GE Profile 24, 15 years old: Occasionally, it trips the house ground fault circuit interrupter (GFCI). Tripping happens about 5 seconds after plugging to mains. For a week the problem disappeared, now it is permanent. It does not trip its Circuit Breaker. When bypassing the GFCI - it works fine.
  • levtg Sep 01, 2010
    As it came, again the fault disappeared. Local technician advised me over the phone that in 90% of cased this is caused by faulty heater in the ice maker. He advised me to disconnect it (3 screws, and power plug). I will debug it once the fault happens again.
  • Refrigerators Master
  • 43,501 Answers
The motor (compressor) is pulling too high amps on the startup ... this tripps the GFCI...
The compressor cap is going bad or the motor is going bad...replace the realy and cap first...
Refrigerator Troubleshooting Refrigerator Compressor
Refrigerator Compressor Start Capacitor and Start Relay
heatman101
Posted on Aug 29, 2010
Coleman mach rv ac unit tripping breaker
If it trips the circuit breaker as soon as you turn the FAN on, suspect either a bad fan motor or a failed fan motor start capacitor. If you are able to turn the fan on but the circuit breaker trips as soon as the COMPRESSOR starts, it is possible that the compressor is seized.
If, on the other hand, the unit is tripping a GFCI (Ground Fault Circuit Interrupter) breaker or GFCI utility outlet, it is possible that neutral and hot are reversed at the outlet into which the trailer is plugged (happened to me this year at an RV park).
May 14, 2015 | Coleman Heating & Cooling
Gfci trips heater not turned on
GFI is Ground Fault Interrupter (or GFCI - Ground Fault Circuit Interrupter) It is doing its job, telling you that there is a short in the unit or wiring. Have a certified electrician check the wiring and unit.
May 17, 2014 | Pentiar Pentair MiniMax 100 BTU Natural...
Hoover Refrigerator Model B38tf. Causes earth leakage circuit breaker to trip. Has just started to occur in last week. What is likely cause and what rectification can be applied?
If you're referring to a GFCI (Ground Fault Circuit Interrupter) breaker tripping, a refrigerator should not be plugged into a GFCI circuit because of the sudden load it requires to start the compressor, etc when it kicks on. The GFCI breakers are meant to be very sensitive, and over time the sudden energy demands caused by a refrigerator can weaken the breaker's threshold, causing them to trip often. Try connecting the refrigerator to another circuit that isn't on a GFCI breaker. If there are no other circuits nearby, you may wish to replace the GFCI breaker with a standard breaker, and replace the receptacles with GFCI receptacles, except of course, the one the refrigerator is plugged into. Be sure and consult and use a qualified electrician for this. Hope this helps..
Oct 29, 2013 | Refrigerators
Installing arc fault interrupter with ground fault
If you meant arch fault with ground fault then no, the two types interfere with each other and trip the breaker as one senses an arch and the other grounding.
If you meant ground fault breaker with a GFCI. receptacle, you only need one of the two, either GFCI. breaker or receptacle.
and for circuits, you can put up to 12 devices (i.e receptacle, light)assuming they consume 1 amp each. Anything over 12 amps or 80% of the rating on the breaker, it will trip/reset.
Or if your talking about wires on a breaker then no more than 2 wires recommended. Try adding a junction box outside the panel if your trying to add other branch circuits or tap off of a receptacle.
Apr 21, 2013 | Siemens Seimens Arc Fault Breaker
No, i have a 50 amp GFCI in my main panel and i am trying to feed a sub panel in my garage. i have power to everything until i plug anything in or turn on the lights.
GFCI's are really temperamental. They are this way for a reason. It seems like you have something that is tripping this. I would try using a regular 50 amp breaker, and then see what happens. You can also try process of elimination. Shut everything down, then bring power up - one item/circuit, appliance, etc. at a time. This will narrow down your problem. Also, if you have a refrig/freezer on this GFCI, this could be tripping it too. Any appliance, etc. that has a motor - usually leaks to ground just enough for the GFCI breaker to sense, and trip it. I hope some of these solution's will help you...Good Luck!
Sep 01, 2011 | Cutler Hammer 1 Pole 15 Amp Ground Fault
After being turned off for 4 days through Hurricane Irene... the pump will trip the breaker whenever we turn it on. The switch is good. We can only assume maybe the water is wet. Any suggestions?
I assume when you say breaker you mean a Ground Fault Circuit Interupter (GFCI) breaker or receptacle. If this is the case then what happens is water can get into devices such as pumps and the water can cause unintended electrical paths from 120VAC nodes to the motor frame which is grounded. The GFCI is designed to detect a nominal 5 mA of current to ground and trip. If the GFCI is tripping I would let the motor dry out for a day (if the weather is dry) and try it again.
If by tripping you mean a standard beaker without a test button is tripping then it is tripping because of high current. If this is the case then it may be a water problem but you are just as likely to have a short in the wiring or the motor. I would try shutting off the safety switch, disconnecting the wires to the motor and wrapping the exposed wires with electrical tape. If you turn the switches on that would normally turn on the pump and the breaker again trips you have a problem in the switches or wires. If the breaker does not trip you have a motor problem. You can try to dry it out but probably it has an internal metalic short. If you have access to the location is you could fix it but if not the motor will need to be replaced. I hope this helps.
Aug 29, 2011 | Emerson THREADED SHAFT UP RATED - 1.00 HP...
I have a GE Profile Model# PDW7700G00CC that trips the circuit breaker when I hit the start button to begin a wash cycle. Green lights are on when I re-energize the unit but problem repeats when I hit...
It sounds like a dead short tripping the CB or a ground fault (short to ground) if the CB is GFCI type.
At start it would energize water valve solenoids, water level sensor (float switch), a timer. These components and circuit should contain the source of the problem.
Find the machine's wiring diagram in the control panel or glued on a panel. Open the control panel and do a visual inspection.
Sometimes a dead short will weld contacts together, check contacts and relays. Isolate parts of the circuit energized tripping the power
Jul 03, 2017 | Dishwashers
The 20 amp breaker for our spa circulation trips within hours or as long as one week. Tthe breaker does not trip off but cuts the power. it requires tripping it off then turning back on. Is this a faulty...
This is probably not a faulty breaker. A GFCI breaker is designed to trip when there is a 4-6ma inbalance of current(usually 5) between the two current carrying conductors (hot and nuetral) You may be having a moisture problem. Check all of your electrical connections (with power off) for moisture. If you find any throughly dry (like with hair dryer) and seal to prevent further problems. Your motor may be an open drip proof motor. IF condensation builds inside that coud also cause problem. There are GFCI testers available if you wanted to test your breaker, but for one time it probably isn't practical.
Aug 13, 2010 | General Electric 20 Amp, 1 Pole Thick Type...
LG Washer trips dedicated breaker
That to me seems like an electrical problem. Every now and again you can get a bad GFCI receptacle that will constantly keep tripping. I would also see that the GFCI is properly sized for the circuit. It needs to be a 20 AMP circuit (just dedicated to the washer) and a 20AMP GFCI receptacle. The way to tell is the 1 of the three prongs of the 20AMP GFCI will be in the shape of a "T" while a 15 AMP will have 2 straight prongs and the ground prong. Hope this ws helpful, don't go spilling any money into your washer without getting that fixed first, because it doesn't seem like a washer problem.
Apr 30, 2010 | LG WM2016C
Sears 90 Series Washing Machined throws ground fault during spin.
pvatki, I am a licensed electrician and the NEC (national electrical code) does not require a clothes washer to be on a ground fault circuit interrupter. Replacing your gfci with a standard duplex receptacle will fix the problem you are having.
Dec 29, 2008 | Kenmore 15864/15862 Top Load Washer
Refrigerators Logo
165 people viewed this question
Top Refrigerators Experts
Charles T Nevin
Charles T Nevin
John Tripp
John Tripp