Have a Lenox HP13 outside, and CB26 Air Handler. Just changed out the Thermostat to a Honeywell RTH7500 programable. Atached the Red to R, Orange to O/B, Yellow to Y, Green to G, Blue to C, and White to Aux. Reset all breakers in main box in house now have no air handler fan and no condenser turn over? What did I screw up?
  • Brian Niten Aug 28, 2010
    Some thermostats have a built in time delay. This could be up to 5 mins. Also the circuit board in your outdoor unit may have the same. It's been my experience that they do. If it hasn't already started running, you may want to turn it back on and give it a few minutes.
    President:
  • 1,515 Answers
Hi, sounds like this is a Lennox heat pump. On the stat wiring it looks as though you wired it correctly except on the reversing valve terminals o/b, the orange wire should be on the o terminal only as the reversing valve is energized through in the cooling mode and will default to heat if the compressor fails. Make sure you have no control wires at the new stat that may have touched and blew the 3 to 5 amp fuse in you air handler. You can go to the air handler and see if the circuit board has this auto type fuse and a control board I believe it will as it may have blown. Just sounds like this is a control voltage problem as this is all you have been working with is the change out of the stat. Keep in mind that this new stat also has a built in time delay that will keep the unit off for several minutes.Check this fuse though. If you have excess to a voltage tester, you could check for 24 volts at the stat by setting it on its lowest ac volt setting and check across R to G or Common and it needs to read 24 or more volts. If not, its either a control volt 3/5 amp fuse or a faulty transformer. You say you had the breakers off, so if you happened to stripped the wires at the sub-base and the R or hot has touched the C terminal it could have taken out the transformer or just a fuse. This is where you need to look first is the control board or control module. Please keep me posted so I can get you up and running. Make sure you have the stat programmed correct also. Please let me know.
Shastalaker7
A/C, Heating Contractor
Posted on Aug 28, 2010
Hey, I purchased your Honeywell RTH2510 Thermostat, but I didn't even think to label the wires when I took the old thermostat off. Upon installation of the new Thermostat (2510) the Air Conditioning...
The connections that you really need to reference would be at the air handler itself. That would tell you which wires go outside to the heat pump and which wires go to the air handler. I can however give you some basics that may help.
Heat Pump Wiring
Terminals/Colors/Function
R- Red- 24v power supply. (Usually a jumper between RC/RH)
G- Green- Fan
W- White- Heat (Sometimes W1-W2, first or second stage heat)
Y- Yellow- Cooling (Same applies as above i.e. Y1-Y2)
C- Common (Most people use blue unless it is used for B terminal and sometimes cooling on older 4 wire systems.
B/O- Reversing Valve for heat pump. Either powered heating or powered cooling, depending on system installed.
Aux- Also used for heat.
Note: Considering that the installer had their own way to run all wires, use different wires, connections, etc. This is just a reference to common wiring in the field.
How the most common system is hooked up:
Thermostat:
Red wire goes to R terminal
Yellow wire goes to Y1 or Y2 terminal
Green wire goes to G terminal
White wire usually goes to W1 or W2 terminal
Orange or Black wire goes to B/O terminal
Brown wire usually goes to Aux terminal
Blue wire goes to C terminal, unless its being used as stated above.
This is without using a fossil fuel kit or zone control board.
Where do they go from the thermostat?
Red
goes to the air handler transformer or board and goes outside to heat pump to power low voltage controls.
Yellow wire goes straight outside to Y terminals on heat pump unless going to a board inside first.
Green goes to the air handler fan relay.
Common goes to the air handler and outside to heat pump.
Black or Orange will go outside to heat pump terminals for reversing valve.
White usually goes outside to heat pump,and inside to air handler. Will explain reason further down.
Brown will go to the air handler to the heat relay for the emergency heat.
On a call for heat, with a powered cooling system (more common).
The R, Y, and G terminals energize, sending a signal to start the blower and pull in the contactor outside. Note that the Y terminal is usually cooling, but since this is a powered cooling system, the reversing valve is not energized, causing the system to run in heat mode. If you have powered heating, the reversing valve terminal will energize also. Depending on thermostat, if you set the temp substantially higher than room temp, it may kick on the emergency/aux heat to quickly raise the room temp. On a call for emergency/aux heat, the R, G, and E/Aux terminals are energized, turning on the electric/gas heat instead of the heat pump. This comes in handy since the heat pump can only pull so much heat from outside before its not enough to properly warm the house, usually around 30 degrees outside temp. If you are running the heat pump and the system goes into "defrost", the outside unit will send a signal back to the air handler, through the white wire I mentioned earlier, to tell the emergency/aux heat to come on while it is in defrost mode, providing heat whenever needed.
Again, this is just a reference guide to some basic wiring, but hopefully it will tell you where the problem is or at the least, give you a good start. There are variables in which things can change the wiring like a zoning system or fossil fuel kit. Even then, you should be able to get pretty close. Hope this helps and Happy Holidays!
Dec 07, 2013 | Honeywell Programmable Thermostat Heater
Hi I have a hb2400vd2m20 air handler and need to know what wires are needed to hook up to my thermostat its a Honeywell, as of the moment there is no heat pump it just the air handler running. I know there...
Honeywell 5000, 8000, 8000 iaq, prestige, round dial analog, digital Honeywell redlink. 1 heat 1 cool thermostat 3 heat 2 cool thermostat. does the stat u have do conventional a/c and heat pump. red wire is hot wire 24 volts not heating its your 24 volt control power. this will be r on your board and t-stat and red wire. y is for cooling mode and is yellow and will be noted y on both board and t stat. green is fan on the indoor furnace and will be g on board and t-stat and the wire is green. blue is the common side of the transformer labeled b on both board and t-stat. I did not see brown on your schematic I looked up I seen orange which is your reversing valve wire for the heat pump whether its calling for cooling or heat this is what changes the flow of Freon to make it to the indoor coil as warm Freon or cold when called for in heat or cool. the thermostat if a vision pro 8000 needs to be programmed in the installer mode which if this is the t-stat u have u need to read through the heat pump section. the green hooked to the orange doesn't look right on the print but that's the breakdown. http://www.manualslib.com/manual/277678/Haier-Hb2400vd2m20.html?page=11#manual heres your schematic
Oct 20, 2013 | Haier 2.0 Ton Multi-position Air Handler...
How to wire Honeywell thermostat RTH7500 from old Weathertron GE
You have a control board on your furnace, there is a 3 amp fuse there, that 3 amp fuse needs to be replaced. You most likely touched a wire even by accident and blew the fuse. You will have to remove the door \panels to get at it. It looks like a normal car fuse
May 31, 2010 | Honeywell Electronic Programmable...
Upgrade Baystat 239 to a Honeywell RTH7600D controller
For Trane sytems, B is your "Common" wire. O is your reversing valve relay, G is your fan, Y is your compressor contactor, R is Hot, Brown will not be used on your electronic tstat. X2 is your backup electric heaters. Without knowing what terminals are on your new tstat, I cannot offer more information than this. The installation manual may indicate what each terminal is controlling. I strongly suggest to write down ALL of the terminals and colors from your old t-stat and be sure to turn off the power to your air handler. Put the fan switch on your tstat to ON before turning off the power. Make sure the fan is running. Then turn the power off to your Air Handler. If your fan stops running, you have turned the power off to your tstat and are ready to start replacing it with your new tstat. I hope you find this helpful. Good Luck!!!
Feb 06, 2010 | Heating & Cooling
Installing 1 1/2 ton Weatherking Heatpump and ADP WAK351807P2 air handler 1 /1/2 with 7.5KW back up heat kit. Can't seem to get the thermostat hooked correctly. I understand the Weather King product...
O energizes the reversing valve when the thermostat is set for COOL. B energizes the reversing valve when the thermostat is set for HEAT.
The O/B is usually a orange or black wire.
You can't hurt anything if you choose O or B incorrectly. Hook one of them up and run the unit. If set for COOL and the unit runs cool inside it is correct. If set for COOL and the unit runs warm inside it is not correct.
If the inside temp is opposite from your setting change the wire to the other terminal.
Remember to disconnect power from the air handler when changing thermostat wires.
The defrost control board on the outside unit should be marked correctly for O or B.
Your thermostat may have a slide switch rather than a separate terminal.
Oct 30, 2009 | Weather King 10AJA6001AH Air Conditioner
System will not turn off
Call the honeywell technical service number listed on the instruction sheet for the thermostat.
They can verify if you have the correct stat for your application and the wires are connected to the right terminals.
May 30, 2009 | Heating & Cooling
Honeywell Thermostat RTH 7500
Assumed all the wiring are correct,
to change from manual switching from heat to cool, press [system] button ( left ) to go into system setting.
then press and hold the [fan] middle button untill option display 120
use up down button to select option 300 ( Manual/Autochangeover) ,
select 0 for manual, 1 for automatic. ( read caution in page 22 of installation manual )
Good luck
Sep 30, 2008 | Heating & Cooling
Replace Carrier tstatccshp01 builders standard thermostat with Honeywell rth7500 series and wiring not matching Does O wire go to Aux..? fan working but no cool air.
No... Aux. is auxiliary heat strip. This is usually a white or black wire its up to the choice of the installers preferance. O or orange wire. is used to the reversing valve on a heat pump. If you do have a heat pump there is a programing section inside the Honeywell t-stat. which should say heat pump or straight cool, then another section that will ask if you want the reversing valve to energize in heat or cool. most Heat Pump brands energize in cool the exception is Rheem and Ruud they energize in heat.
May 17, 2008 | Honeywell Heating & Cooling
Replaced thermostat on FA4ANF030 with Honeywell model rth3100c does not work
if you have a newer t-stat your heat pump reversing valve is either o or b depending on the type of system you have
Dec 02, 2007 | Heating & Cooling
Heating & Cooling Logo
115 people viewed this question
Top Heating & Cooling Experts
Paul Carew
Dan Webster
Dan Webster
Donni Steen