I have an old! rheem package heat pump for outdoor use. Model no. is rpna 024j 005 and i need a new wiring diagram. where can i locate on line?
  • 14 Answers
SOURCE: Need to locate a Ruud Manual
You probably can call 502-456-4050 or go to site information@ruddequipment.com thank you and good luck J
Posted on Dec 19, 2008
farfield
  • 462 Answers
SOURCE: need wiring diagram for 1980's 3 ton package unit
I assume you know if this is correct voltage and single or 3 phase, and whether it will fit your application or not, how is the duct work going to attach, how many people will be in the conditioned area, what is the building made of, how much insulation is has...
A little more to it than just "turn it on".
If you get the models and serial and can contact the manufacturer or their representative you might get a wire diagram. Most any package unit would do. As long as you keep the original equipment controls. If you "patch" it up it may be hazardous by not having safety's where it was designed for. Or for instance It may have a anti freeze thermostat. By passing this could lead to coil freeze up and compressor damage. Leaving out a pressure switch (if any) may do the same or could become dangerous to people in the event of fan motor failure. A low temperature fan speed switch may not be needed now unless you plan to run the AC in below 55'f.
And a few dozen other factors that might need to be considered.
If you feel confident after this then contact carrier.
Please rate me as high as you can and thanks for using fixya.
Posted on May 19, 2009
jumptrout51
  • 3361 Answers
SOURCE: air handler fan not working
Check the fan relay switch in the air handler.
Check the fan motor capacitor.
Check the fan blower wheel for binding.
Posted on May 25, 2009
  • 195 Answers
SOURCE: Rheem Heat pump 5 ton heat strip 10KW what
I would say this is around 75 amps of draw at max for both the compressor and heat units. . Therefore--at least 90 amp breaker, and probably 100 amps for good measure, and at least #4 or #2 wire to the unit.
Posted on Oct 10, 2009
  • 51 Answers
SOURCE: wiring diagram for Rheem rpka-31 jaz heatpump
TURN THE POWER OFF TO THE UNIT. TAKE THE BACK PANEL OF OF THE HEAT PUMP AND LOOK FOR A SQUARE PLASTIC BAG FASTENED TO THE INSIDE OF THE UNIT, IT MAY BE LOCATED BY THE CONTACTS AND SYSTEM WIRING OR ON THE PANEL ITSELF. REMOVE THE PAPER FROM THE PLASTIC AND THIS SHOULD CONTAIN YOUR WIRING DIAGRAM. ALSO LOOK ON THE BACK OF THE PANEL ITSELF FOR THE DIAGRAM. SOMETIMES THE DIGRAM IS PRINTED THERE.
Posted on Apr 13, 2010
I need outdoor wiring diagram
Omg. Outdoor wiring diagram for what???? Lawnmower, vehicle, tractor, well pump, sprinkler system, condenser, heat pump, generator...WHAT MAKE?? WHAT MODEL?? WHAT??
Feb 20, 2017 | Heating & Cooling
Tip
Thermostat wiring terminals and colors
R - The R terminal is the power for the thermostat. This comes from the transformer usually located in the blower section for split systems but you may find the transformer in the condensing unit. For this reason, it is a good idea to kill the power at the condensing unit and the blower section before changing or working on the wiring at the thermostat. If you have a package unit then the transformer is in the package unit.
Red for the R terminal.
RC - The RC terminal is designated for the power for cooling. Some HVAC systems use two transformers. A transformer for cooling and a transformer for heating. In this case the power from the transformer in the blower section would go to the thermostat terminal. It should be noted that a jumper can be installed between RC and RH for a heating and cooling system equipped with a single transformer.
Red for RC terminal.
RH - The RH terminal is designated for the power for heating. See RC above for an explanation. It should be noted that a jumper can be installed between RC and RH for a heating and cooling system equipped with a single transformer.
Y - This is the terminal for cooling or air conditioning and goes to the compressor relay. Typically a thermostat wire pull is made to the air handler on split systems and then this wire is spliced for the separate wire pull which is made to the condenser. Some manufacturers put a terminal board strip near the control board in the air handler so a splice is not needed.
Yellow for Y Terminal.
Y2 - This is the thermostat terminal for cooling second stage if your system is so equipped. Many systems only have a single compressor but if you have two compressors which should only operate off of one thermostat then you need the Y2 thermostat terminal for second stage cooling.
*The most common color I've seen used for this terminal and wire designation is light blue but this varies and is completely up to the installer what color to use. Most installers use the color coding as noted but be aware that some do not use the thermostat color coding.
W - This is the thermostat terminal for heating. This wire should go directly to the heating source whether it be a gas or oil furnace, electric furnace, or boiler,
White for W Terminal.
W2 - This is the thermostat terminal used for second stage heat. There are gas furnaces with low fire and high fire and some depend on control from a two-stage heating thermostat with a W2 terminal. Heat Pumps use staging for auxiliary heat and need a W2 terminal.
*The most common color I've seen used for this terminal and wire designation is brown but this varies and is completely up to the installer what color to use.
G - This is the thermostat terminal used for the fan relay to energize the indoor blower fan. On a split system the blower fan is in the blower section while with a package unit the blower fan is in the outdoor package unit.
Green for G Terminal.
C - This is the thermostat terminal which originates from the transformer and is necessary to complete the 24 volts power circuit in the thermostat but only if the thermostat consumes electricity for power. Many digital thermostats require 24 volts for power so the common wire is necessary.
C stands for common and there is no universal color used for this terminal although black is the most common color I've seen.
O or B - These thermostat terminals are for heat pumps and the B thermostat terminal is used on for Rheem or Ruud and any manufacturer that energizes the reversing valve in heating mode for the heat pump. Most other manufacturers of heat pumps will utilize the reversing valve for cooling and the O thermostat terminal will be utilized for this purpose. This wire goes to outside heat pump condenser where the reversing valve is located.
Orange for O and Dark Blue for B depending on the installer of the heat pump and the manufacturer. If you have a Trane, Carrier, Goodman, Lennox, Ducane, Heil, Fedders, Amana, Janitrol, or any other manufacturer other than Rheem or Ruud you will be utilizing the orange wire for reversing valve. Rheem and Ruud will usually utilize the blue wire for reversing valve.
E - This thermostat terminal is for heat pumps and stands for Emergency Heating. If for whatever reason the heat pump condenser fails and it is necessary to run the heat there is an option on heat pump thermostats for emergency heating. Basically this simply utilizes the back-up heat source many heat pumps have to heat the home without sending a signal to the condenser to run for heat.
E - There is no universal color used for this thermostat terminal designation but this should be wired directly to the heating relay or the E terminal on a terminal strip board in the air handler or package unit if you have a heat pump package unit.
X or Aux - This thermostat terminal is for back-up on a heat pump and allows for auxiliary heating from the back-up heat source usually located in the air handler.
X or Aux - There is no universal color used for this thermostat terminal designation but this should be wired directly to the heating relay or the Aux terminal on a terminal strip board in the air handler or package unit if you have a heat pump package unit.
S1 & S2 or Outdoor 1 and Outdoor 2 - Some thermostats have this terminal and it used for an outdoor temperature sensor. The wire uses for this should be special shielded wire and completely separate form the other thermostat wires.
on Jun 06, 2011 | Heating & Cooling
Rheem error codes
error code 29 is a high pressure open. possible causes are dirty indoor or outdoor coil. indoor or outdoor fan not running, liquid line Freon restriction, or to much Freon in the unit.
Jul 30, 2014 | Rheem RPRL048JEC 4 Ton 16 SEER Heat Pump...
Will a th5000 work with a ruud dual fuel
Are you talking about a pro 5000 Thermostat??? if so then NO it will not work.With this stat you do not have a temperature lock on the heat pump. Say you don't want the heat pump to run below 25 degrees. it won't shut the heat pump. And you don't want the heat pump to run at the same time as the furnace. With the Pro 8000 3 heat and 2 cool thermostat you can lock out the heat pump at 25 degrees outside an turn the furnace on. You will have to install an outdoor thermostat hooked up to the pro 8000 it usually comes with the stat. Honeywell products.
Nov 29, 2013 | Rheem 3.5 Ton 14 Seer / Ruud 100K Btu 80%...
Wiring diagram for Rheem rpka-31 jaz heatpump
Apr 13, 2010 | Heating & Cooling
Goodman PC060-1B Package AC...Need Wiring Help
Depending on the size of your Electric heat you can use one set of wires because your unit does not run with the heat like the heat pump. The large set of wires going to the electric heat should be used. You may have to jumper a new set to the contactor. On Goodman unit come in L1 and L2 jumper to contactor. Very simple good luck. Rus
Jun 21, 2009 | Goodman Heating & Cooling
I tried to replace my digital manual Honeywell thermostat that is only 6 months old (new construction) with a programable thermostat. I followed the instructions marking the wires and connecting them up...
Your "R" terminal is basically your "hot" and your "C" terminal is basically your "neutral" to simplify explanation. The Furnace supplies the "R" power to the thermostat and then depending on what wire the thermostat sends the power back on determines what the system does. The thermostat terminals are as follows "G" is fan, "W" or "aux" is elect heat, "Y" tells the outdoor unit to run, "O" or "B" tells the outdoor unit whether it is heating or cooling, and "E" is emergency heat. "G" should connect from the t-stat directly to the furnace and go no further. "W" or "aux" AND "E" should both connect to your "W" or "W1" terminal in the furnace, there should also be a "W" connection to the heat pump ( this allows the H/P to turn on the elect heat when the unit defrosts) "Y" and "O" or "B" may or may not connect to a terminal in the furnace, usually they just pass through the furnace from the t-stat to the H/P and get wire nutted in the furnace. Now, here is the key. As I mentioned previously "O" or "B", a system will only use one or the other. The entire industry (except for Rheem and Ruud) uses the "O" terminial which has 24v on it when you are cooling and no power when you are heating. Rheem and Ruud use the "B" terminal which is just backwards, 24v in heating and no power in cooling. This is all for a heat pump, If you do not have a heat pump, then disregard the references to "O", "B", "E", and "aux". You will have R-power on red wire, W-heat signal to furnace, G-fan signal to furnace, and "Y" cool signal to outdoor unit.
Jun 08, 2008 | Honeywell Heating & Cooling
Wiring connection for a Ruud air handler & seeking its wiring diagram.
we are trying to install a goodman heat pump with a rheem air handler, the orange wire is hook up and the unit is still staying in the heat mood. does anyone have a wiring diagram for the air handler, their is some white wires in the air handler one with a purple strip and one with a black strip we need help
Jan 05, 2008 | Heating & Cooling