voltage side. Your relay uses 24 Volts.
Dec 13, 2014 | Dryers
Wiring diagram RUUD UAPA-036JAZ
the condensor gets 240 volts a-c and 24 volts a-c to control contactor. pretty straight forward on this 3 ton unit. the 240 volts comes off breaker box and the 24 volts comes off thermostat and common of transformer.
Jun 10, 2014 | Ruud Heating & Cooling
Dayton heater mod 2yu59 is not heating up?
Need to check the low voltage circuit for 24 volts, the 480 volt to 24 volt transformer may have a circuit protection reset or fuse installed. All the 3 phase electric heaters use a low voltage control circuit for operation of relays (24 volt coils).
Nov 22, 2011 | Dayton 2YU59 Electric Heater
I need the wiring diagram to wire a thermostat to the outside unit. Which wire goes where ? My Thermostat has four wires, green, red, white, and yellow. My Outside unit has three wires that are not...
The thermostat wires are this, Red is 24 volts hot, Yellow is cooling, Green is fan,indoor, and white is heat.The outdoor unit wires up to the indoor units terminal board, not the thermostat.The red will go to the R or red 24 volt wire at the furnace.The yellow goes to the yellow terminal at the furnace. You should only have 2 wires to connect at the outdoor unit. Try capping the blue off.It may not be used unless this is a dual transformer unit which you will need a tech to come out and rewire the furnace to make the outdoor unit a 2 wire set-up. This can be very complicated if this is the case. Connect these wires like I have said to the indoor unit, and it should work fine. Please keep me posted. This is only low voltage, so don't let it scare you. If nothing works, I would say that the blue wire outdoors is the 3rd wire for a 2 transformer unit, and will need to be rewired at the indoor unit for it to work, this I would have to be there to do.
Sincerely,
Shastalaker7
A/C, & Heating Contractor
Feb 26, 2011 | Heating & Cooling
Wiring diagram for Thermoking V700MAX
Red or R is the "Hot leg" of the Transformers 24volt supply,
Common or C is the "Neutral leg" of the Transformers 24 volt supply;
and the side of power to which ALL the 24 volt control circuits
terminate to complete the circuit, example; Heat=W, Cool=Y, Fan=G.
Upon a call for heat a switch closes betwen the Red and White Thermostat terminals.
The stat sends the 24 volts to White or W for the heat circuit on W on the
furnaces LVTB low voltage terminal board.
Yellow or Y goes from Thermostat to furnace Y on LVTB, which is simply
a connecting point on its way to the AC units 24v contactor coil located outdoors.
It actually isnt even attached to the furnace many times as it serves no purpose there and simply
continues to the AC unit with the copper lineset that the AC unit feeds.
The remaing 24 volt Thermostat wire goes back to common on transformer to complete the Yellow
24 volt control circuit.
Green or G exits the Thermostat and connects to G on LVTB for the fan relays 24volt coil
and returns to Common to complete the Green 24 volt control circuit.
O is for a Heat pump reversing valves 24 volt solenoid, and return to Common as all 24v circuits must to terminate or complete the circuit.
Some parasitic type Termostats need the 24v power to run, some are battery, some are both.
Nov 01, 2010 | Heating & Cooling
How does a 208V 24Coil Relay works?
A 208 volt 24 volt coil relay is rated for use at 208 volts at the relay contacts. The coil used to energize or closed the relay contacts are operated o 24 volts .a 24 volt transformer is used for the coil circuit.
Hope this helps.
Bob
Jul 30, 2010 | Square D Ehb24020pl 20 A Ehb4 Ehb Circuit...
How to connect a thermostat to heat source. bought thermostat to work in a homemade incubator. i can power in unit but when i connect heat source(light bulb) it wont switch it on when temperature is below...
get yourself a RIB (relay in a box) relay that is rated at 24/120. Also purchase a 24 volt door bell transformer. Wire 2 24 volt thermostat from one side of the transformer to the low voltage side of the relay then to the 24 volt thermostat than back to the other low voltage wire of the transformer. On the high voltage side, from your light bulb cut the wire going to the center lug of the light. Run one side of the wire to one side of the high voltage side of the relay, then run a wire from the other side of the relay (again high voltage side) to the the other side of the wire you cut on the light.
Mar 08, 2010 | Heating & Cooling
How to install and wire thermostat on model WOBC 095QBEA fuel oil furance
is this the 2 wire valve on the furnace, if so i'm pretty sure it's a 24 volt setup, check on valve it should say,there will be a 24 transformer,the valve or relay and a thermostat,one wire from 24 volt side of transformer to valve,other wire from transformer goes to R on thermostat,other wire W from thermostat returns to connect to other terminal on valve or relay if it's forced air, sure hope this helps
Jan 31, 2010 | Heating & Cooling
I have a coleman Evcon model AH16-0 . I am
Typical Thermostat Wiring for 4 or 5 wire Heat/Cool Thermostat (not heat pumps)
4 Wire Termostat
R = Red One Side of 24 volt Transformer
G = Green Blower
Y = Yellow Cool
W = White Heat
5 Wire Thermostat
with one transformer for both units
Rc One Side of 24 volt Transformer
Rh Jumper Rc to Rh
G = Green Blower
Y = Yellow Cool
W = White Heat
5 Wire Thermostat
With 2 transformers one for indoor unit
And one for outdoor unit
Rc = Red One Side of (outside) 24 volt (outside transformer)
G = Green Blower (outside transformer)
Y = Yellow Cool (outside transformer)
Rh = Blue One side of (inside) 24 volt (inside transformer)
W = White Heat (inside transformer)
COOLING ONLY Thermostat
G = Green Blower
Y = Yellow Cool
HEATING ONLY
R or Rh One Side of 24 volt Transformer
W = White Heat
Jan 06, 2010 | Heating & Cooling